Hot Tub wiring?

6togo

Well-known member
Joined
Nov 7, 2016
Messages
173
Location
Harford co , MD
So I have a Hot tub to wire up it's a 50amp unit. it has to run up and down the walls and across a small attic into a 2030 box on the wall near the tub. I planned on running 6/2 Romex thru the attic and walls for an easier install Vs conduit but once outside I will run conduit into the tub from the box. What should I use for wiring in the conduit #6 THHN for the hots and #? for the ground?
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,004
Location
NJ
Verify that you don't need 6-3. Newer hot tubs need a neutral.
#10 for the ground.
You will also need gfci protection and a disconnect within 5-20'. Add a gfci recept.
 
OP
6

6togo

Well-known member
Joined
Nov 7, 2016
Messages
173
Location
Harford co , MD
I believe the 2030 box has a Gfci breaker that came with the tub and it will be 5' away from the tub on a close wall. I looked at the spec sheet and don"t recall it stating a 3 wire but I will be at it tomorrow to verify. Worst case I run 6/3 Romex then a extra #6 wire for the neutral in the conduit.
 

Trip McNealy

New member
Joined
Nov 6, 2023
Messages
3
Location
Alpharetta, GA
Verify that you don't need 6-3. Newer hot tubs need a neutral.
#10 for the ground.
You will also need gfci protection and a disconnect within 5-20'. Add a gfci recept.
I second this. We bought a home last year that has an existing hot tub on the rear patio wired up on a 50A circuit with a double-pole GFCI breaker. When I had an electrician come out for other work, he mentioned should we eventually replace the tub, that we will need it wired up in a similar manner that mm08822 stated. Ours has the disconnect within range but on the interior wall which is not to current code; it needs to be outside.
 

tyromeo55

Member
Joined
Dec 2, 2021
Messages
21
Even if the hot tub doesn't need the neutral, you'll need it to make the GFI work. It won't trip without a neutral.
not true

Edit: I'll bend a little on this. The couple of spec sheets I looked over indicating that it (neutral pigtail) needs to be landed. This is a liability hedge. In function, the breaker does not need it to function properly if a neutral is unused.

from Siemens

"
The Siemens 2-pole GFCI circuit breaker can be installed on a 120/240V AC single phase, 3 wire
system, the 120/240V AC portion of a 240/120 volt, 3 phase, 4 wire system, or on a 208Y/120 volt, 3
phase, 4 wire system. When installed on these systems, protection is provided for 2 wire, 240V AC or
208V AC circuits; 3 wire, 120/240V AC circuits"
 
Last edited:

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,004
Location
NJ
Let's clarify this.....the circuit protected by the gfci cb does not a neutral as part of the circuit being protected.
The gfci cb however, needs to be connected to a neutral for the internals of the cb to function.
1700023169202.png
1700023244602.png1700023534587.png1700023467181.png
 

tyromeo55

Member
Joined
Dec 2, 2021
Messages
21
@
Let's clarify this.....the circuit protected by the gfci cb does not a neutral as part of the circuit being protected.
The gfci cb however, needs to be connected to a neutral for the internals of the cb to function.

I see what your saying and agree with you that (at least for Siemens and SQd) would definitely need to be installed if not simply for its manual stating to do so. But still. I don't believe you can accurately say "It won't trip without a neutral" as quoted elsewhere. I've personally tested it as have others in depth on other forums (mike holt). If your only using the 2 phase conductors and omit the neutral pigtail the breaker will (i beleive) function provided leakage over its design limit. One thing Id bet you would /could loose on the SQd would be the self test or even the trip button.

Again... Yes. I agree that it needs to be installed My brain just has a little internal skip when I see the exact wording in post 6
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,004
Location
NJ
@


I see what your saying and agree with you that (at least for Siemens and SQd) would definitely need to be installed if not simply for its manual stating to do so. But still. I don't believe you can accurately say "It won't trip without a neutral" as quoted elsewhere. I've personally tested it as have others in depth on other forums (mike holt). If your only using the 2 phase conductors and omit the neutral pigtail the breaker will (i beleive) function provided leakage over its design limit. One thing Id bet you would /could loose on the SQd would be the self test or even the trip button.

