Help with wiring size for 2 post lift?

Dr_Pippin

Well-known member
Joined
Feb 23, 2023
Messages
101
Had a plan for wiring up my 2 post, but a friend just pointed out I might consider a change. My original plan was 10 gauge NM-b for the motor and 12 gauge NM-b for a 20 amp circuit mounted on the post. I finally looked at the motor plate and saw it’s a 3hp motor. A friend suggested instead wiring the motor to the 12 gauge and instead using the 10 gauge for a welder outlet. Going to the ol’ google and searching the wiring requirement for a 3hp motor, I’ve found about five different “definitive” answers on other forums. Can someone give me a sixth definitive answer on if I can run my lift motor on 12/2 Romex with a 20 amp breaker? I feel like this motor plate is missing information.

IMG_6994.jpeg
 

Attachments

  • IMG_6994.jpeg
    IMG_6994.jpeg
    736 KB · Views: 21
To avoid these ads, REGISTER NOW!

ratflinger

Well-known member
Joined
Jul 7, 2016
Messages
322
Location
South Central Texas
Found it. Bucher lists it as a 2.2kw unit, so at 240v you'll pull just under 10a. I'd use 12ga, but that's me.
 

Attachments

  • 2024-04-02_21-48-46.png
    2024-04-02_21-48-46.png
    101 KB · Views: 22
Last edited:
OP
D

Dr_Pippin

Well-known member
Joined
Feb 23, 2023
Messages
101
Difficult to say since they didn't bother to spec the amp load. A lift motor from Derek Weaver in this size & ETL cert requires a 30a feed. While #10 will handle the amps I believe code says 80%, so you would need #8. You need to go back to the manufacturer and have them provide the amp load so you can size the circuit correctly. Even if it turns out to be only 20a, I'd use #10 only.
Thanks for confirming that not all the necessary info is on the motor plate. This is my first time trying to read a plate, so I didn’t know if I was missing something or if it just wasn’t all there. I’ll call the lift company tomorrow (Advantage).
 
OP
D

Dr_Pippin

Well-known member
Joined
Feb 23, 2023
Messages
101
Found it. Bucher lists it as a 2.2kw unit, so at 240v you'll pull just under 10a. I'd use 12ga, but that's me.
Thank you for finding and sharing that info. Didn’t occur to me to search for the motor specifically.

I will use 12 ga for the lift, and take my friend’s suggestion of using the 10 ga for a welder outlet. Thank you!
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,785
Location
Richmond, VA
The NEC requires wiring it based on the nameplate HP rating. A 3hp motor is listed at 17a @ 240v, then you uprate it 125% for wire sizing and get 21a. So that would mean #10 nm-b or #12 thhn in conduit..
The reality is that at a 2.2kw draw, it's not really 3hp, so I expect it would run fine on 12 nm-b, but it's not code compliant

1712129255581.png

If you want a welder outlet, 10nm-b will work for welders up to about a 50% duty cycle. 12 is good for something like a 35% duty cycle.
 
Last edited:
OP
D

Dr_Pippin

Well-known member
Joined
Feb 23, 2023
Messages
101
The NEC requires wiring it based on the nameplate HP rating. A 3hp motor is listed at 17a @ 240v, then you uprate it 125% for wire sizing and get 21a. So that would mean #10 nm-b or #12 thhn in conduit..
The reality is that at a 2.2kw draw, it's not really 3hp, so I expect it would run fine on 12 nm-b, but it's not code compliant

1712129255581.png

If you want a welder outlet, 10nm-b will work for welders up to about a 50% duty cycle. 12 is good for something like a 35% duty cycle.
And this is why I found so many different answers searching online. Thank you. From what you shared, I understand using 12 ga wire for the lift motor doesn’t meet NEC, but seeing as it’ll be the only thing on the circuit and will have very short run times I’m comfortable using 12 ga.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,785
Location
Richmond, VA
Make sure you have a disconnect of some sort at the lift. We've seen too many stories of contactors sticking closed and guys unable to shutdown a lift. A 30a dual pole switch is cheap insurance.
 

