How close do Motor thermal overloads have to be

To avoid these ads, REGISTER NOW!

Dagny

Well-known member
Joined
Jul 25, 2014
Messages
3,059
Location
Northern Wi.
I have never heard of a thermal cutout with an ampere rating all I have worked on are motor specific and only have a part no.

Now if you are talking a motor starter on a very consistent load heaters sized for a couple amps more than your motor is drawing will protect it well.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,028
Location
Peace Valley,mo
Unless the overloads are in a hot room would change correct heaters. Check ebay or google used electric equipment ,starter heaters used never had a problem.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Who manufactured the overload relay? Some manufacturers are easier to source heater coils for then others.
 

Mzungu

Well-known member
Joined
Sep 3, 2022
Messages
176
For those type of overloads they are based on the service factor of the motor and an ambient temperature of less than 40 C. Usually the manufacturer builds in an extra allowance according to that service factor. Selection is based on their chart along with your motor parameters.
 
To avoid these ads, REGISTER NOW!

dutchgray

Well-known member
Joined
Sep 28, 2014
Messages
6,481
Location
Dorset. England.
Standard is to set overloads to 125% of motor FLA, some overloads have the 25% over built in so you set to FLA, others you have to add it yourself, read the instructions with the overload.
You can set up to 140% FLA if necessary if you get trouble and you check actual amp draw and are not over FLA running.
 
OP
T

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
26,201
Location
Niagara Region, Ontario, Canada
HEre's a few pictures. My single phase motor draws 22 amps, which I read as needs a b32 and the controller has b45 (31 amps) . too far apart I imagine? what is the proper name for the strips, and what's a ballpark cost on them?
Thanks
 

Attachments

  • IMG_20221031_125438.jpg
    IMG_20221031_125438.jpg
    849.1 KB · Views: 12
  • IMG_20221031_125448.jpg
    IMG_20221031_125448.jpg
    544.6 KB · Views: 12

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Is the motor 3Ø or 1Ø? The overload relay pictured is 3Ø, if single phase SQ D makes a jumper kit for 2 poles so only one heater coil would be required, but either jumpers or heater coils have to heaters tobe installed in order for the relay to reset, if 3Ø then all 3 heaters are needed, entering square d b32 into duckduckgo yielded a lot of hits & eBay had prices all over the place.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
I found used b32 local to me for $13 each.
I am told if I am running single phase motor to leave the center heater coil in place and wire the line & load to the 2 outer terminals . ?
You have no choice but leave the heater coil in or use jumpers, the relay will NOT reset without one or the other in place, if you doubt me, take one out & try to reset it.


The price has doubled since I looked for them some years ago.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,244
Location
Modesto, CA
I found used b32 local to me for $13 each.
I am told if I am running single phase motor to leave the center heater coil in place and wire the line & load to the 2 outer terminals . ?
You could put a jumper in the center and one of the other heater spaces. Only need 1x since its 240v
 

Mzungu

Well-known member
Joined
Sep 3, 2022
Messages
176
Give your local wholesaler a call. Guillevin, Nedco, and Graybar are all in your area. They are Square D distributors and may even have it in stock. Better than paying the outrageous fleabay shipping rates they charge Canadians.
 