CoopVA, can you show a link for the non-fused disconnect that you like?
I don't think it is a switch??? Home Depot s description says it is but I believe it is simply a disconnect. GE for 8$ too. Its a glorified range plug,,, hahahaha Ruins a good piece of wire with another splice.
^^I don't know what you pointed to but electricity is electricity. Theoretically, you can have a motor that pulls 100A (@ 2% efficiency) and produce 5hp and you can have a motor that pulls 20A (@80% efficiency) and produce the same 5HP.
I'm not disputing if there's HP value to plugs or not. As a matter of fact, each motor is designed slight differently with loading characteristic (amp, torque, etc...). Again, you can have one 5HP that pulls different amp base on its efficiency rating. Therefore "HP" rating is not the true value for termination and wiring requirement. It just so happen that motors have an HP value, and people use the term "HP" for ease of conversation/understanding.
Wow tons of information given. Mind blown. Info overload. My intention is to wire a branch circuit off of the sub panel already located in the garage. When this panel was installed, it was done so for light duty use with only 50 amp service. I know I am limited with that, but I don't care to run another 100ft 100 amp service since this isn't my permanent place of living.
I was hoping to be able to wire a single plug that I could use for either compressor or welder. Not both simultaneously. However, it seems based on the discussion here that safety wise as well as cost, hard wiring the compressor would be the best bet.
I can continue to run my welder off 110v, as I don't do any real heavy gauge welding at home that can't be done multi-pass.
As for supplies...35 amp breaker for code even though motor states 22 amps?
And I happen to have about 50-60' of 10/3 that was given to me by a friend off a construction site that they left behind. How do I know if the wire is adequate?
^welcome to GJ. You'll find different minded people with different background; some will act like robot and give you answer what they heard and some will provide you a direct answer.
That ROMEX wire #10AWG is proper for your Century 5HP motor.
I appreciate all the responses. Better to have multiple points of view anyway.
By chance, would that Romex also be adequate for my welder in the future?
Alright, so many conflicting opinions here.
Simple question. Is the wire I have adequate for running the compressor?
Or do I need to run #8?
The plate on the motor says 22 amps, but I don't know if that is running amps, startup surge, etc. Nor can I find out searching online. To me, if #10 is rated for 30 amps, then a 30 amp breaker with my #10 wire would be fine. But I have next to no idea what I am talking about so I could be entirely wrong.
Second question - Is the wire I have adequate for running my Miller 211? According to the manual at 230v it is going to pull 25 amps max.
Seems I was replying as you were typing. I will be hard wiring it that is settled.
Now I'm just trying to figure out what I need to pick up to do so. I'm not saying you are wrong, but I am curious why it says 22 amps on the name plate if a 5hp compressor requires 35?
Sorry for all of the antics. Let's get back to productivity on this subject.
if the Full Load Amp rating is 22A, then a 30A capacity wire will be proper
(120% is right under 30A).
The proper breaker for the #10 wire is 30A or less. Note that circuit breaker or any fuses is intended to primarily protect the wiring, not the equipment.
This is very silly! It's even sillier when y'all say I'm wrong, you don't dare to reference the code.
Who are the GJ experts that explain to y'all of this? When reading codes, it's important to NOT take it as face-value but analyze it and then interpret it. It happens all the time in my work line.
AGAIN, I'm not disputing the power (HP) value that one motor make when it comes to wire sizing. #10 wire size may not work for other 5HP based on specific motor design. I'm sure NEC will provide some general current value based a "typical" 5HP motor design but that's general - that's code guys, it's conservative! If I was to provide a turn-key installation for any 5HP motor out there to run on the feed line, I would size it up to #8. Again, this is not a job, it's for his specific motor he provided.
Like I said before, HP is relative (NOT DIRECT) to FLA, and I highly doubt NEC will advise using "HP" to size wire w/o specifing a general statement regarding the NEMA design characteristic (torque, speed, etc...) of modern AC motor.
Not all motor will have the "normal speed" of 1700rpm or 3400rpm; it's all different from brand to brand. Also, not all motor ppl use are NEMA design specs!!!
Go ahead and quote what NEC says about HP and wire size. Like all codes, it will state very general but enough for accurate interpretation.
FYI:
After speaking with my electrician, he suggested pulling 10-3 for a compressor and 8-3 for a welder. He did suggest keeping the 8-3 run as short as possible.
A purchase of either is not imminent, heck, maybe not ever. But maybe the next guy who lives in my house will want them? With the walls open, it's much easier for me to do it now and 'future proof' it the best I can.
In case interested, this article provides the cites that you must use the NEC table values to determine ampacity of motor circuits based on HP ratings.
Section 430-6(a)(1) requires the use of Tables 430-147 through 430-150, based upon the motor horsepower rating, for determining the ampacity of circuit conductors and for sizing any switches or branch-circuit short-circuit and ground-fault devices for the circuit. The current rating marked on the motor nameplate is only used for sizing of overloads for the circuit and if the motor nameplate ampacity is larger than the table values given.
