I have a 30k BTU Reznor V3 in my oversized 2 car (25'D 27'W 12'T). Tonight i am taking it down and going to buy a bigger Hot Dawg because the 30k just doesn't cut it. The question is, should i go 45K or 60K? It's only a $25 difference in price, but i fear that the bigger one will use up too much oxygen and/or turn on and off too much in my garage. The garage is fully insulated with a ceiling fan.

Anyone have an educated opinion on this? Thanks to all that reply.
 
To avoid these ads, REGISTER NOW!

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
Too LITTLE Information.

Welcome to GJ, but no way to get proper advice with such skimpy info.

How good is insulation?? Size and # of windows and garage door?? Insulated GD??

In Siberia or Florida?? Now would be a good time to Update GJ Profile.

What were reasons Reznor "could not cut it" as likely it was proper size if garage was fully insulated.
 
Last edited:
OP
R

ranger098

Member
Joined
Jul 23, 2013
Messages
14
Location
Mound, MN
Hi, I did say the garage is fully insulated, meaning insulated GD, walls and ceiling. No windows, just a side entry door which is solid core. Also it's attached to the house so 2 of the walls meet up to the home.

I am in MN, where its currently 0 and is set to be -15 tonight. Yesterday (it was 0 yesterday too) my 30k heater was running for over 1.5 hrs and only got to 40 degrees, even with the ceiling fan running. When i said the 30k "doesnt cut it" i mean it takes about 1.5 hours to warm up the garage to 60 even when its around 20 outside.

One would think 30k would be plenty, but i think my high ceiling and very cold MN temps prevent the reznor from warming up quick enough for me.

The specs on a hot dawg say that a 45k btu has a max mount height of 10', which is lower than my ceiling (12'), which makes me lean toward the 60k. however i do not like the idea of it taking more oxygen from the garage, giving me headaches.

Thanks for the response!
 

HoosierBuddy

Well-known member
Joined
May 9, 2006
Messages
2,922
Location
Southern Indiana
however i do not like the idea of it taking more oxygen from the garage, giving me headaches.

Thanks for the response!

A vented gas appliance doesn't effect the oxygen level in the garage. Assuming it uses ambient air for combustion (some do, some pull combustion air from outside)...it pulls all the molecules that make up "air" through the burner assembly that air mixed with combustion byproducts is expelled through the flue.

If ambient air is used for combustion, this air must be replaced into the building space "somehow". Generally in a garage, I would think most of that air comes under or around the overhead doors.

My point being...the air in the garage's oxygen content is unaffected as air is "replaced" due to negative pressure in the heated space.

This is NOT true with a ventless heating product by the way. Those heaters have oxygen depletion sensors for the very reason you suggest.

Phil

p.s. To the original question: I'd likely go with the 60K unit. It'll give you quicker recovery if you turn it down when the garage isn't occupied and then turn up the t-stat when you're out there.
 
Last edited:

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
I just discovered that you had other thread about your Reznor 30K Btu being too small.

Does sound like your tall ceilings and cold climate is hurting your ability to heat. Make every effort to close up any leaks and upgrade like you are planning.

You could run the numbers but since you know exactly how long the 30K took, I'd say go with 60K Btu as sounds like you need it.

If you were closer, I'd buy the 30K unit off your hands ! Good luck with install which won't use up any oxgen in garage. Only question you have is normal heater or seperate combustion which draws in outside air (ie best for shop with paint fumes or lots of dust).
 

Jagmandave

Well-known member
Joined
Nov 6, 2011
Messages
6,303
Location
Overland Park, Ks.
Just an educated guess on my part, but if it were me I'd go with the 60K too.....I think you'll be happier with more heat more quickly.

A buddy just installed a 17K BTU heater in his shop and it doesn't do squat except heat the area right in front of it, in my garage the same amount of BTUs warms my shop nicely.

Go big, you'll be happier.
 

jvitez

Well-known member
Joined
Nov 30, 2009
Messages
2,429
Location
Big Sky Country, Canada
I think 60K will be too big. You sound like you want intermittent heat. However, to be able to heat fast in our current arctic conditions, you'll be wildly oversized during milder temps, which means the heater will shut off too soon, never reach maximum combustion efficiency, and feel colder due to heat stratification, though your ceiling fan will help. So, you'd be sacrificing comfort and efficiency for the rest of the year to allow quick warms during Siberian weather.

Instead of replacing the heater, could you add some electric heat? Use both for quick warm ups then just leave your current NG heater to maintain temps?
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,410
Location
N CA
First I wouldn't replace the 30. I'd start it up sooner. You are in these extreme weather conditions about 10-15% of the total heating season and you are going to size for that? Not the best idea, imho. You may have to wear more clothes in these extreme conditions, but on balance the 30 will still do a decent job annually.
 

toyotadriver

Well-known member
Joined
Dec 30, 2010
Messages
1,586
I would go with the 60k and then set the thermostat to have a 1-2 degree temp swing in each direction. So, if you set the thermostat to 60*, it will come on when it gets to 59* and shut off when it gets to 61*. That can make up for having too large of a heater when it's warmer in your arctic temps by making it run longer when it's running and then it'll be off for longer periods of time. The heater should be sized for the coldest temps you'll potentially get. Your 30k is clearly too small. Another 15k isn't much more and I don't think that it'll be enough. I heat a 30x40x10 shop building with a 80k btu heater and I live in a much warmer climate. My 80k btu works perfectly.

