Ok guys, I need some help...
A few weeks ago, I bought a Husky 60 Gallon compressor from HD to put in my basement workshop , got it down to the basement and put it under the stairs. Last weekend I did all the wiring and went to turn it on and got nothing... No hum, nothing...
http://www.homedepot.com/p/Husky-60-Gal-Stationary-Electric-Air-Compressor-C602H/205389936
I have done my a fair share of electrical wiring in the past so I'm comfortable with it and it isn't new to me. When I setup my basement shop I ran 5 new breakers/circuits. 1-30A 230V for my table saw and welder, 2-20A circuits for receptacles to power tools, 2-15A circuits one for lights and the other for receptacles.
Wiring details:
Ran a dedicated 230V line & breaker (12/2 on a 20A two pole GE slim/wafer breaker, 2 hots & a ground) The manual recommends a minimum 20A breaker and say it pulls around 16amps). It's about 20-25' from the panel. I ran the 12/2 romex to a box on the wall right by the compressor with 2.5' long 12g stranded pigtail from the pressure switch on the compressor into the box.
When the compressor wouldn't run, I tested the voltage at various points along the run. With the breaker on, I get approximately 130V on each leg at the box on the wall. I get the same voltage on each leg at the pressure switch. testing at the terminals going into the motor, With the pressure switch in the on/auto position, I get the same voltage. With the pressure switch off, I get 0 volts on each leg. Seems like I'm getting voltage all the way to the motor.
Upon this, I called "Husky" (Mat Industries), spoke with their "electrical guy" told him the testing I did and he says I probably have a bad motor. He did say that they recommend a 10/2 and a 30A breaker due to nuisance tripping when the motor turns on under load but he said the 20A should "work". I responded and said their manual mentions nothing of that and recommends a 20A breaker. I'm not arguing the point and I don't mind switching to a 30a breaker if need be, just stating they should probably put that in the manual.
You would think that if 20 was too small for the amperage when the motor kicks on, it would just trip the breaker. I'm getting nothing...
After speaking with Mat industries, The HD store manager agreed to send a couple guys to bring me a new compressor and take the "bad" one away since I don't live far from the store. Last night they swapped them out. I wired up the new one and still get nothing... Could I have another bad compressor motor? Or am I doing something wrong? or a bad breaker? I'm stumped...
Should I move up to a 30A breaker? I thought about taking the lead/plug off my welder and wiring it up to plug the compressor into that 30A Circuit since it's on that same wall and I know it works.
A few weeks ago, I bought a Husky 60 Gallon compressor from HD to put in my basement workshop , got it down to the basement and put it under the stairs. Last weekend I did all the wiring and went to turn it on and got nothing... No hum, nothing...
http://www.homedepot.com/p/Husky-60-Gal-Stationary-Electric-Air-Compressor-C602H/205389936
I have done my a fair share of electrical wiring in the past so I'm comfortable with it and it isn't new to me. When I setup my basement shop I ran 5 new breakers/circuits. 1-30A 230V for my table saw and welder, 2-20A circuits for receptacles to power tools, 2-15A circuits one for lights and the other for receptacles.
Wiring details:
Ran a dedicated 230V line & breaker (12/2 on a 20A two pole GE slim/wafer breaker, 2 hots & a ground) The manual recommends a minimum 20A breaker and say it pulls around 16amps). It's about 20-25' from the panel. I ran the 12/2 romex to a box on the wall right by the compressor with 2.5' long 12g stranded pigtail from the pressure switch on the compressor into the box.
When the compressor wouldn't run, I tested the voltage at various points along the run. With the breaker on, I get approximately 130V on each leg at the box on the wall. I get the same voltage on each leg at the pressure switch. testing at the terminals going into the motor, With the pressure switch in the on/auto position, I get the same voltage. With the pressure switch off, I get 0 volts on each leg. Seems like I'm getting voltage all the way to the motor.
Upon this, I called "Husky" (Mat Industries), spoke with their "electrical guy" told him the testing I did and he says I probably have a bad motor. He did say that they recommend a 10/2 and a 30A breaker due to nuisance tripping when the motor turns on under load but he said the 20A should "work". I responded and said their manual mentions nothing of that and recommends a 20A breaker. I'm not arguing the point and I don't mind switching to a 30a breaker if need be, just stating they should probably put that in the manual.
You would think that if 20 was too small for the amperage when the motor kicks on, it would just trip the breaker. I'm getting nothing...
After speaking with Mat industries, The HD store manager agreed to send a couple guys to bring me a new compressor and take the "bad" one away since I don't live far from the store. Last night they swapped them out. I wired up the new one and still get nothing... Could I have another bad compressor motor? Or am I doing something wrong? or a bad breaker? I'm stumped...
Should I move up to a 30A breaker? I thought about taking the lead/plug off my welder and wiring it up to plug the compressor into that 30A Circuit since it's on that same wall and I know it works.