If a single motor is being installed for a continuous duty application, Section 430-22 requires the branch-circuit conductors to have an ampacity of not less than 125 percent of the motor’s full load current rating based upon Tables 430-147 through 430-150.
The tables give FLC (full load current) based on nameplate horsepower. This table value FLC must then by multiplied by 1.25 to arrive at the required minimum wire ampacity.
The FLA (full load amps) listed, here 22, is used only for the overload (thermal protection on the motor itself).
That's not entirely true
You are absolutely correct he has to use the 60 C deg column as UL and the NEC only require equipment 100 amps and above to be designed 70 C deg. Unless otherwise stated on the device you must assume it is 60 C deg
But as for Hp rates - No
The NEC is Very specific allowing you to wire dedicated circuit based off the Manufactures FLA/Current rating.
430-6 (a)(1) Exception 3 - Period End of Subject
Not to even take in account for motor efficiency but the motor design load has been sufficiently demonstrated to the Underwriter Laboratory to draw the rated amount of current.
No where in the NEC are you required to wire to what you suspect the motor MIGHT be changed out to
Moreover, it is MOST unclear that exception you refer to applies here. That the exception states specifically that it is for nameplates on the APPLIANCE, not the motor.
The very following section of the NEC, Section 430.6(A)(2), states, "Nameplate Values. Separate Motor Overload protection shall be based on the motor nameplate current rating."
The commentary that follows states:
"[the] ampacity of motor branch circuit conductors . . . are determined by the ampere values listed in Tables 430.247 through 430.250, not the ampere values listed on the motor nameplate. The ampere rating provided on the motor nameplate is used to size the overload protective devices . . . ."
Thus, we have a pretty nice explanation of what the motor plate amps are to be used for and motor nameplates are distinguished from appliance nameplates expressly.
But, I suppose you would argue that this section is just for bare motors that are not part of some appliance and an air compressor is an appliance and it can use the manf. stated current rating. I think the section is UNCLEAR at best. It is poorly drafted, no doubt.
I suppose if the compressor has a UL listing and a label on the compressor itself, apart from the motor plate, that we could use your exception. For me, it all comes down to whether the compressor is a "listed motor-driven appliance" with a UL listing and separate UL labeled specification plate, otherwise it gets treated like a motor.
^NEC calls it full-load current and manufactures calls them full-load amp; they're the same. I have to SCREAM at y'all guys again: FLA is the SAME as FLC.
Use of the term “full load current (FLC) rating” indicates the table rating while use of the term “full load ampere (FLA) rating” indicates the actual nameplate rating. This makes it easier to clarify whether the table ampacity or the nameplate ampacity is being used.
FLC in NEC tables are more like theoretical values, based on a general motor design specification or characteristic -
He said he likes to run an extra neutral wire on 'future' stuff - that way in the future I could run 120v out of it if necessay. I'm not sure if it's worth the $25 difference in wire cost to me, however.
For a temporary installation, surface mount conduit to the compressor is probably your best bet. In that case, 10AWG stranded wire is the way to go. If you decide to use the leftover 10/3 nm cable instead, then be aware that it "might" not meet code,
That gray romex wire is proper w/ 30A breaker to run that 5HP, and many other 5HP out there.
Those gray romex are actually more expensive with better rating. Don't they have higher amp capacity than the typical romex?
Against some advice, and following some others, I got the compressor wired in with the romex I had and a 30 amp breaker. It is running just fine. I will say, start up amperage is a surge. Lights in the garage dim pretty good for a fraction of a second.
I'm renting from family so I can do as I please to the place with no issue as far as permission goes. I've got it hooked up with the wire I had, and a 30 amp breaker. For the time being, that is how it will stay. So far no problems. If somehow I end up living here for longer than I anticipate, I will upgrade the sub panel and the wiring to the compressor.
This is crazy because I tried to explain the logic behind it and thought many of y'all guys are good at reading the NEC; I guess I'm wrong about that. I'm no electrician but I can very well read codes and I'm very good at it.
If you want to follow the code, let's follow the code. Base on the NEC 2011 (430.22 (E)), the full-load current value to size the wire is 30.8Amps for that Century B384 motor. SO NO, IT'S NOT 35A.
Again, the OP isn't providing a service.
If you want to use the table based on general 5HP design specs, go ahead and size it up based on 35A FLC (28A*1.25).
As long as his breaker is 30A, the wire is protected and his motor will run under 30A - that whats matter!
Many of you mention start up in-rush current, so why not size that wire/breaker to ...let's say... #2/100A? ...why even mention it? Why? So silly!!!
If anyone of you is an electrician and wanting to bid on large project, you will never win any contract because your copper/aluminum cost will be too high!
All along, I was just trying to make some practical sense from experience and most of y'all guys say I didn't read the NEC. Well fine, I haven't looked at the NEC in ages. Well, the truth is you and others obviously did not read NEC section 430.22.
The code usually are general and flexible but y'all guys are stuck with sizing wire only with "HP" value.
AGAIN, FUNDAMENTALLY, HP VALUE IS NOT DIRECT RELATION TO CURRENT (AMP).
