I need to run 60 amp service to the detached garage but my house panel is full and will not allow tandem breakers, other than getting another meter at the garage what are my options?
Thx,
Mike
Thx,
Mike
Never heard of that ! A limited number, yes.I need to run 60 amp service to the detached garage but my house panel is full and will not allow tandem breakers, ...
Never heard of that ! A limited number, yes.
I did find out that Square D made 2 styles of tandem QO breakers ! The older boxes will not accept the newer style tandems and you really have to search for the older ones !
There are two types non-CTL, made for panels prior to 1968, & CTL, the non-CTL type do not have the rejection tab on the twin breaker to prevent installation on unnotched bus stabs, & cost more then the CTL type. Older panels will be marked if they can use twins, just like the CTL type used now. The Non-CTL type should not be used in CTL type panels.
I believe that "CTL" stands for "Current Limiting".
Never heard of that ! A limited number, yes.
I did find out that Square D made 2 styles of tandem QO breakers ! The older boxes will not accept the newer style tandems and you really have to search for the older ones !