I'm a retired CMAT and worked with auto A/C most of my career, to include, working at a shop from '86-'94 specializing in A/C & Electrical. I'm trying to finish up an install on a new R410a regular split system for my house. My question is to the HVAC Pros, mainly as their experiences would be great but any suggestions at this point would be appreciated.
Can nitrogen, unintentionally be, pushed through front seated service valves, into the precharged outside unit?
Install manual instructions have been followed except 3 deviations.
#1 I used Staybrite 8 w/stay clean flux.
#2 I wanted to take my leak check pressure to 380-400psi up from 150psi, system design pressure shows 448psi for both evap and OSU. The reason I wanted to do that was for our high ambient temps, the higher pressure of R410a and the OSU is pre charged so once I release the genie I'll need recovery assistance if leaks are found.
#3 I'm using Dawn liquid and water in a spray bottle to leak check with bubbles. Has work well in the past.
I ran low on nitrogen and could only develop about 200psi Friday evening,on initial leak check. The system held 200psi for an hour and no bubbles seen at joints. I then hooked up my vacuum pump with hose to an Appion valve core tool and a CPS digital micron guage. I pulled it down to 230mic and shut the valve off and disconnected vac pump. It rose to 240 at 20min, 280 at 40mins, 320 at 75mins, 360 at 130mins and finally to 380 at 140mins. This is well below the vacuum decay limit in the instructions.
Saturday I pick up a refilled Nitrogen tank and decide to attempt to achieve my higher pressure test. I run pressure up to 380psi and watched in disbelief as it drops to 360 in several minutes, I repeated this 3 more times as I go over the joints, drier,equalizer line, service and txv valves, manifold hoses, packing nuts, base of guages, no bubbles, nothing visual! It was continually dropping when I removed the guages and replaced the shrader caps leaving the 300+psi in it, a severe weather warning with chance of hail, I didnt want to leave my new guage set outside in the rain.
So last night I'm reading HVAC forums for things on pressure testing and found 2 references to the possibility of unintentionally pushing nitrogen past the service valves and I immediately get sick to my stomach. Could this be true? How could it hold charge in a hot warehouse or allow me to attain 230microns and hold 380mics? Did I somehow contaminate my yet to be released charge?
Today mid morning I quickly hook up the guages and find 235psi rising to 237 at heat of the day and staying there past 6pm. WTH is going on. I'm afraid to try another higher pressure test as I dont want to further contaminate but if it's already happened, well that's unfortunate.
Thanks in advance, Scot.
It's been a bit of a roller coaster trying to buy a digital manometer that was repeatable, a micron guage that doesn't leak and valves that dont seep in a deep vacuum. I currently have an Elitech and another CPS micron guages that leak internally but bleeding up vacuum to be useful for any thing. The defects will be sent back soon but it took 3 to get 1. Not good odds. No QC it would seem. So verify your micron guage before spending an hour pulling one down only to find your shiny new guage IS THE LEAK.
I'm a retired CMAT and worked with auto A/C most of my career, to include, working at a shop from '86-'94 specializing in A/C & Electrical. I'm trying to finish up an install on a new R410a regular split system for my house. My question is to the HVAC Pros, mainly as their experiences would be great but any suggestions at this point would be appreciated.
Can nitrogen, unintentionally be, pushed through front seated service valves, into the precharged outside unit?
Install manual instructions have been followed except 3 deviations.
#1 I used Staybrite 8 w/stay clean flux.
#2 I wanted to take my leak check pressure to 380-400psi up from 150psi, system design pressure shows 448psi for both evap and OSU. The reason I wanted to do that was for our high ambient temps, the higher pressure of R410a and the OSU is pre charged so once I release the genie I'll need recovery assistance if leaks are found.
#3 I'm using Dawn liquid and water in a spray bottle to leak check with bubbles. Has work well in the past.
I ran low on nitrogen and could only develop about 200psi Friday evening,on initial leak check. The system held 200psi for an hour and no bubbles seen at joints. I then hooked up my vacuum pump with hose to an Appion valve core tool and a CPS digital micron guage. I pulled it down to 230mic and shut the valve off and disconnected vac pump. It rose to 240 at 20min, 280 at 40mins, 320 at 75mins, 360 at 130mins and finally to 380 at 140mins. This is well below the vacuum decay limit in the instructions.
Saturday I pick up a refilled Nitrogen tank and decide to attempt to achieve my higher pressure test. I run pressure up to 380psi and watched in disbelief as it drops to 360 in several minutes, I repeated this 3 more times as I go over the joints, drier,equalizer line, service and txv valves, manifold hoses, packing nuts, base of guages, no bubbles, nothing visual! It was continually dropping when I removed the guages and replaced the shrader caps leaving the 300+psi in it, a severe weather warning with chance of hail, I didnt want to leave my new guage set outside in the rain.
So last night I'm reading HVAC forums for things on pressure testing and found 2 references to the possibility of unintentionally pushing nitrogen past the service valves and I immediately get sick to my stomach. Could this be true? How could it hold charge in a hot warehouse or allow me to attain 230microns and hold 380mics? Did I somehow contaminate my yet to be released charge?
Today mid morning I quickly hook up the guages and find 235psi rising to 237 at heat of the day and staying there past 6pm. WTH is going on. I'm afraid to try another higher pressure test as I dont want to further contaminate but if it's already happened, well that's unfortunate.
Thanks in advance, Scot.
It's been a bit of a roller coaster trying to buy a digital manometer that was repeatable, a micron guage that doesn't leak and valves that dont seep in a deep vacuum. I currently have an Elitech and another CPS micron guages that leak internally but bleeding up vacuum to be useful for any thing. The defects will be sent back soon but it took 3 to get 1. Not good odds. No QC it would seem. So verify your micron guage before spending an hour pulling one down only to find your shiny new guage IS THE LEAK.