I have a Reznor UDAS that's almost done. Tstat is Honeywell Vision pro 8320U (saved from prior hvac system).
I have a 24 v transformer.
Reiznor is single stage and Reznor takes G, W and R wires. G - fan, w - gas valve?, R - ?
Now, how to wire the tstat?
Per the tsat manual for a heat only system:
Rc - power
R - (Rc and R joined by jumper)
W - heat relay
C - 24vac common
So do I wire from the 24 v transformer to the c and R terminals on the tsat?
Then do I run an R wire to the reznor?
I know the G and W wires run from tsat to Reznor. Reznor manual does not make clear what the R controls. Perhaps I don't need a separate transformer, as the circuit diagram does show a 24 v transformer on the reznor. Doe this supply 24 v to the tsat?
I also see a Reznor note about setting the tsat heat anticipator to 0.6 amps. I see nothing in the tstat manual about heat anticipator; the closest I see is that the electrical ratings of the terminals are:
W - heating, 0.02 to 1.0 amps
W2 - heating - 0.02 to 0.6 amps
Can anyone help with these questions?
Thanks,
Tom
I have a 24 v transformer.
Reiznor is single stage and Reznor takes G, W and R wires. G - fan, w - gas valve?, R - ?
Now, how to wire the tstat?
Per the tsat manual for a heat only system:
Rc - power
R - (Rc and R joined by jumper)
W - heat relay
C - 24vac common
So do I wire from the 24 v transformer to the c and R terminals on the tsat?
Then do I run an R wire to the reznor?
I know the G and W wires run from tsat to Reznor. Reznor manual does not make clear what the R controls. Perhaps I don't need a separate transformer, as the circuit diagram does show a 24 v transformer on the reznor. Doe this supply 24 v to the tsat?
I also see a Reznor note about setting the tsat heat anticipator to 0.6 amps. I see nothing in the tstat manual about heat anticipator; the closest I see is that the electrical ratings of the terminals are:
W - heating, 0.02 to 1.0 amps
W2 - heating - 0.02 to 0.6 amps
Can anyone help with these questions?
Thanks,
Tom