Help with radiant floor heat

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,223
Location
Arkansas
Here is a pic of my current plan. I already have the water heater, ex tank, fan coil, manifolds, and of course tubing in the floor. Our frost line here in Northern Arkansas is 18" and about 1/2 my floor is below that cause I cut into the hillside. 1" styrofoam under the concrete with reflective foil backing facing down. I plan on using only the floor OR the fan coil but NOT both at once, hence the shutoffs at the Tees. Just wanting to keep the shop 55-60 but possibly sometimes blow hot air directly towards work area via the fan coil. I will use a standard thermostat of some sort and a couple common relays for controlling the pumps. My questions are......Am I missing anything component wise? Which pump do I need for the main floor tubing?
 

Attachments

  • SUNP0385.jpg
    SUNP0385.jpg
    101.5 KB · Views: 127
To avoid these ads, REGISTER NOW!

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,436
Location
N CA
Not sure what the mix ratio will be, but you are going to be in for a lot of glycol on that system. I would drop the glycol and run water. Glycol seems to offer advantages, but it must be monitored and maintained or it can screw up a system over time. It is not a "one and done" type component. If you feel the slab absolutely has to have it add a small plate hx and treat only the slab/AH portion. Before I used glycol I'd install a supplemental DV heater for back-up. Glycol adds to the viscosity of the fluid and requires more circulator. Component wise you might want to consider a Watts pressure reducing/relief combo unit on the feed.
 
OP
P

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,223
Location
Arkansas
Oops!! That should say Propylene glycol mix. I had an old water source heat pump given to me and the tank has about 30 gallons in it.
This is closed loop and I plan to pressureize 10-15 psi.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,436
Location
N CA
Old HP...old glycol? Check the ph prior to putting it into your system.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,034
Location
Peace Valley,mo
To accurately pick a pump need to know size and length of pipe. Also what type of pex is it? With or without the oxygen barrier.
 
OP
P

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,223
Location
Arkansas
Yes, oxygen barrier pex. Specs are on my pic above....4 loops 1/2" 300ft each setup as a single zone.
 

Copymutt

Well-known member
Joined
Sep 3, 2016
Messages
3,455
Location
Colorado
24 yrs on a closed loop water only system.NG. One of the best investments i ever made. We get much colder here. Occasionally minus teens for several days.
I do have a hanging 35k heater also, but never needed to use it to keep the in floor from freezing. Its been bullet proof.
 
To avoid these ads, REGISTER NOW!

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,034
Location
Peace Valley,mo
1200' 1/2" pex = 11 gallons of water add another 2 gallons for boiler and fan coil 13 gallons. 4 gallons of glycol 30%. I wouldn't use used glycol because you don't know what the additives levels are. Fan coils don't put out much heat under 120*. Floor heat water temps run 5-10* over thermostat setting. Piping pex floor loops the two manifolds pipe a-b-c-d supply d-c-b-a return that will give you equal flow through the loops. To pipe system correctly with the fan coil a primary secondary loops would have done. Since the floor piping flow rate is 3.6 gpm @ 10k btu's per gallon your close to the out put of the water heater. Might just try just the floor.
 

86turbodsl

Well-known member
Joined
Jul 1, 2005
Messages
6,565
Location
Michigan
If you're going to run a HX, you might look at methanol as your antifreeze. cheap and doesn't degrade like glycol. Pumps easier too. poisonous though, so take your precautions.
 
OP
P

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,223
Location
Arkansas
A friend of mine gave me a Grundfos UP26-99f pump. Will this work fine on the floor or is it too much pump?
 
OP
P

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,223
Location
Arkansas
Thanks, I'll see if I can trade this one for an 008. Some more hvac guys I know use that one on the Hardy outdoor wood furnace.
 