Ok I"ve made my mind up this is the compressor I'm going to buy.
http://www.northerntool.com/shop/tools/product_200350477_200350477 What gauge of wire and breaker do I need to run this? I read on another site that it needs an 80 amp breaker. That seems kind of big to me. Does anyone have any experience with this? I plan on putting the compressor about 25ft from my breaker box but the wires would need to be ran up the wall along the ceiling and back down the wall to a junction box where I can run it into a flex line to the compressor.
First off what size service do u have? Any other large electric loads? 7.5HP is a good sized load on startup.
U said it will be 25' from the panel? Is it within sight of the panel? If so then u dont need a disconnect.
U will need 50a rated wire. This is because wire for motor circuits is sized @ 125% of NEC table FLC. 7.5hp is 40a FLC.
So use #6/2 NM-b or #8 THHN in pipe. If u use THHN in pipe u will need 2 #8 and a #10 for the EGC.
U cant use an outlet and plug unless u can find one rated for 7.5HP or more. So it will need to be hardwired.
Breaker can be max 250% of NEC table FLC.
Nah. 40 amp @ 230 will work but 50 is a better bet.I have an Atlas 7.5 on 50. Never had a problem. Put a box with a disconnect switch to wire into.You want it right there for maintainence.
Breaker size depends on motor.
Disconnect isnt required if within 50' of and within sight of the panel.
Run your 3 wires in 1/2" or 3/4" gray electric PVC.
Here's a wire chart
http://www.amplepower.com/primer/gauge/
Wrong chart. Thats for DC 12v....