I bought a used Quincy Air Compressor with a 220 steping down to a 110 I think. My old unit had a 20 amp fuse- can anyone tell me how to size the unit for the main line?
I fear I have only 3 wires and will need a 4th that will be not only a pain but expensive.
Any help and ideas would be wonderful
Ron
 
To avoid these ads, REGISTER NOW!

GeorgiaHybrid

Well-known member
Joined
Sep 9, 2008
Messages
3,763
Location
Extreme NW Georgia
Why do you think it steps down to 110 from 220? Can you post pictures of the motor plate? Does it have a mag starter? If yes, pictures there also. Include a photo of the pressure switch also.

Either way if it is 220, all you need are 3 wires. The pressure switch side might run a 110 leg thru the mag starter but I can't see the need for a neutral and a ground to be able to run 110.
 

mmg440

Well-known member
Joined
Oct 24, 2008
Messages
360
Location
Dixion, Missouri
Maybe even a 3 phase. That you would need more then just a wire. I am sure there are memeber that can help sizing but first it will have to be idenified for what it is. This doesn't make sence to me "...220 steping down to a 110..." Don't really know what you are tring to say with that.



:needpics:
 
To avoid these ads, REGISTER NOW!

GeorgiaHybrid

Well-known member
Joined
Sep 9, 2008
Messages
3,763
Location
Extreme NW Georgia
So is 10-2 with ground ok for most compressor installs? Or do you need 10-3 for some reason for just single phase?

For most home compressors, that would work. For higher HP motors or long runs of wire, you might need to go up a size to 8 GA wire.

10-2 with ground is all you need for a 220 circuit. If you are running to a sub-panel or if you plan on adding a 110 accessory to the compressor (110 volt hour meter for example) the extra wire will be required and you will need 10-3 with ground or separate wires in conduit.
 

Dragster Racer

Well-known member
Joined
Feb 9, 2008
Messages
1,891
Location
Morrison, IL
We can't recommend a wire size until we know the load. What size compressor motor are you trying to insall?

I understand that. I was more curious about the number of wires. I ran 4 for a dryer circuit, but I understand that some dryers run 110V controls, thus the need for the fourth wire. I ran 10-2 yesterday for the future compressor, which won't need more than 30 amp circuit, and I wanted to make sure I did the right thing.
Thanks for the responses.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
For my 3 1/2HP unit I used regular 12-2/wG. For a 220 Motor, you only need two wires and a safety ground. As noted, wire size depends on load and run length.
 