How do you ground a metal box with larger gauges?

To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,499
Location
Richmond, VA

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,279
Location
Texas
Is that aluminum. Looks like it. I’ve wondered about alu with copper ground wires. Why doesn’t that cause the same type issues we see with copper wiring in houses? i.e. corrosion and loss of continuity.

Maybe because grounding lugs are not exposed to AC?

I ask because I picked up a box full of aluminum lugs at Restore but have been hesitant to use them.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,969
Location
Central Iowa

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,969
Location
Central Iowa
Is that aluminum. Looks like it. I’ve wondered about alu with copper ground wires. Why doesn’t that cause the same type issues we see with copper wiring in houses? i.e. corrosion and loss of continuity.

Maybe because grounding lugs are not exposed to AC?

I ask because I picked up a box full of aluminum lugs at Restore but have been hesitant to use them.
Pretty much all lugs are aluminum.
 

Bad Habit

Well-known member
Joined
Mar 19, 2014
Messages
1,993
Location
Chumstick WA
The lugs are a different alloy than whats used for wire. Much more stable for corrosion and thermal characteristics. All lugs should have markings for what type of wire they are rated for. Have never seen an aluminum lug not rated for CU wire (UL/ETL listed ones at least)
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
Is that aluminum. Looks like it. I’ve wondered about alu with copper ground wires. Why doesn’t that cause the same type issues we see with copper wiring in houses? i.e. corrosion and loss of continuity.

Maybe because grounding lugs are not exposed to AC?

I ask because I picked up a box full of aluminum lugs at Restore but have been hesitant to use them.
There have been lugs made of aluminum but were copper conductors only. AL lugs are fine in most cases, I would not use one where it was exposed to the weather but that is a rare situation.
 

Gozo

Well-known member
Joined
Oct 10, 2013
Messages
250
Location
Central VA
Is that aluminum. Looks like it. I’ve wondered about alu with copper ground wires. Why doesn’t that cause the same type issues we see with copper wiring in houses? i.e. corrosion and loss of continuity.
When ever I’ve had that concern, I’ve put a bit of Noalox in with the wires. I think it’s more of peace of mind thing than anything else. My CH breaker panel has aluminum ground buss bars with bare copper wiring; 50 years, not a bit of corrosion. Then again, it’s in a 100% dry environment.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,004
Location
Modesto, CA
When ever I’ve had that concern, I’ve put a bit of Noalox in with the wires. I think it’s more of peace of mind thing than anything else. My CH breaker panel has aluminum ground buss bars with bare copper wiring; 50 years, not a bit of corrosion. Then again, it’s in a 100% dry environment.
is the ground bar an add-on? CH panels typically come with copper busbars
 

Gozo

Well-known member
Joined
Oct 10, 2013
Messages
250
Location
Central VA
There are 2 types of Cutler Hammer breakers.
The CH has silver plated copper busbars.
The BR has aluminum.
Which type do you have?
I had to go check. It’s the CH. and I thought they were aluminum all this time. Learn something new everyday on GJ.
I still have a bottle of Noalox in the garage. Used it on appliance grounding lugs over the years. Probably more mental and insurance than anything else.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,004
Location
Modesto, CA
There are 2 types of Cutler Hammer breakers.
The CH has silver plated copper busbars.
The BR has aluminum.
Which type do you have?
nope not quite. Cutler hammer is no longer around as they were bought by eaton. So there isnt 2 types of CH breakers. Theres 2 types of EATON breakers- Eaton CH and Eaton BR

The BR breaker line was formerly made by BRYANT before eaton took them over.
 
OP
E

enochian

Well-known member
Joined
Sep 16, 2015
Messages
76

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,499
Location
Richmond, VA
So the 2 wires go into the 2 holes right?

No wire nut right?
Your EGC lands there, then you run it out to the receptacle. The connection to the box comes with it screwed to the ground hole.

We still don't know what wire size or type you are dealing with, though. That bar is not what I would use if a nut would suffice
 

Doozer75

Well-known member
Joined
Oct 24, 2009
Messages
260
Location
Buffalo NY
The lugs are a different alloy than whats used for wire. Much more stable for corrosion and thermal characteristics. All lugs should have markings for what type of wire they are rated for. Have never seen an aluminum lug not rated for CU wire (UL/ETL listed ones at least)
Not a different alloy.
The connection lugs are silver plated to prevent dissimilar metals corrosion.
The silver is very thin, but that is the difference.
Wire is just aluminum.
Lugs and buss connections are plated.
Silver is also used on switch contacts.
The reason for this is,
the oxide form of silver is nearly the same
conductivity as pure silver.
As we know from copper turning green,
this is very not true for copper.


-Doozer
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,731
Location
VT
Man the misinformation in this thread is off the charts.

And we still don't know wtf the OP is trying to bond....
 
OP
E

enochian

Well-known member
Joined
Sep 16, 2015
Messages
76
Man the misinformation in this thread is off the charts.

And we still don't know wtf the OP is trying to bond....


2 different projects with stranded aluminum wire.

1. In-wall oven with some kind of obscure legacy SEU cable

2. Hardwired drop-in stovetop.
 
Last edited: