Just had a Hot Dawg 75K unit heater installed. Unit has a power exhaust. My HVAC buddy put it in…. One question, he put a thimble on the interior side where it contacts the drywall but do not see one on the exterior? Is this correct or should there be one? He put high temp fire caulk around the exterior penetration. Feedback appreciated. See pics below
That is not a thimble on the inside.
That is a support plate, it works like a Chinese finger toy. The vent pipe cannot be easily pushed inside from outside. At least until the screws/anchors pop out of the drywall.
This is a Type B vent thimble (which also needs to be visible when installed):
Your HVAC buddy did not install it properly.
Type B vent is not allowed for horizontal installations, and I am reasonably sure that this stipulation pre-dated the rule change in unit heater installation instructions.
Your equipment does not have a "power exhaust", it has a draft inducer. It pulls the gases through the heat exchanger. If you stuck a manometer in the flue pipe, it will read a negative pressure. It is not a minor technicality.
The only allowable installation for Type B vent in a horizontal configuration requires a power venter like a Field Controls SWG series, which will require a controls package and a barometric relief damper. And then you will get into makeup air issues.
Feedback: Not installed properly.
Just because there may be other similar installations does not make it right. Because it is not installed properly, you are assuming a great deal of potential risk.
The equipment safeties cannot detect a rotted out flue pipe, and the equipment will therefore continue to operate.