Hidden outlet?

Copymutt

Well-known member
Joined
Sep 3, 2016
Messages
3,396
Location
Colorado
In process of making and installing soffits. Existing exposed eves have a couple of weatherproof outlets for roof heat tape which will not be utilized. Does code permit just leaving them in place, enclosed under soffit? If not I can relocate or just terminate in the box.
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,241
Location
VT
I'm going to guess no, as this would be the same as a hidden junction box....

Leave them for Xmas lights?

Put a new box in, nut the wires and put a weather tight lid on it painted to match?
 
Last edited:

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,635
Location
Long Island
I'm going to guess no, as this would be the same as a hidden junction box....

Leave them for Xmas lights?

Put a new box in, but the wires and put a weather tight lid on it painted to match?
How are the soffits being enclosed? I've seen many done like a drop ceiling, and boxes above a drop ceiling may be allowed (not in a plenum, but elsewhere). If the soffit can be easily opened to access the box, I think that would be good enough. If you're screwing up cement board, then yeah, expose the box to the underside.
 
OP
C

Copymutt

Well-known member
Joined
Sep 3, 2016
Messages
3,396
Location
Colorado
Fabricated sheet metal soffit, several inches below the outlets. Extending them would also result in a hidden box, no access. Do I remember an in line, in wall approved connector for extending an NM-B run?
 
To avoid these ads, REGISTER NOW!
OP
C

Copymutt

Well-known member
Joined
Sep 3, 2016
Messages
3,396
Location
Colorado
Yes there are, but just like fat Propanel screws, Infrared bath heat fixtures, round soffit vents, Home Depot doesn't stock them!CC4AD3FE-635E-47BB-B77B-4472CE1F0580.png4A1F4A9A-7F67-473E-B1BB-FD90F6A32DDB.png
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,905
Huh?

There are connectors designed to splice and tap NM-b that can be buried in a wall.
no, it doesn't. Look it up. 334.40 B was changed for the 2014 code cycle to allow concealed use only for repair, not extension or a tap. In exposed wiring (like an attic say) they can be used for a splice without a box in extending a circuit. I don't understand why if it's good enough to repair with it, it's not good enough for new work, but that's the code language.
(a different section allows their use in pre fabricated housing)
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,982
Location
Central Iowa
The wires go back to somewhere, switch, gfci, breaker, etc. Find where that is, disconnect them and forget about it. Or you could get in the attic, if there is one, find the cable and cut it and put it in a box. That would be my last choice, I personally won't go in attics between May and October. Too damned hot.
 
OP
C

Copymutt

Well-known member
Joined
Sep 3, 2016
Messages
3,396
Location
Colorado
Still pondering whether to incorporate an access panel. Cleaner to go in from the soffit end panel as both outlets are close to the ends. Thx for all the suggestions. Score so far, me 100+, wasps 2.
 