In Phoenix, we don't run heat. Come home from work and AC is going full blast. Thermostat is off and even if it was on it is set at 76. House is down to 60.

Put new batteries in thermostat, still won't shut down. Had to go trip the breaker. It's a 20+ year old roof top unit.

I'm a tenant so I don't have to worry about fixing it but wtf?
 
To avoid these ads, REGISTER NOW!

Fierljeppen

Well-known member
Joined
Jan 26, 2018
Messages
1,159
It's probably a stuck relay on the control board or thermostat. Either way, 20+ years for an AC unit in Phoenix is impressive.

I'm expecting to shovel a lot of heavy snow in Chicago tomorrow, so I'm a little light on sympathy at the moment.
 
Last edited:

Mr_fixit

Well-known member
Joined
May 24, 2008
Messages
1,221
Location
Rustylvania
A mouse chewing on the wires? A squirrels nest ? Hang a picture lately? Any remodeling done lately?
 

Done That

Well-known member
Joined
Aug 18, 2017
Messages
601
Location
MO
Sounds like welded contactor if not the tstat, but not sure why it had a cooling call to engage if off unless rodent s etc as stated above.
 
To avoid these ads, REGISTER NOW!

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Not a welded contactor. The evaporator fan wouldn't be running, the evaporator would most likely be iced, it would possibly cycle on the low pressure cut out and the house would not be cold.

Take the T-stat off the sub base. If the unit continues to run, it's not the T-stat, Something is shorted. Take the R wire off the T-stat sub base. If the cooling runs normally, there's a short between the R, G & Y wires or (very unlikely) at the control board. If the evaporator fan stops, but the unit continues to run the compressor, there's a short somewhere in the R & Y circuits. Again, it could be the T-stat wires themselves or a problem with the control board.

Tommy
 

acmikee

Well-known member
Joined
Feb 2, 2005
Messages
301
Location
olympia, wa
do what LS said i suspect bad t-stat or wiring
with the t-stat removed check V between R and Y if 0V stat ok if 24V reinstall stat and go to indooor unit and remove the R wire if still running bad/shorted board if it shuts off bad wiring
 