The hot water recirc system in our (circa 2003) home hasn't worked great since we bought it in 2020, and it's been making a racket if the pump runs very long for the last year. I thought it might be air in the return line, but after installing a vented 90* fitting in that return I don't believe that to be the case. So now I'm thinking of replacing the pump. It's a 3yo Grundfos Comfort PM. When I took it apart, the surface area the impeller rubs against was rusted and pitted. I got the rust off, but the surface is still pitted.
I need help sizing a new pump, as I believe the current one is too small. Here's a photo of the system:

The system is made up of three loops of cold supply, hot supply and hot return, in order from right to left. (The rightmost lines support outside hose bibs and can be ignored.) The hot supply line out of the tank is 1" copper, and it serves the three 3/4" PEX supply lines. The three hot water return lines on the left are 1/2" PEX, feeding into the 3/4" copper line leading to the Grundfos pump.
The three hot and return loops are:
Loop 1 (Kitchen) - 35' of 3/4" PEX and 35' of 1/2" PEX return. The Taco Comfort calculator (http://apps.tacocomfort.com/wizard_dhw.html) I used calculates 3.39 feet of head for this loop, at 1.1GPM (which the calculator says is the max recommended for 1/2" PEX at 140*).
Loop 2 (Master Bath) - 49' of 3/4" supply and 1/2" return line. Calculated head is 4.72.
Loop 3 (Guest Bath) - 72' of 3/4" supply and 1/2" return line. Calculated head is 6.96.
The utility room supply and return lines have a calculated head of .64 at 3.2GPM (the limit for 3/4 copper).
My question is, what GPM and head figures do I use to size the pump? It seems to me I'd need 3.3GPM from the pump to get 1.1GPM through each of the return loops, or does their differing lengths make it more complex than that? I have no idea what head number to use. I know not to simply sum them, but I'm not sure just using the figure from the highest one (6.96 + .64 from the utility room loop = 7.6) is right, either.
The current Grundfos pump appears to have a max head pressure of 3.9', at which it flows next to nothing. Sure enough, it only works marginally well if running all the time, and if the Guest bath loop is closed. I'm considering the Grundfos Alpha 15-55 HWR-T, but am concerned it's way too big. For example, at 7.6 feet of head (from the paragragh above), it flows nearly 9GPM, way more than allowed if I expect the pipe and tube to last.
I've been reading, watching and ciphering all day, and am coming to you guys for expertise. School me, please.
Mark
I need help sizing a new pump, as I believe the current one is too small. Here's a photo of the system:

The system is made up of three loops of cold supply, hot supply and hot return, in order from right to left. (The rightmost lines support outside hose bibs and can be ignored.) The hot supply line out of the tank is 1" copper, and it serves the three 3/4" PEX supply lines. The three hot water return lines on the left are 1/2" PEX, feeding into the 3/4" copper line leading to the Grundfos pump.
The three hot and return loops are:
Loop 1 (Kitchen) - 35' of 3/4" PEX and 35' of 1/2" PEX return. The Taco Comfort calculator (http://apps.tacocomfort.com/wizard_dhw.html) I used calculates 3.39 feet of head for this loop, at 1.1GPM (which the calculator says is the max recommended for 1/2" PEX at 140*).
Loop 2 (Master Bath) - 49' of 3/4" supply and 1/2" return line. Calculated head is 4.72.
Loop 3 (Guest Bath) - 72' of 3/4" supply and 1/2" return line. Calculated head is 6.96.
The utility room supply and return lines have a calculated head of .64 at 3.2GPM (the limit for 3/4 copper).
My question is, what GPM and head figures do I use to size the pump? It seems to me I'd need 3.3GPM from the pump to get 1.1GPM through each of the return loops, or does their differing lengths make it more complex than that? I have no idea what head number to use. I know not to simply sum them, but I'm not sure just using the figure from the highest one (6.96 + .64 from the utility room loop = 7.6) is right, either.
The current Grundfos pump appears to have a max head pressure of 3.9', at which it flows next to nothing. Sure enough, it only works marginally well if running all the time, and if the Guest bath loop is closed. I'm considering the Grundfos Alpha 15-55 HWR-T, but am concerned it's way too big. For example, at 7.6 feet of head (from the paragragh above), it flows nearly 9GPM, way more than allowed if I expect the pipe and tube to last.
I've been reading, watching and ciphering all day, and am coming to you guys for expertise. School me, please.
Mark