Help me. Modine garage heater

Cwill375

Member
Joined
Dec 29, 2018
Messages
5
Location
Backyard
I have a Modine garage heater it only has one orifice and I think it’s to big for me running natural gas trying to find out what I need there are no numbers on it or the unit
 
To avoid these ads, REGISTER NOW!

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,901
Location
Niagara Region, Ontario, Canada
is it a new heater? what does the spec label say , propane or nat gas?
does it have a sticker that says it's converted?
why do you think it's too big for nat gas?
what size/model heater ?
 
OP
C

Cwill375

Member
Joined
Dec 29, 2018
Messages
5
Location
Backyard
is it a new heater? what does the spec label say , propane or nat gas?
does it have a sticker that says it's converted?
why do you think it's too big for nat gas?
what size/model heater ?



Sorry there is no labels on it there is one that says it’s propane but I can put a pencil lead in the hole of the orifice I just got a new gas valve for it due to the old one being bad. When I go to turn it on you can hear the gas flow and then get the explosion ignition where it like getting to much gas
 

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,901
Location
Niagara Region, Ontario, Canada
I think this is beyond average DIY, the gas valve probably needs to be adjusted for proper pressure . the orifice will need to be sized properly, and if there's no labels on it, your insurance company may have issues with it.
there are conversion tables on-line to help with orifice sizing, but you should talk to a pro, in my opinion
 

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,254
Location
The UP, God's country
Don’t know about Modine, but other manufacturers offer conversion kits with new orifices, pressure regulator springs, and installation / setting instructions for conversions.

Conversion isn’t exactly plug and play.

Buy the kit, or a new heater. They’re incredibly inexpensive.
 
To avoid these ads, REGISTER NOW!

jenga70

Member
Joined
Oct 7, 2014
Messages
17
Propane typically runs at 11" W.C. pressure while NG typically runs at 3.5" W.C. pressure, so pressure needs to be set for which ever fuel.

There should be some stamped markings on the orifice. I have a 75K Modine and it runs a single #21 orifice (.159" dia) that feeds into a mixing tube and five burners work of that.
 

jlrut

Well-known member
Joined
Dec 30, 2018
Messages
81
Location
Michigan
You never specified what gas you are running and what the unit and gas valve are set up for. Also, installing a fast open gas valve in a unit designed for slow or step opening will cause those symptoms as well.
 
OP
C

Cwill375

Member
Joined
Dec 29, 2018
Messages
5
Location
Backyard
I have found that the orifice is a 45 I’m trying to run natural gas. When I run propane it starts up great but will trip the the button on top
 

jenga70

Member
Joined
Oct 7, 2014
Messages
17
I had convert my mode from propane to natural gas, so I have went through this exercise. My was a 75K BTU unit and had the labeling on the side, so it was pretty straight forward.

A 45 orifice is a .082 dia hole. For LP at 11" W.C. pressure, that works out to 46969 BTU output.

If the new valve was setup as NG specific, then the pressure range is set much lower than propane but it is not set to a specific number as different appliances run at different pressures.

1) You need to get a manometer and adjust it to 3.5" W.C. (That's what my unit labeling said for example). You can make your own manometer, goggle it but your on your own. I had a local connection, so he dialed it in for me.

2) Obtain the orifice size that has the same BTU output as the LP fuel at 11" W.C. In this case, if you run NG at 3.5" W.C. pressure, you need a number 29 size orifice and that gives 46961 BTU output.
 
OP
C

Cwill375

Member
Joined
Dec 29, 2018
Messages
5
Location
Backyard
I had convert my mode from propane to natural gas, so I have went through this exercise. My was a 75K BTU unit and had the labeling on the side, so it was pretty straight forward.



A 45 orifice is a .082 dia hole. For LP at 11" W.C. pressure, that works out to 46969 BTU output.



If the new valve was setup as NG specific, then the pressure range is set much lower than propane but it is not set to a specific number as different appliances run at different pressures.



1) You need to get a manometer and adjust it to 3.5" W.C. (That's what my unit labeling said for example). You can make your own manometer, goggle it but your on your own. I had a local connection, so he dialed it in for me.



2) Obtain the orifice size that has the same BTU output as the LP fuel at 11" W.C. In this case, if you run NG at 3.5" W.C. pressure, you need a number 29 size orifice and that gives 46961 BTU output.



Dude that was the best info I have gotten from anyone thank you very much this will be a big help again thank you
 