I have two condensers I have a sub panel feeding them. The subpanel is mounted on the outside of my house at the condensers. I am getting new condensers installed but I have to move the subpanel to have the working clearance in front of it. I am moving it about 4’ to the right. I am just going to use the current subpanel as a junction box and install a new one. So my question is does it need a grounding electrode? Currently there is only two hots and a ground feeding the current subpanel. I don’t know why the electrician who wire the house did it this way and it is going to be very difficult to pull new wire from the panel inside and feed the condensers with two breakers. So, does the new sub need a grounding electrode or not?
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,581
Location
Long Island
It needs a grounding electrode, but if everything served by it is 240V, it does not need a neutral. So your two hots and a ground are fine for these purposes, but you cannot use it for 120V or 120/240V appliances.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
A subpanel in the same structure doesn't need a grounding electrode.
Only detached structures need them
"The subpanel is mounted on the outside of my house at the condensers."
 
Last edited:
OP
R

raco232

Well-known member
Joined
Jan 2, 2018
Messages
87
Location
South Memphis, TN
The sub panel is 240v w/ground, no neutral and is mounted to the exterior brick wall of my home. I put a ground rod in yesterday, but I got thinking that was probably not necessary, since the panel is attached to the home. That is why I am asking here, is it necessary or not? Is it ok to leave it or should I remove the #6 bare copper?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,700
Location
NW Iowa
Just move one of the condensing units over. Seems a lot easier seeing as that's what's getting replaced.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,991
Location
Modesto, CA
The sub panel is 240v w/ground, no neutral and is mounted to the exterior brick wall of my home. I put a ground rod in yesterday, but I got thinking that was probably not necessary, since the panel is attached to the home. That is why I am asking here, is it necessary or not? Is it ok to leave it or should I remove the #6 bare copper?

several people already answered your question

you wasted your money

it wont harm anything to leave it
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Its just a couple extra bucks you were not required to do. No big deal and a more local rod for the outside equipment cant really hurt.
Generally,, the code isn't really meant to make the best design,, but in basic areas the standards are pretty good, doesn't mean the minimum standard is inadequate,,, look at all the 12 wire do work 14 would easily do. In theory we can tend to know how something was done by when it was done and everyone tries to do it the same way.
A weakness we see here is spec built garages with a single circuit. A modern garage should be wired about like a modern kitchen. 2 separate small appliance circuits and dedicates for the built in or known loads.
 