teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
I'm putting in a hot tub and there is a pre-existing GFCI panel where a hot tub previously sat. I am going to wire it myself and I'm comfortable doing so.

I'm aware that code dictates the disconnect must be a certain distance from the hot tub. Usually > 5 feet I believe.

This panel is more like 3 feet away.

I don't care about code but I do care about safety. How big of a safety risk am I taking by leaving the panel in its current spot? I'm assuming the rationale for the code is the panel could potentially become energized and a (child probably) could reach from inside the water and touch the panel. How likely is such a situation to actually occur, assuming all wiring is done otherwise properly?
 
To avoid these ads, REGISTER NOW!

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,759
Location
East Bay SFO
Safety is important.
How about building a small wall between the hot tub and the disconnect so that it would be impossible to reach from the tub to the switch unless you had flexible arms 5 feet long. 😎
 
OP
T

teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
Yes my understanding is code would permit that. In my case though a wall would look pretty dumb in this location. I could put a wooden box around it though...

I really just want to try and understand the rationale for the rule because as we all know plenty of electrical codes exist for a variety of situations that may never occur at our specific homes.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,759
Location
East Bay SFO
If a guest somehow electrocuted themselves in your hot tub with an electrical panel less than 5 feet from the water, I bet the judge and/or jury would find you liable.

We used to have a hot tub in the back corner of our back yard patio and I had the electrician install the fused disconnect on the house wall about 20 feet away from the tub. One inch EMT running along the bottom of the fence connected everything up properly.
 
OP
T

teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
If a guest somehow electrocuted themselves in your hot tub with an electrical panel less than 5 feet from the water, I bet the judge and/or jury would find you liable.
I understand that.

What I do not understand is, what are the actual chances of that happening and what specific circumstances could trigger that.
 
OP
T

teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
You know, I could just ask an AI these questions and get an actual answer. "Just do it" without articulating a reason completely negates the point of a discussion forum where we are here to LEARN things. I want to know the WHY.

So anyway, I asked the AI and it was far more helpful, explaining that, among other things, a mouse could chew through a line wire and energize the panel.

So now instead of being browbeaten on the topic I LEARNED SOMETHING NEW and I'll relocate the panel now.

Thanks, not.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,759
Location
East Bay SFO
I bet the odds of that happening are extremely low.
Will everyone using that tub be responsible sober adults? Will groups of children especially teenagers be using it unsupervised?

We all take risks everyday. I have 3 steps leading from our driveway up to the path to the front door. Code does not require a handrail and I don’t have one. Could somebody in a frail condition fall on those steps? Of course!

Our house was built in 1950. Is it up to code in every respect? No. Do I have a personal liability insurance rider? Yes.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,759
Location
East Bay SFO
Just for another example of AI advice, I asked about the 3 steps up from my driveway. Here is the response.

Karl home Transitional Handrail Stair Railing Fits 3-Step Iron Rail Kit  891262135247 - The Home Depot
While not universally required for three steps, installing a handrail is strongly recommended for safety, and may be legally mandated depending on local codes. Many building codes require handrails for stairways with three or more steps, or when the vertical rise exceeds a certain height (often around 30 inches).
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
You know, I could just ask an AI these questions and get an actual answer. "Just do it" without articulating a reason completely negates the point of a discussion forum where we are here to LEARN things. I want to know the WHY.

So anyway, I asked the AI and it was far more helpful, explaining that, among other things, a mouse could chew through a line wire and energize the panel.

So now instead of being browbeaten on the topic I LEARNED SOMETHING NEW and I'll relocate the panel now.

Thanks, not.
Fantastic!
 

kbuhagiar

Well-known member
Joined
Dec 27, 2005
Messages
1,790
Location
Escondido, CA
You know, I could just ask an AI these questions and get an actual answer. "Just do it" without articulating a reason completely negates the point of a discussion forum where we are here to LEARN things. I want to know the WHY.

So anyway, I asked the AI and it was far more helpful, explaining that, among other things, a mouse could chew through a line wire and energize the panel.

So now instead of being browbeaten on the topic I LEARNED SOMETHING NEW and I'll relocate the panel now.

Thanks, not.
I understand your motivation, and I'm glad you got the response that you were looking for, but... please do not be so naive as to believe that AI is the ultimate - or even accurate - authority on ANYTHING.

Especially electrical or engineering codes.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,192
Location
Modesto, CA
I understand that.

What I do not understand is, what are the actual chances of that happening and what specific circumstances could trigger that.
Impossible to answer such a question. Way too many variables and predicting odds is like betting on horse races and sports games…
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,192
Location
Modesto, CA
I understand your motivation, and I'm glad you got the response that you were looking for, but... please do not be so naive as to believe that AI is the ultimate - or even accurate - authority on ANYTHING.

Especially electrical or engineering codes.
Bingo

And the AI answer was wrong…
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,229
Location
NJ
I understand that.

What I do not understand is, what are the actual chances of that happening and what specific circumstances could trigger that.
For someone to dream up every scenario where there is an injury risk would be fruitless.
Requiring a minimum distance can eliminate many of them but never all of them.

What's the point of asking for "chances of"?
What if the probability is 8% that a specific situation could occur......what side of that number do you want to be on?

GFCI functionality has been known to fail and it only monitors the downstream circuit, could care less about the conditions of the upstream circuit.

If you really want the answer, go back to NFPA and ask the CMP that authored that change in NEC to splain da data/reasons.
 

Cruzan80

Well-known member
Joined
Jul 22, 2015
Messages
4,437
Location
Denver, CO
IIRC, here it needs to be at least 5ft away, but Flex liquid-tite can't be used for further than 6ft...

Or something else like this that means I have a very narrow window to put the box and still meet min/max length...
 
