I just found that my home heater (NG) was installed without a fresh air intake, its high efficiency with a PVC exhaust line should a fresh air line be installed ?
I just found that my home heater (NG) was installed without a fresh air intake, its high efficiency with a PVC exhaust line should a fresh air line be installed ?
As Im in the process of tightening the air seal of the home where does fresh air come into play ?
Not running the intake pipe was just lazy on the installers part. I would suggest that you find and follow the manuf instructions when adding the intake.
Why would this be ? Also according to the US energy guide sticker its a 92.1 AFUE with 96.6 being most efficient.
I'm pretty sure most 92% furnaces are made for a single pipe,you could upgrade it with a combustion air pipe though.Why would this be ? Also according to the US energy guide sticker its a 92.1 AFUE with 96.6 being most efficient.
It depends on what the efficiency rating of the furnace is,some are,designed to be single piped.
That can be a problem with any furnace.I consider direct venting as more of a safety issue. You contain the flue gas by-products. As well, many people simply assume that they have adequate combustion air. The code calls for 50cu ft/1000 btu of input. Frequently when someone buys a house with an open basement the first thing they do is drag a pile of 2x4's down to the basement and build a wall around the water heater, furnace or boiler. The other issue is that people will fill the basement half way to the floor joist and there you go again. Even with what calls as sufficient air doesn't take into consideration the number of ways we push air out of a house. bath fans, dryer vents, range hoods. We have taken the technology of the thermos bottle and applied it to home construction. A lack of combustion air generally doesn't happen all the time, but conditions can occur and you need to remember that every system has a personality. You hope that it is more Jeckyl than Hyde...or is that the other way around. I was a rep in the 6 New England states and sold oil and gas equipment as well as chimney products and power venters. I have seen hundreds of homes with exactly the problems I'm describing here. Why not just two pipe it and be done with the worry.
If you want to maximize the efficiency then use a concentric vent pipe system. That way the cold intake air is being pre-heated by the exhaust gas.
The room is the basement with no rooms and 900 sf. Dagny your question is at the root of my confusion, the furnace is shipped as a direct vent with sealed combustion and may be installed as direct vent or as non direct vent so if there is enough air from inside the home to feed combustion is there any good reason (comfort, air quality) to get combustion air from outside ? As Im in the process of tightening the air seal of the home where does fresh air come into play ?
Not running the intake pipe was just lazy on the installers part. I would suggest that you find and follow the manuf instructions when adding the intake.
Tommy, Im not a HVAC guy but I believe the return air comes from vents at the top of rooms on the first and second floors and the combustion air mostly comes from the basement where the furnance is located which is a completely open space. So if there is not a way to get fresh air in place is getting combustion from air leaks considered OK ?