how do they get single phase from three phase?
ericm
Southern Oregon
The place we just bought has a large irrigation pump that's run off a dedicated 480 3phase. There's an electric gate which I'm pretty sure is run off the same meter. The docs for the gate operator say that it can run on 120 or 240v single phase.
My question is how do they normally get single 120/240 single phase from 480 three phase and does it matter for the three phase equipment?
LXCam
Tap two legs of the 480 and use a single phase transformer to step it down to 120/240.
Assuming it is feed from that and you have a 1/2hp drive motor you’d only need a little 1.5kva transformer. So if you see something like that, well there ya have it.
LXCam
Btw, if they are doing that you’re going to have either a 480v breaker panel or a fused disconnect feeding the transformer, then either a breaker or fused disconnect before the gate operator. Point being, they’ll be some equipment upstream that stands out.
rlitman
Long Island
That's one option, if there's a 3 phase panel to take from, and probably the better one. If you ONLY need 240V and don't need a neutral, and the service is 277/480 wye, you can also tap that single phase with a buck transformer (or reverse feed a boost transformer; they're the same thing). The advantage to this, is that buck/boost autotransformers are WAY smaller than step up/down transformers.
E
ericm
Southern Oregon
There's a couple electric boxes that aren't the usual homeowner stuff I'd recognize. One has a switch for the pump. The other is large, maybe 2' tall, with a big rotary switch knob and a small round push button labeled "reset". Next time I'm there I'll open it. There's a lot of what I'll charitably call farm wiring on this place so it might not have breakers/fuses in all the right places.
The meter showed something was drawing 0.009 kW. Since the pump wasn't on, that must be the transformer?
step down transformer. for a gate operator, the transformer can be very small
that is the pump controller.
yyc_ranger_4x4
Calgary, Ab
I'd double check that pump, it may be a dual voltage and you're actually running it 208V 3phase.....if you don't have separate 480V and 120V panels with a transformer around, then most likely it's 120/208V 3phase....
dave*99
Coastal NJ
Post a couple photos of all your panels and we can tell you what’s there.
Photos of panels, labels breakers and transformers will tell the story.
Otherwise we will make loads of assumptions and……. Well you get the idea
Jim greengo
Behind my house
We used to run the old Lincoln tombstone 240v single phase welders off of 277v on jobsites all the time.
The worked/welded really good from what I remember. Hahaha
Bert_
NW Iowa
Did they last? I would think the transformer would run kind of hot.
Or just considered it consumable?