OP
T

teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
Doesnt care about code or the fundamentals?
Right. I don't care about code. I do care about safety, and learning the WHY of things.

I understand your motivation, and I'm glad you got the response that you were looking for, but... please do not be so naive as to believe that AI is the ultimate - or even accurate - authority on ANYTHING.

Especially electrical or engineering codes.
Which is why I came here first, looking for information. I agree.

Too bad the AI answer is wrong if the panel is properly bonded it would be impossible for it to become energized because the feeding breaker would trip…
Do you have something to add?
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,192
Location
Modesto, CA
Right. I don't care about code. I do care about safety, and learning the WHY of things.


Which is why I came here first, looking for information. I agree.


Do you have something to add?
I explained the why and no dont need to add anything. did you read the second half of my sentence that you responded to about the panel bond?
 
OP
T

teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
I explained the why and no dont need to add anything. did you read the second half of my sentence that you responded to about the panel bond?
Your explanation of the rationale behind the NEC rule is that a bonded panel is impossible to become energized?
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,229
Location
NJ
Right. I don't care about code. I do care about safety, and learning the WHY of things.
The Code Making Panels that address each tri-annual revision of the NEC are many-times using recent historical data regarding fires, electrocutions, failure modes, best practices, lack of best practices, public input to close gaps and provide a better future set of requirements.

So think "The Code" as a living book of the latest minimum best practices for the electrical industry.
 
Last edited:

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,229
Location
NJ
Your explanation of the rationale behind the NEC rule is that a bonded panel is impossible to become energized?
Anything can change after the correct installation - due to mechanical damage, weather/oxidation, intentional change. The first two reasons mentioned are many times unrecognized.
 
OP
T

teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
I went looking for one single case of a human being ever reaching out from a hot tub and touching a GFCI spa panel and being shocked and could not find one. I do not think there has ever been one single recorded case of this occurring ever, anywhere.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
I went looking for one single case of a human being ever reaching out from a hot tub and touching a GFCI spa panel and being shocked and could not find one. I do not think there has ever been one single recorded case of this occurring ever, anywhere.

**** it, screw the disconnect right to the tub.


Why do people come here looking for direction and then argue why they shouldn't follow established practices or code?
 
OP
T

teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
**** it, screw the disconnect right to the tub.


Why do people come here looking for direction and then argue why they shouldn't follow established practices or code?
For the same reason you can login to an electrician forum and see them discussing the same type of issues.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
I went looking for one single case of a human being ever reaching out from a hot tub and touching a GFCI spa panel and being shocked and could not find one. I do not think there has ever been one single recorded case of this occurring ever, anywhere.
****, that settles it. Any other codes you can summarily dismiss via a little googling?
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
I'm putting in a hot tub and there is a pre-existing GFCI panel where a hot tub previously sat. I am going to wire it myself and I'm comfortable doing so.

I'm aware that code dictates the disconnect must be a certain distance from the hot tub. Usually > 5 feet I believe.

This panel is more like 3 feet away.

I don't care about code but I do care about safety. How big of a safety risk am I taking by leaving the panel in its current spot? I'm assuming the rationale for the code is the panel could potentially become energized and a (child probably) could reach from inside the water and touch the panel. How likely is such a situation to actually occur, assuming all wiring is done otherwise properly?
Line of site is normally good enough.
So you can see the disconnect while you're servicing the equipment.
 
OP
T

teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
"I don't care about code" and finding justification for it to be unnecessary feels contrary to your statement.

Good luck with the project, I hope no one gets hurt.
Since you are so big mad about this topic why don't you help educate the class. You obviously know more than me.

So please describe a theoretical scenario in which a hot tub bather would reach out and touch a GFCI subpanel that is too close under code and become electrocuted. Let's try to exercise a little intellectual curiosity here instead of just acting angry and rude.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
So please describe a theoretical scenario in which a hot tub bather would reach out and touch a GFCI subpanel that is too close under code and become electrocuted.

You're soaking in the tub, all of a sudden the bubbles stop....

You reach over to re-set the breaker while completely soaking, standing in a puddle (or worse still in the tub) and BAM, you get electrocuted do to any numerous issues of why a dripping person shouldn't be trying to reset breakers.
 
OP
T

teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
Are spa panels really built with such a lack of safeguards where that scenario is even plausible?

>>> reminder the scenario we are talking about here never been recorded as happening, ever, globally <<<
 

Cruzan80

Well-known member
Joined
Jul 22, 2015
Messages
4,437
Location
Denver, CO
**** it, screw the disconnect right to the tub.


Why do people come here looking for direction and then argue why they shouldn't follow established practices or code?

Just to be clear, for my use case, I am moving the hot tub into place, and then mounting the disconnect. I just thought the Min/Max being a 1-2ft window was pretty odd (though it was listed separately, so it may have to do with the type of "conduit/tubing" I am using).

What is the correct "catch-all" term for the stuff going around wiring to protect them? MC/Liquid-tite feels wrong calling it "conduit", but EMT sounds weird as "tubing".
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,192
Location
Modesto, CA
I went looking for one single case of a human being ever reaching out from a hot tub and touching a GFCI spa panel and being shocked and could not find one. I do not think there has ever been one single recorded case of this occurring ever, anywhere.
youre kidding right? you really think every single case of an incident would be published online? smh :headscrat
 

whateg01

Well-known member
Joined
Mar 13, 2006
Messages
11,815
Location
doo dah, kansas, usa
You're soaking in the tub, all of a sudden the bubbles stop....

You reach over to re-set the breaker while completely soaking, standing in a puddle (or worse still in the tub) and BAM, you get electrocuted do to any numerous issues of why a dripping person shouldn't be trying to reset breakers.
And nobody ever drinks in a hot tub so there's never a chance that a drunk person would do that! /s
 