Again... Yes. I agree that it needs to be installed My brain just has a little internal skip when I see the exact wording in post 6
Which mode of tripping are you referring to? I believe for ground faults it is 100% required as the circuity and logic processor need power. Possibly for overload/short circuit it may function as a standard cb w/o panel neutral connected to cb. Can't say I ever thought about not connecting it.....otherwise, what is the point to buy/install it?
 

tyromeo55

Member
Joined
Dec 2, 2021
Messages
21
Which mode of tripping are you referring to? I believe for ground faults it is 100% required as the circuity and logic processor need power. Possibly for overload/short circuit it may function as a standard cb w/o panel neutral connected to cb. Can't say I ever thought about not connecting it.....otherwise, what is the point to buy/install it?
For academic purposes.... Take a 2 pole GFCI breaker and completely omit connecting a neutral. Take any or both phase conductors and leak its rated current to earth (typically 6ma) It will (in my experience) trip. The internal potential relay and its CT dont rely on logic (at least not where I've seen). The logic is for automated periodic testing and sometimes feedback. Could you imagin a potential death riding on the hope that a little logic board is working properly? Admittedly Its been many years but at one time we were required to test every breaker installed for a particular large commercial customer. Sometimes I think it would be neat to make another test rig if only to show green horns trip curves and show how potential Short circuit capacity can have affect

I really just need to learn to keep my mouth shut and not take things to literal. bad "tick" of mine - Apoligies to all for de-railing.
 
To avoid these ads, REGISTER NOW!

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,072
Location
Fernley, Nevada, about 30 miles east of Reno.
Even if the hot tub doesn't need the neutral, you'll need it to make the GFI work. It won't trip without a neutral.

I should have been more clear......I meant the white wire needs to be connected to the neutral bus in order for the GFI portion of the breaker to trip. The overload and short circuit portions will work without the white wire connected.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,269
Location
Coastal NJ
So I have a Hot tub to wire up it's a 50amp unit. it has to run up and down the walls and across a small attic into a 2030 box on the wall near the tub. I planned on running 6/2 Romex thru the attic and walls for an easier install Vs conduit but once outside I will run conduit into the tub from the box. What should I use for wiring in the conduit #6 THHN for the hots and #? for the ground?
Since the conduit is outdoors, you will need THWN
 
OP
6

6togo

Well-known member
Joined
Nov 7, 2016
Messages
173
Location
Harford co , MD
Ok so once I got to the tub today it did require a neutral so I ran 6/3 from the main panel to the 20/30 spa box. This 20/30 is a bit different than I have dealt with before big wire in and 10/12ga. to the spa. One thing I'm unsure of the is the specs show the two Gfci breaker but only one gets a neutral wire not both and they both have a spot in the center for one. I assume these are universal and fit other spa setups but I would like to know if the second neutral is needed.
 

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,072
Location
Fernley, Nevada, about 30 miles east of Reno.
Every GFI breaker needs to have the built-in white wire connected to the neutral bus.

Not every GFI breaker will have the neutral connected to the load.

The built-in white wire needs to be connected to the neutral bus because the internal GFI circuitry is 120 volts and uses one of the poles and the white to operate.
 
OP
6

6togo

Well-known member
Joined
Nov 7, 2016
Messages
173
Location
Harford co , MD
Yes both 20 and 30 amp breakers have the built in white pig tail going to the bus with the neutral from the main panel. Both breaker have a third lug for neutrals but it only shows one of them getting the neutral from the spa. I believe the 30amp runs the heater and the 20amp runs the pumps and panel that way they are isolated if the heater fails you can still move water so it don't freeze.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,600
Location
BC
Both of our hot tubs (30A and 50A) require neutral. Whatever that is worth. These are "simple" tubs with single 2-speed motors and heater.

Mine is a simple one too. (20yo Beachcomber.) On this one, the neutral is only needed for the underwater light.
 

juddspaintballs

Well-known member
Joined
Sep 1, 2011
Messages
324
Location
Hedgesville, WV
Ive seen 20/30 hot tub setups that definitely require a neutral… this means running 6/3 NM-b
Yep. I wired up my dad's hot tub and I was prepared to do a 50A GFCI breaker only to find out that it required a 20/30. The package he bought came with the panel and breakers at least, so all I had to do was run the wiring and hook it up to the hot tub.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,977
Location
Central Iowa
Whenever someone calls me about wiring a hot tub, the first question I ask is "is it a Hot Springs?" If yes, I know it's a 20/30 and the disconnect is going to be provided. If no, it's more than likely that I have to get the disconnect. Either way, it's getting a neutral.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,784
Location
Austin, TX
A buddy bought a hot tub recently (higher end, local hot tub shop) - I was helping him wire it and I found that the instructions for that particular tub (dont remember brand) explicitly prohibited the use of many of the common Home Depot / Lowes "spa panel / breaker" brands...
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,004
Location
NJ
A buddy bought a hot tub recently (higher end, local hot tub shop) - I was helping him wire it and I found that the instructions for that particular tub (dont remember brand) explicitly prohibited the use of many of the common Home Depot / Lowes "spa panel / breaker" brands...
Interesting. So what did they "allow"?

Please have your buddy screenshot that requirement or get mfr/model#.
 