Sorry guys, probably a dumb question, but the only fluorescents I've done were either troffer style or ones that plugged into a switched receptacle. I'm wondering if the surface mounts need a fixture box installed to make the connections and/or mount it to? Or just pull the wire through a hole in the ceiling and make the connection inside the fixture itself and mount it to the ceiling?
 
To avoid these ads, REGISTER NOW!

RECox286

Well-known member
Joined
Apr 11, 2012
Messages
1,399
Location
South Joisey (yeah, that is part of the USA)
I use a Romex connector thru the closed portion of the fixture, where the ballast

resides, as an entrance for the house wiring, and use the troth as a mechanical

enclosure, which it is. Fasten the fixture directly to the ceiling rafters, and then

run 1/2" EMT from fixture to fixture as necessary. You will find KO's for this purpose

at likely spots on the fixtures.

Uncle Bob
 

Steevo

Well-known member
Joined
Aug 18, 2009
Messages
8,738
Location
43.49600, -112.04300
I did as Bob suggests, I ran a romex from the switch to the first fixture in a row, brought it in through the ceiling (small hole in the sheet rock), through a romex fitting in a knockout in the back of the fixture. I used box spacers between fixtures, so they had a hard connection between them, and I then ran standard 14ga wire (hot/neutral/gnd) from fixture to fixture down a row to tie them all together. I have four fixtures in a row, each with four bulbs.

Romex connector:
ARLINGC00003_C7_TR_001.jpg


Box spacer:
2611176.jpg


My lights:
1081764363_BoEru-M.jpg


Oh, and the fixtures are screwed through the sheet rock into the trusses every 2 feet.
 
Last edited:
To avoid these ads, REGISTER NOW!

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
I'm putting in individual light fixtures, not continuous runs like Steevo. I plan to run all my romex in the attic and enter each fixture through a hole in the sheetrock ceiling. That way, I wont have to run visible EMT along the ceiling from fixture to fixture like REFCox286 suggested...

My .02 worth,
Paul
 