TxSteve

Well-known member
Joined
Aug 22, 2023
Messages
121
Location
Granbury, Texas
You said it's a 20 amp circuit. 20 amp requires 12 gauge for runs < ~50 ft depending on what's acceptable voltage drop.

I'd use 12/2 and move on. You can use 10 if it will make you feel better - it's only money ;)
 
OP
D

Dr_Pippin

Well-known member
Joined
Feb 23, 2023
Messages
101
Make sure you have a disconnect of some sort at the lift. We've seen too many stories of contactors sticking closed and guys unable to shutdown a lift. A 30a dual pole switch is cheap insurance.
I’ve got one in hand. Thank you for suggesting.
You said it's a 20 amp circuit. 20 amp requires 12 gauge for runs < ~50 ft depending on what's acceptable voltage drop.

I'd use 12/2 and move on. You can use 10 if it will make you feel better - it's only money ;)
I didn’t know for sure it was a 20 amp circuit. I had to run wires from the sub panel into the attic before I completed drywall, so I ran 10 ga to be sure I was covered no matter what the lift ended up needing. Now I’m considering repurposing that 10 ga for a welder outlet and using the 12 ga for the lift instead of for a 20 amp outlet as I had initially planned. Got a whole bunch of outlets on the wall on the other side of the lift, so don’t know how critical this one would actually be for my regular usage.


And an answer from Advantage Lifts:
Hello,



The motor plate should state the FLA (fully loaded amperage) at 15.9A.

You will need to run a 20A breaker for this.
 

TxSteve

Well-known member
Joined
Aug 22, 2023
Messages
121
Location
Granbury, Texas
I’ve got one in hand. Thank you for suggesting.

I didn’t know for sure it was a 20 amp circuit. I had to run wires from the sub panel into the attic before I completed drywall, so I ran 10 ga to be sure I was covered no matter what the lift ended up needing. Now I’m considering repurposing that 10 ga for a welder outlet and using the 12 ga for the lift instead of for a 20 amp outlet as I had initially planned. Got a whole bunch of outlets on the wall on the other side of the lift, so don’t know how critical this one would actually be for my regular usage.


And an answer from Advantage Lifts:
Sounds like a good plan. Don't waste a 30 amp circuit on a 20 amp draw.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,061
Location
Modesto, CA
You said it's a 20 amp circuit. 20 amp requires 12 gauge for runs < ~50 ft depending on what's acceptable voltage drop.

I'd use 12/2 and move on. You can use 10 if it will make you feel better - it's only money ;)
the motor is NOT a 20a circuit. thats not even how a motor circuit is sized.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,061
Location
Modesto, CA
I don't follow. The MFG states a 15.9 amp draw and a 20 amp circuit which requires 12 gauge wire.

That's not how motor circuits are sized under the NEC. The manufacturer is wrong and should stop labeling the motor as 3hp, then
The NEC FLC table lists 3hp as 17a so a motor with a 15.9a FLA is about right for 3HP.... regardless, if the motor nameplate says 3HP, it needs to be wired with 21a rated wire (17a x 125%)
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,785
Location
Richmond, VA
The NEC FLC table lists 3hp as 17a so a motor with a 15.9a FLA is about right for 3HP.... regardless, if the motor nameplate says 3HP, it needs to be wired with 21a rated wire (17a x 125%)
You're right, I had the 2.2kw figure in mind from earlier and didn't really think of the 15.9 fla
 

ratflinger

Well-known member
Joined
Jul 7, 2016
Messages
322
Location
South Central Texas
@wyliesdiesels - Please explain. The motor is listed on the label as 3hp, but in the pdf I posted the motor is rated at 2.2kw with no mention of HP. If what you say is true (not doubting you) then the motor should be listed as a 4kw. So why the confusion here? Is the motor not really a 3hp or is the rating posted wrong?
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,785
Location
Richmond, VA
@wyliesdiesels - Please explain. The motor is listed on the label as 3hp, but in the pdf I posted the motor is rated at 2.2kw with no mention of HP. If what you say is true (not doubting you) then the motor should be listed as a 4kw. So why the confusion here? Is the motor not really a 3hp or is the rating posted wrong?
The nameplate matters, a pdf doesnt
 

TxSteve

Well-known member
Joined
Aug 22, 2023
Messages
121
Location
Granbury, Texas
Honest question - I thought the 125% upsizing was for continuous duty use. Is that not right?