In light of your other thread, you DEFINITELY need the 60k.
 
Last edited:

toyotadriver

Well-known member
Joined
Dec 30, 2010
Messages
1,586
First I wouldn't replace the 30. I'd start it up sooner. You are in these extreme weather conditions about 10-15% of the total heating season and you are going to size for that? Not the best idea, imho. You may have to wear more clothes in these extreme conditions, but on balance the 30 will still do a decent job annually.



The OP lives in MN. I bet he sees those temps for longer than 10-15% of the heating season.
 
To avoid these ads, REGISTER NOW!
OP
R

ranger098

Member
Joined
Jul 23, 2013
Messages
14
Location
Mound, MN
I just sold the 30k.. even when the temp was in the 30's (quite warm for MN) it took over a half hour to warm up. Sometimes i just dont have the ability (or want) to turn it on early, and around here we see temps 20 and under for about 3 months straight.

Right now i am leaning toward the 60k mainly because quick heat up and recovery times are important to me, and i plan to have this heater for a long time and take it with me to my next home, which i can assure you will have much more than an oversized 2 car! I will heat up the garage and then turn down the therm a couple ticks to prevent it from coming on so often. I may have to play with the therm a little more than a 45k, but i think that is an OK trade for faster warm up times.

Also, has anyone heard that oversizing is more efficient because the heater runs for less time? An HVAC guy told me this, but i didnt really trust that shady dude.
 

Jimmy_B

Well-known member
Joined
Dec 24, 2011
Messages
381
Location
..........
I'm in MN too and have about the same cubic feet to heat. I have a 75k BTU unit for 14 years without too many problems. I replaced the inductor motor this year and a controller 2 years ago. It heats up pretty quickly and recovery is quick after opening an overhead door. I wouldn't trade it for anything smaller.


My stepson does HVAC work in MN. He says the opposite about oversizing from what you've been told. YMMV
 

Pate

Well-known member
Joined
Oct 16, 2007
Messages
731
Location
New York
I have a 32' x 22' x 12' that's very well insulated (including doors) and the 45K works great.
 

dave67fd

Well-known member
Joined
Apr 25, 2011
Messages
872
Location
Southern NH
It is easier to maintain temp than to go up and down with big temp swings. Find a happy medium, set the thermostat and leave it.

Agreed, My 150,000 BTU house furnace took over an hour to heat my ~1000 sq/ft house from 45 to 70 one year when I shut i't down for vaca.

My 75k Mr Heater will take that long to bring up my 1000 sq/ft garage from 35 to 65. When you have alot of metal/tools/cabinets etc.. it takes awhile to bring all that up to temp.
 

ChargedUp!

Well-known member
Joined
Mar 11, 2010
Messages
503
Location
Twin Cities, MN
I'm in Plymouth, MN and have just under 1000sqft with 12'8" ceiling height of attached garage. When I built the house, I was all ready to buy a 100k heater. The HVAC guy said an oversized heater would not be as efficient and sold me on a 45k unit. I keep the garage between 58-60 degrees at all times and if/ when I open the 18x10 door, recovery time is around 15 minutes I would say to get me back to 60.
I'm surprised your 30k didn't work better for you...
 

meathooker

Well-known member
Joined
Dec 10, 2013
Messages
254
Location
Iowa
im an hvac contractor. i would install the 60k if you were my client


i have a similar sized gargae with 9' ceilings and i have a 60k
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
The ideal heater would be a multi stage unit, Reznor and others offer a two stage option.

The 30k is sized properly for a garage that is kept warm all the time if it is able to bring it to temp and keep it there. Bringing the temp up from single digits in a short time frame will require a considerably larger unit.

I would go with the 60k.
 

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
I have a 24X36 garage with 8 foot ceilings and I have a Hot Dawg 60,000 Btu natural gas heater that is vented outside thru the rear wall. My garage is insulated, walls are R-19 and the ceiling is R30. I have one window, an insulated entrance door and an insulated overhead door. Here in southeastern Wisconsin it can get pretty damn cold but the heater keeps the garage at 50 degrees and when I am working out there I turn it up 70 degrees. It doesn't take very long to bring the temperature up, but the actual length of time it takes depends on how cold it is outside. This is the second Winter I have been using this heater and so far it is working very well. I would highly recommend the Hot Dawg heater to anyone who is looking for a heating system to keep their garage warm.
 
Last edited:

Yankeefarmer

Well-known member
Joined
Jul 25, 2011
Messages
1,179
Location
Connecticut
Go with the 60K. My shop is 29 x 29 x 9' high and I 've heated it 20 years now with a Williams 60k propane wall furnace. It heats up in a reasonable period of time and cycling is not an issue. ( For reference, insulation is fiberglass in 2x4 stud walls and ceiling is 2x6 joists.)

Edited to add I'm on the Mass/Ct border, so it gets cold here, though probably not as cold as where the OP lives.
 