Here are some specs. I have a navien ch210 combi boiler. I am trying to use the remote that comes with it as a thermostat. But it isn't triggering my taco relay so the secondary pump never kicks on. The boiler does fire up and circulate just fine and I do have the dipswitch for the external thermostat off

I have the T T from the boiler hooked up to the taco sr501 switching relay at the 6 n/o and at 5. Is this not correct?
 
To avoid these ads, REGISTER NOW!
OP
F

Flexia

Well-known member
Joined
Mar 8, 2013
Messages
215
Location
Akron/Canton Ohio
All I see there is "N", CN18, Yel/Wht feeding (1) pump directly. No relay...

Tommy
There is a relay its just sealed on the board. Here is the ladder. I was thinking about making a relay to hook the the pump wire to trigger the taco relay
4db9934a8e3d840553b6c691cfea52e0.jpg
 

Rookie2

Well-known member
Joined
Feb 27, 2013
Messages
1,925
Location
Western Pa.
I would call the tech line !
All I see that it could possibly be is (outputs) T/CN26 or R/CN25 or that S block .

If you wired the taco sr501 correctly then by jumping R & W the circulator should run.
 
To avoid these ads, REGISTER NOW!

truckman5000

Well-known member
Joined
Mar 11, 2008
Messages
1,440
look at the sr501 wire diagram, you need to put a hot? jumper to the #5? terminal. As i dont have one infront of me, but the pump contacts dont get line voltage, without the jumper. Its a 24v/120v contact, bringing 120 to it would power the pump
 
OP
F

Flexia

Well-known member
Joined
Mar 8, 2013
Messages
215
Location
Akron/Canton Ohio
look at the sr501 wire diagram, you need to put a hot? jumper to the #5? terminal. As i dont have one infront of me, but the pump contacts dont get line voltage, without the jumper. Its a 24v/120v contact, bringing 120 to it would power the pump
That's not the problem. I can bridge the R&W on the taco to start the pump. The problem is the boiler isn't telling the taco really when to turn on
 
OP
F

Flexia

Well-known member
Joined
Mar 8, 2013
Messages
215
Location
Akron/Canton Ohio
I would call the tech line !
All I see that it could possibly be is (outputs) T/CN26 or R/CN25 or that S block .

If you wired the taco sr501 correctly then by jumping R & W the circulator should run.
When I got home today I put my multimeter on the cn26/ external power. It does throw 120v out when the primary pump in the navien in on. I'll prob make a relay that will flip from that 120 and then it will bridge the R&W when flipped.
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
How is the remote going to work as a thermostat? I thought you could only use it to adjust the boiler temp? Does it have any type of room temp sensor in it?

I would use a normal thermostat to control the taco relay and the aux contacts in the relay to turn the boiler on and off.
 
OP
F

Flexia

Well-known member
Joined
Mar 8, 2013
Messages
215
Location
Akron/Canton Ohio
How is the remote going to work as a thermostat? I thought you could only use it to adjust the boiler temp? Does it have any type of room temp sensor in it?

I would use a normal thermostat to control the taco relay and the aux contacts in the relay to turn the boiler on and off.
Yes the navien remote can act like a thermostat. Has temp sensor and is programmable too
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
I would call the tech line !
All I see that it could possibly be is (outputs) T/CN26 or R/CN25 or that S block .

If you wired the taco sr501 correctly then by jumping R & W the circulator should run.

That's what I was thinking, too.

I got so wrapped up in trying to find a relay on the diagram I forgot to post that.

Tommy
 
OP
F

Flexia

Well-known member
Joined
Mar 8, 2013
Messages
215
Location
Akron/Canton Ohio
Just to update you guys. I used the external power term on the navien to flip a small 120v relay that then will bridge the TT on the taco relay.

It works for me but is an extra step. You could get a bigger 120v relay that will get triggered from the boiler to power the pump. But I already had the taco contoler
 