W/o gripping the idea behind electricity well, and NEC is the only thing you got, I can understand why one would use "HP" to size their wire.
^So what did the OP do?
If you really want to go into code, then NEC allows two methods of sizing wires based on service duty (not motor rated duty):
1)Table 430.148 (NEC 2011)
2)article 430.22 (E)
I suggest you and everyone read both.
I fully intend to replace the wire I have with 8/2 when I've got an extra $100 to throw at it.
I'd also love to upgrade the panel when I have an extra $500 to throw at wire for that. Unfortunately, in my current position, money is even harder to come by than the truth about eletrical code.
Had I known this question would have started a ******* match, I wouldn't have bothered asking the internet experts.
Just how long is that wire run from the panel to the junction box next to the compressor? $100 would just about buy you a 125-foot spool:
http://www.homedepot.com/p/Southwire-125-ft-8-2-NM-B-Wire-28893602/202316591
![]()
which, if you need anywhere near that much, potentially brings voltage-drop into the equation, which in turn MAY warrant upsizing to AWG 6.
OTOH, $35 will get you a 25-foot roll at your local Lowe's:
http://www.lowes.com/pd_330916-295-28893621_0__?productId=3338754
and it's probably available even cheaper if you shop harder than I just did (which took all of 10 seconds).
I think you are overestimating those costs, as well. But regardless, the "I can't afford it" claim brings us right back to the question I asked you earlier:
Can you afford to reimburse your family for the replacement value of that house/garage, out of your pocket?
It would not have deteriorated so badly, had some folks not insisted on repeatedly posting bogus information. That happens sometimes.
Maybe I should've copy and paste the whole portion of NEC in the first place. Hopefully, you don't twist NEC's language like you did w/ mine....
It's NOT two alternate methods which the installer can pick from at his whim. Article 430.22 requires the use of Table 430.248 (in the case of single-phase AC motors; there are alternate tables for other motor types) for conductor sizing, regardless. The motor in question is specifically marked as being "Continuous Duty". Table 430.22(e) pertains to derating "Intermittent Duty" motors; and would in any case effectively cause the minimum required conductor size to grow LARGER, not smaller.
ARTICLE 430 Motors, Motor Circuits, and Controllers
430.1 Scope. This article covers motors, motor branch-circuit
and feeder conductors and their protection, motor overload
protection, motor control circuits, motor controllers, and motor
control centers.
Motor Circuit Conductors, 430.21 through 430.29 Part II
[Part] II. Motor Circuit Conductors
430.21 General. Part II specifies ampacities of conductors
that are capable of carrying the motor current without overheating
under the conditions specified.
430.22 Single Motor. Conductors that supply a single motor
used in a continuous duty application shall have an ampacity
of not less than 125 percent of the motor full-load current
rating, as determined by 430.6(A)(1), or not less than specified
in 430.22(A) through (G).
Decision #1- For Continuous Duty Application: Article 430.6(A)(1) said:430.6 Ampacity and Motor Rating Determination. The
size of conductors supplying equipment covered by Article
430 shall be selected from the allowable ampacity tables in
accordance with 310.15(B) or shall be calculated in accordance
with 310.15(C). …
The required ampacity and motor ratings shall be determined
as specified in 430.6(A), (B), (C), and (D).
[430.6](A) General Motor Applications. For general motor applications,
current ratings shall be determined based on
(A)(1) and (A)(2).
[430.6(A)](1) Table Values. Other than for motors built for low speeds
(less than 1200 RPM) or high torques, and for multispeed
motors, the values given in Table 430.247, Table 430.248,
Table 430.249, and Table 430.250 shall be used to determine
the ampacity of conductors or ampere ratings of switches,
branch-circuit short-circuit and ground-fault protection, instead
of the actual current rating marked on the motor
nameplate.
Decision #2- For Intermittent Duty Application: 430.22(E) said:(E) Other Than Continuous Duty. Conductors for a motor
used in a short-time, intermittent, periodic, or varying
duty application shall have an ampacity of not less than the
percentage of the motor nameplate current rating shown in
Table 430.22(E), unless the authority having jurisdiction
grants special permission for conductors of lower ampacity.
#1 said:... instead of the actual current rating marked on the motor
nameplate.
#2 said:[430.6(A)](1) Table Values. Other than for motors built for low speeds
(less than 1200 RPM) or high torques, and for multispeed
motors, the values given in Table 430.247, Table 430.248,
Table 430.249, and Table 430.250 shall be used to determine
the ampacity of conductors or ampere ratings of switches,
branch-circuit short-circuit and ground-fault protection, instead
of the actual current rating marked on the motor
nameplate.
Is below(Quote #1) what you read and understand from the NEC?
If that's all you grasp, you missed the sentences before it which changes the meaning completely.
Complete language.
Anyways, I'm no helpful here... I'm out!![]()

This is like trying to talk to a Liberal about guns...
Now why did you have to go and do that?
Every coin has two sides. A smart guy like you should know that.