I received my new MillerMatic 211 and need to update my service receptacle and verify wiring in my garage.

With a 50 A breaker can I use #10 wire & NEMA 6-50R?

I currently have a 50 amp circuit service as pictured below but the incorrect receptacle and not sure what my wire is.






 
Last edited:
To avoid these ads, REGISTER NOW!

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
Being a welding receptacle, you can't use the derating from whatever else was planned to be on there to supply it. So if you have a 50A breaker on it, you will need to have #8 CU I believe offhand.

If you reduce that to the appropriate 25-30A breaker, no problem using the #10 wire that's already there since it is larger than the required #14.
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,728
Location
SE Michigan
I'd take off the cover plate to ascertain wire size. The 50A circuit is just fine if its breakered properly for the wire size. Hopefully its hooked to a #6 awg wire.
 
OP
I

isuhunter

Well-known member
Joined
Aug 27, 2011
Messages
532
I'd take off the cover plate to ascertain wire size. The 50A circuit is just fine if its breakered properly for the wire size. Hopefully its hooked to a #6 awg wire.

If its to a #6, would you keep the #6 and replace the receptacle only?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Even though welder use only outlets can have smaller conductors than a general use outlet, I highly recommend wiring and over current protecting the circuit as a standard circuit. Which means 50A breaker using #6 NM or #8 THHN in conduit with a 6-50 receptacle.
 
To avoid these ads, REGISTER NOW!

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,728
Location
SE Michigan
If its to a #6, would you keep the #6 and replace the receptacle only?

Yes, I'd make the receptacle a 6-50R, if that's what is supplied with your welder. If not I think you can find appropriate "appliance cord pigtails" at the box stores with that male end already molded onto a short cordset. Could possibly be near appliances as that would be a classic cord for an electric range/oven.
 
OP
I

isuhunter

Well-known member
Joined
Aug 27, 2011
Messages
532
If I wanted to move the receptacle to the middle of my garage, what size wire would you replace with?
 