My Bro-in-law just bought a Kobolt 80 gallon 2 stage compressor. The problem is it keeps tripping the breaker. Its a 230 v 22F.L.A 5 HP motor. We have #10 wire about 9 ft long and a double 30 breaker. The breker is new but hes going to get another just in case its that. What else can cause this? I had a Husky that was the same and i needed to buy some kind of starter for it that had heaters. Could this be the problem?
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!
OP
D

dawgee

Well-known member
Joined
Mar 28, 2012
Messages
1,035
Location
rhode island
Thanks for the help guys it needs a line starter , its what i suspected but wasnt sure what it was called.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,750
Thanks for the help guys it needs a line starter , its what i suspected but wasnt sure what it was called.

The lack of a mag starter is not why the breaker is tripping, the breaker is too small and it needs wiring rated for 35A if the conductors are THHN they are, but if NM cable needs to be at least 8AWG. The NEC requires that motor circuits be sized by 125% of the tables in article 230 not nameplate amperes, which for a 5 HP single phase motor is 35A. A 40 or 50A breaker would be appropriate.
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,687
Location
NW Iowa
40 or 50a breaker is a good size for a 5 hp motor, NEC allows up to 70A breaker for a 5hp. 30A is definitely to small.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Thanks for the help guys it needs a line starter , its what i suspected but wasnt sure what it was called.

Youre confused about what a mag starter does.

The abscence of one would not alter the trip curve spec of the breaker.

As said above, the 30a breaker is too small.

Motors and inductive lods have whats called in-rush current which occurs on startup. In-rush current can be 4x-8x the FLA.

This is why the breaker is tripping.

BTW this unit needs to be hardwired unless you use pin and sleeve connectors...
 