How are breakers in a surface mount raceway set up?

kjbenner

Well-known member
Joined
Jan 1, 2011
Messages
264
Location
NE Ohio
I'm used to seeing surface-mounted steel raceways full of receptacles, switches, and breakers. I was just realizing I don't really know how it works to have a breaker not in a panel (for what it's worth, I'm not trying to do this, I'm just curious).

I'm talking about things like this: https://www.legrand.us/wire-and-cab...000-circuit-breaker-housing-fitting/p/g6046kd, https://www.legrand.us/wire-and-cab...reaker-housing-fitting/p/g3046kd?text=G3046KD

Is the raceway treated like a subpanel, where you have one or more breakers in the raceway circuit breaker housing fed by a larger breaker at a main panel (and would you need to run a new ground)?
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!
OP
K

kjbenner

Well-known member
Joined
Jan 1, 2011
Messages
264
Location
NE Ohio
Go here > https://www.legrand.us/wire-and-cab...reaker-housing-fitting/p/g3046kd?text=G3046KD and download the installation instruction .pdf file. It has all the info you're likely to need (with illustrations).
The breakers have line in/line out lugs, opposed to a bus bar arrangement
Thanks. That makes sense, the hot goes through the breaker and the neutral and ground just pass by... but how is this breaker fed? Like if I have a 20A breaker in a raceway, is it fed by a 20A breaker back at the panel (in which case I'm not sure the utility of this arrangement), or can you have a single larger breaker at the panel feeding smaller breakers down the line in the raceway (in which case I didn't realize you could do this outside of a subpanel)?
 

klassenl

Well-known member
Joined
Feb 20, 2016
Messages
713
Location
Southern Alberta
Thanks. That makes sense, the hot goes through the breaker and the neutral and ground just pass by... but how is this breaker fed? Like if I have a 20A breaker in a raceway, is it fed by a 20A breaker back at the panel (in which case I'm not sure the utility of this arrangement), or can you have a single larger breaker at the panel feeding smaller breakers down the line in the raceway (in which case I didn't realize you could do this outside of a subpanel)?
The short answer is yes. The long answer is there are many rules to follow.
 