Hi guys, I have a 2 stage ingersoll rand 60 gal compressor that I'm looking to temporarily wire in my basement about 10-15 feet from my panel until I get electric ran to my garage which will be a while. I have limited knowledge in electrical and I'm not sure exactly what I need.
From what I have read in my searches on this forum, it is recommended that the compressor is to be hard wired but when I bought it (used by the way) it had a plug. I'm thinking of using this plug for now.
So what would I need as far as wire type and breaker?
Sticker on the motor
[/URL][/IMG]
Plug that it came with
[/URL][/IMG]
[/URL][/IMG]
nadogail
Coronado, CA
You have a 230 volt motor that needs a two pole 30 amp breaker and #10 wire, plus the appropriate twist lock receptacle
pattenp
Virginia - USA
Here's the catch. To be wired NEC compliant being listed as 5HP motor it needs to be hardwired with wire that has a minimum of 35A capacity such as #10 THHN or #8 Nm. 30A plug only has a 3HP rating. It's okay to use 30A breaker, but if you experience startup tripping then up it to a 40A.
Spunks
Ok so I will get a 40A two pole breaker and at least #10 wire. It sounds like hard wiring it would be better which I don't mind doing. I don't want to do any damage to the compressor. Would there be anything else I would need to hard wire it?
U will also need a disconnect if not within sight of and more than 50' from panel.
I tried looking under the "disconnect" section on the home depot website and I'm not sure what I need. Could you recommend one?
The compressor will be about 10-15 feet from my panel, if there was any issue wouldn't the breaker trip at the panel?
aircommuter
Greeley Hill, CA
You might look for an A/C disconnect, just a box with a way to disconnect power, some use a switch , some just a pullout device, those compressors usually have a disconnect at pressure switch that might qualify. It is mainly for you final install, you need a box to connect to anyway, might as well use a disconnet for that purpose.
Spunks
Ok I understand. What amp should I get? 40A or more?
Norcal
A pullout A/C disco comes in 3 flavors, 30A, and 60A, fusible, and 60A non-fusible.
Spunks
I do have this from an old dryer. Would this work?
[/URL][/IMG]
[/URL][/IMG]
The disconnect is for servicing.
But the panel is only 15' away? Is it within sight of the compressor? If so then u dont need a D/C...
Spunks
The compressor will be in a storage room so I wouldn't say within sight no. I don't mind purchasing a D/C if its really recommended
marklc
Not sure you would need a disconnect at all if you are plugging it in? Unless I missed something which is highly possible LOL.
pattenp
Virginia - USA
The plug shown earlier is only rated up to 3HP and should not be used as a disconnect for a 5HP motor.
Not only is it recommended but it is required by code since the compressor is not within sight of the panel...
Spunks
Ok picked up a 40A two pole breaker, 60A non-fusible D/C. I have 10/2 and 10/3 wire at home that I want to use. A neutral is not needed in this application correct?
brewchief
No neutral but #8 wire should be used if nm(romex), you can use #10 if thhn wire in conduit. A short section of flexible conduit with #10 thhn wire in it can be used to connect to the compressor from the disconnect, can be purchased ready to go as an A/C whip and is often cheaper to buy that way then as individual parts and pieces.
Spunks
Ok I will look into that
Spunks
Hey guys got it wired up. I ended up using the #8 gauge romex, 60amp D/C, and A/C whip. After more searching on here I learned that THHN wire is better but my local HD only had 500' rolls. I don't need anything near that so I grabbed the cheaper romex (125').
I have been reading about plumbing for it as well so thats next. Whats there is temporary.
[/URL][/IMG]
thanks for the help guys:thumbup:
Spunks
Cool basement. Guessing you live in the Northeast.
Haha yes sir. Originally thought of keeping the compressor in the garage but now I think its a good idea in keeping it in the basement where its cooler and pipe the air to the garage.