Ok it was a dumb question :spit: I was just curious as why 4/0 4/0 2/0AL is required to feed the house from the breaker at 200amp. but not to feed my 200amp. meter?
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
The power company doesn't follow the NEC.

They size their wire to the load, where as the NEC says you have a 200 amp breaker, you need 200 amp wire regardless.
 
To avoid these ads, REGISTER NOW!
OP
7

700jfm

Well-known member
Joined
Jan 29, 2008
Messages
383
The power company doesn't follow the NEC.

They size their wire to the load, where as the NEC says you have a 200 amp breaker, you need 200 amp wire regardless.

Thanks Aceman :thumbup:
 