I'm surprised the motor plate doesn't have FLA listed...
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
PDF was from was an official doc from the manufacturer, shouldn't they match?
The manufacturer of the lift is not the manufacturer of the motor. The catch is the NEC specifies to use the motor HP if listed on the motor data label to determine supply conductor size. But if the lift manufacturer gives instructions stating required conductor size and overcurrent protection, then that's what you use.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,021
Location
NJ
The NEC requires you to size the motor conductors based off a specified amperage listed in table 430.248 found by looking up the stated hp of your motor.

You no longer simply use the motor FLAs from the nameplate.

Once you have the value from the table, add 25% to it to determine wire size.

BTW 1hp = 746watts....2.2kw = 3hp.
 
Last edited:

ratflinger

Well-known member
Joined
Jul 7, 2016
Messages
322
Location
South Central Texas
The manufacturer of the lift is not the manufacturer of the motor. The catch is the NEC specifies to use the motor HP if listed on the motor data label to determine supply conductor size. But if the lift manufacturer gives instructions stating required conductor size and overcurrent protection, then that's what you use.
The PDF in question was from the motor manufacturer, Bucher Hydraulics. What I don't understand is why a motor rated for 2.2kw requires more power and a larger gauge wire than a 2.2kw load would seem to need. I'm not an electrical engineer.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,021
Location
NJ
I believe the NEC doesn't require the 25% addition if the motor is used in a non continuous application such as a lift.
Agreed. In this case it would be hard to consider it continuous duty. 430.22E allows from 85% to 140% of FLAs depending on motor service rating - which we don't know.

I'd call it good with 12-NM-B. (It's 90C wire anyway. 🤫)
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
Honest question - I thought the 125% upsizing was for continuous duty use. Is that not right?

I'm surprised the motor plate doesn't have FLA listed...
To size the circuit conductors you have to use the value listed in NEC article 430 in the table shown in that article for the type motor of being used, plus 125%, NOT the nameplate value. Still out of State until early Friday morning so still don't have access to my code books to make it more specific.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,021
Location
NJ
Honest question - I thought the 125% upsizing was for continuous duty use. Is that not right?

I'm surprised the motor plate doesn't have FLA listed...
The footnote in NEC 430.22E states all motors are treated as continuous unless its use meets the exceptions in 430.22E.

Kind of bazzar w/o FLAs on the nameplate. But hey, it's from china.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
To size the circuit conductors you have to use the value listed in NEC article 430 in the table shown in that article for the type motor of being used, plus 125%, NOT the nameplate value. Still out of State until early Friday morning so still don't have access to my code books to make it more specific.
I assume you meant times 125%, not plus 125%.
 

TxSteve

Well-known member
Joined
Aug 22, 2023
Messages
121
Location
Granbury, Texas
To size the circuit conductors you have to use the value listed in NEC article 430 in the table shown in that article for the type motor of being used, plus 125%, NOT the nameplate value. Still out of State until early Friday morning so still don't have access to my code books to make it more specific.
I'll be interested in your interpretation based on 430.22(E) Other Than Continuous Duty
 

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
Make sure you have a disconnect of some sort at the lift. We've seen too many stories of contactors sticking closed and guys unable to shutdown a lift. A 30a dual pole switch is cheap insurance.

Yup, happened to me when my lift was new. Ha sent happened since in 20 years but once was enough.

This is approximately what the switch looks like in the Bend Pak HD9 4 post lift. Hard to believe this thing is rated at 2HP. But it explained a lot.

1712444647940.png
 