Quite a few conflicting opinions. Decided to do some research for my own install.

NEC Article 430, deals with motors.

430.6(A)(1)
Exception 3
- (paraphrased) If the motor is marked with both HP and FLC
(aka FLA), use the FLC to determine the ampacity of the conductors.

430.22 Single Motor. Conductors that supply a single motor
used in a continuous duty application shall have an ampacity of
not less than 125 percent of the motor full-load current rating,
as determined by 430.6(A)(1), or not less than specified in
430.22(A) through (G)

In the OPs case, FLC = 22A * 1.25 = 27.5A conductors.

Misc:
Compressors are not covered by the NEC Appliances article.
Compressors are considered continuous duty motors.
The nameplate contains a lot of info that could be used in sizing, SF, Time, Temp, Code.

The exception you paraphrased is for appliances. An air compressor is not an appliance.
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,769
Location
Southern Oregon
Got it. Thanks.
"Exception No. 3: For a listed motor-operated appliance that is marked
with both motor horsepower and full-load current, ..."

5HP = 28FLC per table 430.248 multiplied by 125% per 430.22 = 35A minimum conductor
as was previously stated several times
This should be in Electrical FAQ post, not that anybody would read it.
 