Honda Generator

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
I picked up a Honda EN2500 generator at an auction for $19. The engine (gx160) runs great put the unit does not produce power. The push button switch did not seem to work so I opened up the cover and jumped the switch. Still nothing. I put a voltmeter in place of the switch and it read 2.2 volts. This is higher than the 0 volts it read before I started the motor. Do you guys have any ideas? I plan to replace the switch so do not worry about my safety. THANKS
 

Attachments

  • DSCN1640.JPG
    DSCN1640.JPG
    114.9 KB · Views: 65
  • DSCN1642.JPG
    DSCN1642.JPG
    109.8 KB · Views: 56
  • DSCN1643.JPG
    DSCN1643.JPG
    113.2 KB · Views: 49
  • DSCN1641.JPG
    DSCN1641.JPG
    118.5 KB · Views: 50
To avoid these ads, REGISTER NOW!

Streetbu

Well-known member
Joined
Jan 7, 2014
Messages
3,082
Location
Central NY
First thing to try, reassemble it, plug in an electric drill to one of the outlets. Start the engine. Grab the drill, depress the trigger, carefully spin the Chuck as quick as you can while holding the trigger down. This will energize/excite the field in the generator and it may just start working. Generators have a tendency to lose their charge if they've sat for an extended time. Be careful, if it does take off you don't want to get your hand cut or clothes caught in the chuck....
 
OP
R

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
I am seeing that the "switch" is labeled a protector circuit 20A. The want $50 for a new one. Can I just use a 20 amp fuse?
 

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,571
Location
Minneapolis, MN
That sounds like a 20 amp breaker. Are you getting power to the breaker? If you have no power to the breaker it won't help to replace it.
 
To avoid these ads, REGISTER NOW!

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,571
Location
Minneapolis, MN
One side of the breaker should be the hot side coming from the generator head. If you still have low voltage there it is probably not the breaker. You could disconnect the hot side from the breaker and then test again just to be doubly sure if it is the breaker or not.
 
OP
R

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
I ordered a new circuit breaker. I tested the capacitor and it read 13uF like it should. I tried the drill backwards and that did not work. I assume that I can replace the outlet with a standard 120V outlet. If after changing the outlet, changing the circuit breaker and it still does not work (I will try the drill again), what more can I do?
 