Help with Fan control and lights/outlet

realred2

Member
Joined
Jan 1, 2009
Messages
22
I'm going to be installing a Fan and lights in my garage and would like to run them from the ceiling outlet (for the door opener, thats not being used) I want to put in a 3 gang box with Fan control, then light switch, then outlet as there is currently only a single outlet in the garage. I think if I run 14-2 from the ceiling outlet to the Fan outlet, then 14-3 from fan to 3gang box, I can get everything working right. Does this sound like it will work to everyone else?
Ceiling outlet ..............Fan.................... Switches/outlet on wall
black...........to........black(bypass fan).............to fan switch (and pigtailed to others)
white...........to..............white.......................to white for outlet
##........................Red to black on fan............to switched out put

And a second line of 14/2 for the lighting off the light switch?

Maybe this helps... yellow = white line/nuetral
fanlightoutlet.jpg


Any help?
 
To avoid these ads, REGISTER NOW!
OP
R

realred2

Member
Joined
Jan 1, 2009
Messages
22
it is a 20, and I ran 12-3 and 12-2 from the outlet to fan, to switch and new outlet. I did run 14-2 to the new light though.
 
OP
R

realred2

Member
Joined
Jan 1, 2009
Messages
22
Can I ask why? I know the lights not going to be pulling enough for it to need 12-2. it's a in-ceiling can with a 15 watt lamp (CFL) And will have 2 more with it eventually, but thats not enough to need #12 wire.
 
To avoid these ads, REGISTER NOW!

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
beacause all wiring in the ckt must be rated for the breaker size.in your case 20 amp and #12.
 

Sokoloff

Well-known member
Joined
Jun 11, 2005
Messages
400
Location
Cambridge, MA
Concur with oleguy and torque. The reason is that the breaker protects the wire (or protects the structure from a fire caused by the wire). In your situation, 14 guage is rated for 15 A, so suppose there were a sustained overload (partial short or overload) drawing 18A. The breaker won't ever trip, the 14 guage will overheat, bad situation...

Your next question might be "Can I just replace the breaker with a 15A breaker?" and my answer would be "No, because the next guy might see the first wire is 12-2 and decide to upgrade the breaker back to 20A." I can't recall if that's what the NEC says as well, or if it just seemed a good practice (to avoid doing that).
 

Torque1st

MEMBER EMERITUS
Joined
Sep 14, 2008
Messages
5,668
Location
KC Metro, Kansas
Concur with oleguy and torque. The reason is that the breaker protects the wire (or protects the structure from a fire caused by the wire). In your situation, 14 guage is rated for 15 A, so suppose there were a sustained overload (partial short or overload) drawing 18A. The breaker won't ever trip, the 14 guage will overheat, bad situation...
The next owner may install some high draw equipment like a little space heater that he wants to go on and off with the lights and extends that light wire. Or a wire is penetrated by a screw or nail (I did it myself once) shorting it. ALL the wire in that circuit must be rated for the breaker capacity, -except wiring specifically exempted by the NEC, like short pigtails of fixture wire inside of a UL light fixture that is covered by other sections of the code.
 