@Pattenp- Yeah really, considering the fact the OP was already having a hard time keeping track off all the different options he could go with!
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I thought so. I know you know what you're doing from all your posts and just thought it was a typo. Others on here may misread that and think they can put regular romex in conduit though!

We should also steer away from using "Romex" as a wire type because it's a brand of NM.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I hope I don't regret this, but if you run conduit from house panel to jbox in barn and use individual THHN/THWN wires, you could use #8 aluminum and save some $$$. Aluminum is about a third of the cost of copper. You can use 2 #8 and 1 #10 and you could get by with 3/4 PVC conduit.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
We should also steer away from using "Romex" as a wire type because it's a brand of NM.

Good point! Agreed!

I hope I don't regret this, but if you run conduit from house panel to jbox in barn and use individual THHN/THWN wires, you could use #8 aluminum and save some $$$. Aluminum is about a third of the cost of copper. You can use 2 #8 and 1 #10 and you could get by with 3/4 PVC conduit.

LoL! I think u might be confusing the poor guy again!
 
OP
T

Todd.Brock

Well-known member
Joined
Jul 15, 2008
Messages
4,249
Location
Cincinnati
I am Confident in my ability to execute but like to talk out loud if I'm not 100% sure on the plan. Sorry if I have talked this to death!!

I ended up running a 30 amp 240v circuit in the garage for the compressor. I couldn't figure out a way to run the air line underground without a big *** trench and a bunch of filters and dryers. This is for storage, so I just need some lights and a couple of receptacles.
 
OP
T

Todd.Brock

Well-known member
Joined
Jul 15, 2008
Messages
4,249
Location
Cincinnati
Results are in, 120.8 volts at outlet with only a ~20 watt CFL and timer for a chicken coop. Dips to 113 with 900 watts, 110 with 1200 worth of heater. All this on 55 feet of 14 gauge.

However an additional 26 watts of CFL (my shed light setup) results in a mere 0.1 volt drop. ;)

Good bad or ugly (probably the latter two) there are your numbers. :D

Thank you for taking the time to do that. I appreciate it. Hopefully the 10ga will be more than enough to compensate!
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
I am Confident in my ability to execute but like to talk out loud if I'm not 100% sure on the plan. Sorry if I have talked this to death!!

I ended up running a 30 amp 240v circuit in the garage for the compressor. I couldn't figure out a way to run the air line underground without a big *** trench and a bunch of filters and dryers. This is for storage, so I just need some lights and a couple of receptacles.

No, u didn't talk it to death. This stuff can get complicated with all the possible variables! We've given u a # of options! Now you've gotta pick ur poison! :D

Thank you for taking the time to do that. I appreciate it. Hopefully the 10ga will be more than enough to compensate!

Believe it or not, there's actually a formula for calculating voltage drop. So u don't have to test a particular wire with a load to figure out what the VD will be!
 
Last edited:

cafyrman

Well-known member
Joined
Aug 21, 2011
Messages
76
Location
Poway, CA
I am Confident in my ability to execute but like to talk out loud if I'm not 100% sure on the plan. Sorry if I have talked this to death!!

Don't worry about that. The beauty of a forum is that others can learn. I know I learned a few things in this thread that will be helpful to me.
 
OP
T

Todd.Brock

Well-known member
Joined
Jul 15, 2008
Messages
4,249
Location
Cincinnati
Ok. Guys, my neighbor and I are renting a trencher on Friday. It runs 63 bucks for 3 hours. 12" deep and 2.5 inches wide. Perfect. I ordered 125 ft of 10-2 UF at .85/ft. Fortunately he is trenching too so we can split the cost. Anyway, I'm going to stick it in 1" PVC just for an extra measure of cheap insurance. Attached is a crude diagram of the inside. Other than the drawing skills any flaws with the plan? Thanks!ImageUploadedByTapatalk1349315953.060793.jpg
 
OP
T

Todd.Brock

Well-known member
Joined
Jul 15, 2008
Messages
4,249
Location
Cincinnati
I am using a 20 a breaker so I planned to use 12ga THHN in conduit within the building. I will also be using a single pole switch At the entry point to serve as the disconnect. Is that an ok plan?
 

jpinca

Well-known member
Joined
Sep 23, 2011
Messages
225
Location
NorCal
I guess too late, but I'd go with the 240v option. Nothing says you have to use it, but next year when you want to run the compressor or mig out there, you'll be glad you did.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I am using a 20 a breaker so I planned to use 12ga THHN in conduit within the building. I will also be using a single pole switch At the entry point to serve as the disconnect. Is that an ok plan?

Yeah, all's okay. I know you said 20A in your first post, so my question was a test question. :evil:
 
OP
T

Todd.Brock

Well-known member
Joined
Jul 15, 2008
Messages
4,249
Location
Cincinnati
Yeah it's too late. This is just a storage shed. The mig and compressor are in the garage. Technically I could run my 110 mig and compressor out there. Pattenp, thanks for keeping me honest,
 