I know this isnt "garage" related, but just wanted to get some cost opinions. Our 15 y/o central AC quit...compressor shorted to ground. It's an R-22 system, 5 ton, in a two story house. I have a "guy" who's always treated me well on repairs, and he's quoted me a new system for $7800.00 which includes a Lennox 14 SEER 5 ton unit, new evap coils, etc, and a new two stage 110K gas furnace. Does this sound about right installed? The house, built in the 70's is set up for one unit only and we both agreed it would be very tough(expensive) to convert it to a two unit AC system. In addition, I have a 7/8" suction line which kind of prohibits the newer high SEER units with over 1" suction lines. the lineset runs from the attic of the two story to outside and currently has a run over over 30' I'd guess. The current furnace it at least 15 y/o as well, so I'm guessing it wouldn't be much longer before I had a cracked heat exchanger, so having the whole thing priced.
Too many variables to comment on pricing.
But, you will NOT get the rated efficiency out of the new equipment if the airflow is not up to snuff.
Proper airflow is also critical for the variable speed motors because those will make every attempt to deliver what they are set for, to the point of self destruction. If the motor doesn't self destruct, your amp draw will be way higher than the plain old PSC motor, negating any energy efficiency gains.
A two hole total static pressure test can determine whether or not the existing total duct + coil + filter is too restrictive or not. Additional test ports can narrow down problem areas.
I assume that your speced equipment has an AHRI match? If not, you won't get the SEER rating, assuming that the airflow is good.
Did the person installing your equipment do a proper load calculation, or did they do an "old equipment label" calculation? 110k BTU in Memphis??? You live in a 3k+ SF house (80% AFUE) with no insulation?
Airflow is determined by the equipment requirements, so some "duct problems" can be reduced by installing properly sized equipment.
Does your current system have one air filter or two? If you have a 5 ton drive and only one air filter, I can guarantee that your airflow is not right and you are most likely getting only 4 tons (or less) of airflow at the equipment, before duct losses- which are very significant in a typical residential attic duct system.
As far as linesets go, there are tables that tell capacity losses for less than ideal installations. Changing them is always the right answer, but sometimes it isn't practical (homeowner doesn't want the mess) to impossible. There are flush kits and suction cleanup driers available.
Proper installation is key. I bet your existing condenser should have had an 1-1/8" lineset. Equipment failures due to poor installation are at a ~10 year to 15 year horizon, depending on just how badly it is installed. Almost anything will hold together long enough to make it through a 1 year warranty.
There are also specific piping practices when the evaporator is located over the condenser (different practices for the opposite situation).
Good luck.