If I was going to the expense of 10 wire would use 3 conductor but now its not such a simple circuit.
I'd hate to throw that in the mix.

If I was going to the expense of 10 wire would use 3 conductor but now its not such a simple circuit.

If I was going to the expense of 10 wire would use 3 conductor but now its not such a simple circuit.
I thought so. I know you know what you're doing from all your posts and just thought it was a typo. Others on here may misread that and think they can put regular romex in conduit though!
We should also steer away from using "Romex" as a wire type because it's a brand of NM.
I hope I don't regret this, but if you run conduit from house panel to jbox in barn and use individual THHN/THWN wires, you could use #8 aluminum and save some $$$. Aluminum is about a third of the cost of copper. You can use 2 #8 and 1 #10 and you could get by with 3/4 PVC conduit.
Results are in, 120.8 volts at outlet with only a ~20 watt CFL and timer for a chicken coop. Dips to 113 with 900 watts, 110 with 1200 worth of heater. All this on 55 feet of 14 gauge.
However an additional 26 watts of CFL (my shed light setup) results in a mere 0.1 volt drop.
Good bad or ugly (probably the latter two) there are your numbers.![]()
I am Confident in my ability to execute but like to talk out loud if I'm not 100% sure on the plan. Sorry if I have talked this to death!!
I ended up running a 30 amp 240v circuit in the garage for the compressor. I couldn't figure out a way to run the air line underground without a big *** trench and a bunch of filters and dryers. This is for storage, so I just need some lights and a couple of receptacles.
Thank you for taking the time to do that. I appreciate it. Hopefully the 10ga will be more than enough to compensate!
I am Confident in my ability to execute but like to talk out loud if I'm not 100% sure on the plan. Sorry if I have talked this to death!!

I am using a 20 a breaker so I planned to use 12ga THHN in conduit within the building. I will also be using a single pole switch At the entry point to serve as the disconnect. Is that an ok plan?