Here's some info to educate yourself.
Info from:
http://www.jcrproductions.com/
Basic Motor Overcurrent Selections Using An Inverse Time Breaker On A 5 h.p., 230 Volt, Single Phase Motor.
When it comes to overcurrent protection for motors, the rules for sizing the protective device as stated in Article 240 are not applicable. When you are working with motors and motor circuits you are dealing with a "different animal" as compared to other resistive loads and their supply circuits. Motors do not always draw a constant or steady amperage as resistive loads normally do. Therefore, with the exception of torque motors, (as given in 430.52(D)) overcurrent protective devices are rated or set according to the values given in Table 430.52 for the device to be used.
For our single phase motor rated 5 h.p. and 230 volts, Table 430-248 states that the amperage to be considered for this motor is to be 28 FLA (full load amperes). Having determined the FLA, it is now time to follow the requirements of section 430.52(C)(1). This section tells us that when sizing our overcurrent device for our motor, we are not to exceed the values as given in Table 430.52. When using an inverse time breaker for the overcurrent protective device, the value given in the table to be used is not to exceed 250% of the motors full load current rating. In order to size the overcurrent device, this percentage is to be simply multiplied by the motor's full load current rating or FLA as shown in the following calculation:
The current rating of our motor is 28 amperes. Therefore, 28 amperes X 250% = 70 amperes
Based on this calculation, an inverse time breaker would be installed in this motor circuit at a maximum initial rating of 70 amperes.
Earlier in this article, motor circuit calculations were referred to as a "different animal". We will now expose the reason for this descriptive statement. We have determined by calculation that the inverse time breaker used for this motor, and its condition of use, is to be rated at 70 amperes. Using the branch circuit calculation requirements of 430.22(A), we find that our minimum permitted branch circuit conductor size (using 430.22(A), Table 310.16, and 110.14(C)(1)(a)(4)) is a #10 THW. Some contractors and inspectors who are operating within the general overcurrent guidelines of Article 240 find a #10 THW supplied by a 70 ampere breaker to be Unacceptable, Incorrect, or just plain SCARY! This can only be due to a lack of understanding with respect to the relationship between overload and overcurrent devices and their respective duties.
Just to set the record straight, in this motor circuit, not only is a 70 ampere breaker supplying the #10 THW conductor acceptable code, IT IS PERFECT CODE!
In closing, the relationship between overload and overcurrent protection in motor and motor compressor applications will be presented in a separate article in the near future. For those who may want an advance peek into this future article please review section 430.31 and remember.... there is more here than meets the eye!
Relax and have fun with your new motor overcurrent knowledge, and in your motor and motor compressor circuits STOP protecting your conductors in accordance with their ampacities as stated in section 240.4. IT DOES NOT APPLY TO MOTOR APPLICATIONS!