Being a welding receptacle, you can't use the derating from whatever else was planned to be on there to supply it. So if you have a 50A breaker on it, you will need to have #8 CU I believe offhand.
If you reduce that to the appropriate 25-30A breaker, no problem using the #10 wire that's already there since it is larger than the required #14.
I'd take off the cover plate to ascertain wire size. The 50A circuit is just fine if its breakered properly for the wire size. Hopefully its hooked to a #6 awg wire.
I'd take off the cover plate to ascertain wire size. The 50A circuit is just fine if its breakered properly for the wire size. Hopefully its hooked to a #6 awg wire.
Even though welder use only outlets can have smaller conductors than a general use outlet, I highly recommend wiring and over current protecting the circuit as a standard circuit. Which means 50A breaker using #6 NM or #8 THHN in conduit with a 6-50 receptacle.
Yes, I'd make the receptacle a 6-50R, if that's what is supplied with your welder. If not I think you can find appropriate "appliance cord pigtails" at the box stores with that male end already molded onto a short cordset. Could possibly be near appliances as that would be a classic cord for an electric range/oven.