Hot water heat zone question

66HertzClone

ALLIANCE MEMBER
Joined
Dec 6, 2006
Messages
4,042
Location
Long Valley, NJ
I have 3 zone baseboard hot water heat in my home, a gas fired boiler. The first zone covers the 3 bedrooms, and the two full baths, second zone covers the rest of the ground floor rooms, the third zone is the solarium in my basement. I have Lux Wi-Fi programable thermostats for each of the zones. This system was oil fired when I bought the house, the boiler was leaking and I wanted to have a standby generator installed so I switched to gas and replaced the boiler. I don't use the solarium much, so I have the thermostat set to keep the temp at a minimum temp and often turned off completely. I was going to do some work down there and turned the temp up to 68 degrees, before going down to the basement I noticed the temperature in the bedroom zone had increased and was over 70 degrees, I use one of the bedrooms as an office and the temp in there was at 72. I checked the app for the stats and the bedroom was set to 68 as normal.

I went to the basement and found the temp was climbing but probably due to the size of the room, the starting temp, the temp had only reached 65 degrees. Seems that when the basement heat is running the heated water is also flowing through the bedroom circuit. I don't know much at all about how these systems work, but I assume the the zones would be separate so there shouldn't be an overlap. Is this normal or was something done wrong when the new boiler was installed causing this to happen?
 
To avoid these ads, REGISTER NOW!

TurnipTruck

Well-known member
Joined
Aug 28, 2005
Messages
1,572
Location
Southcentral Alaska
Can you post pics of the near-boiler piping?
My first thought is missing or bad check valves either in or near the pumps, or a sticking zone valve.
Have you noticed this problem before? How long since the boiler replacement?
 
OP
6

66HertzClone

ALLIANCE MEMBER
Joined
Dec 6, 2006
Messages
4,042
Location
Long Valley, NJ
I will go down and get some pictures for you. I really haven't used the heat in the basement since the installation a few years back, I live alone and have a disability so going to the basement isn't something I do often at all. There is manifold area that was some sort of controller for water flow, it isn't close to the boiler but I would guess that's what you want to see.
 

TurnipTruck

Well-known member
Joined
Aug 28, 2005
Messages
1,572
Location
Southcentral Alaska
I am assuming the 007e pump heats the indirect water heater, so the three 007-F5 pumps are your house zones. Those pumps did not come from the factory with check valves. If they did they would have FC in the model number. So, unless the black ******* under each pump are disguised check valves OR someone inserted checks into the pumps after purchase, you don’t have a way to stop ghost flow or back flow in one zone when other zones are pumping.

IMG_1012.jpeg

-I am not a professional-
 
OP
6

66HertzClone

ALLIANCE MEMBER
Joined
Dec 6, 2006
Messages
4,042
Location
Long Valley, NJ
Thanks, that was informative, the length of the zone for the basement is very short so I guess that’s why I notice it. I will use my infrared thermometer and see if this happens across all of the zones. I’ll talk with the installer and see what he can do for me. Thanks
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,981
Location
Peace Valley,mo
To avoid these ads, REGISTER NOW!

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,656
Location
Fargo, ND
I can't explain why, but every so often on hydronic heat we have had one zone call for heat, and when that pump ran, it created flow in another zone. We often just added a zone valve and wired it to the pump, so when the pump got power the valve opened.

Often we would go with one larger modulating pump for all zones and zone valves.
 
OP
6

66HertzClone

ALLIANCE MEMBER
Joined
Dec 6, 2006
Messages
4,042
Location
Long Valley, NJ
Agree with post 6 check valves are needed. Since we don't the t stat model this manual just looked at this manual. Setting is just for boiler there isn't anything for cycle rate or any other adjustments.
This is the thermostat that I have, four actually, one for each of the three heat zones and one for the A/C which was added to the house later.

 

Just_Steve

Well-known member
Joined
Jun 2, 2020
Messages
893
Location
Dutchess County, NY
I have 4 zones for heat, when I remodeled kitchen I had someone install a toe kick heater, it's installed incorrectly such that any zone call for heat triggers the heater. I haven't fixed it only because the kitchen needs the extra heat.
 