How did I wire this incorrectly?

dhumac

Member
Joined
Apr 19, 2016
Messages
14
Location
East Coast Newfoundland
Also known as - how did I screw up!

I don't have a picture, but here is the layout. I'm wiring a 5000 watt garage heater - 10/2 wire to the heater (30 amp double pole).

Wiring to the heater:
Black load to black heater wire and white load to red heater wire.

Wiring to the thermostat:
I have a 28 amp double pole thermostat. I wired black to black and red to white. Now the problem is I didn't have my reading glasses and I'm not sure if I wired the load to line side or load to load side - I actually looked for something that indicated line/load on the thermostat, but I could see it.

When I switched to power on it was fine, but then when I turned the thermostat on, it sparked at the thermostat red wire and tripped the breaker. I then turned the power off and unwired the thermostat and capped the wires until I can figure it out.

So - if I wired load side to line side I wouldn't have expected it to short - but I could be wrong ... am I? Or could it be something different? Any pointers or direction would be appreciated. I've never wired a double pole thermostat before - single pole ones yes.

Thanks for any pointers.
 
To avoid these ads, REGISTER NOW!
OP
D

dhumac

Member
Joined
Apr 19, 2016
Messages
14
Location
East Coast Newfoundland
My 10/2 was black/white the thermostat was black/red+black/red and the heater is black/red.

I kept all black together, and paired red to white all along.
 
OP
D

dhumac

Member
Joined
Apr 19, 2016
Messages
14
Location
East Coast Newfoundland
Yes, standard 240v/30amp breaker - black to one of the breakers, white to the other (wrap it with electrical black tape for the inspector to sign off on) - ground to ground bar.

The thermostat is 28a.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,716
Location
NW Iowa
Did you look at the the instructions for the stat? Many times the black wires are line and load is red.
 
To avoid these ads, REGISTER NOW!

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
..... I think that thermostat is suppose to break one of the power legs... ONLY
so if you have 240V... chose the black to black or the white to red to connect your thermostat.. NOT both.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,716
Location
NW Iowa
..... I think that thermostat is suppose to break one of the power legs... ONLY
so if you have 240V... chose the black to black or the white to red to connect your thermostat.. NOT both.

Very possibly if this is a single pole stat, I got the jest this is a double pole but could be wrong. Again read the instructions.
 
OP
D

dhumac

Member
Joined
Apr 19, 2016
Messages
14
Location
East Coast Newfoundland
Got my electrician buddy to drop down ... I needed all red to one side all black to the other ... the back of the thermostat was ambiguous. It had load labeled to one side with both red and black wires coming from that side of the thermostat, and line then also had red and black wires. I needed to tie the Reds to the white and black from the panel and then the blacks to white and black to the heater.

It’s now toasty in the workshop. Just gotta finish the garage itself and life will be good ... we’ll warm at least.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
so you had a line to line short?

This is why pictures wouldve been very helpful. Hard to diagnose something like this over the internet without seeing it...
 

6PTsocket

Well-known member
Joined
Mar 12, 2014
Messages
4,593
This is why nobody should be without at least a cheap multimeter. A quick continuity check and turning the stat up and down enough to get the contacts to open and close would have showed you what was going on. Even a simple battery powered trouble light would have been good enough for this job. You obviously understand how it should work so it would have been a piece of cake to check out what that stat was doing.

Sent from my SM-G900V using Tapatalk
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
And this is why manufacturers need to do a better job of labeling terminals. I've ran into instances like this before myself, with no markings to indicate what wire is what. Agreed, that's when you pull out the meter, but you shouldn't have to.
 

6PTsocket

Well-known member
Joined
Mar 12, 2014
Messages
4,593
And this is why manufacturers need to do a better job of labeling terminals. I've ran into instances like this before myself, with no markings to indicate what wire is what. Agreed, that's when you pull out the meter, but you shouldn't have to.
After you have figured out how it should work, the marks make perfect sense. Sometimes not so much, before. What shoud be and what is are not the same thing. You have to deal with what ya got.

Sent from my SM-G900V using Tapatalk
 