I understand that. But at some point something will fail, the upright, the baseplate, the anchor, the slab. It would be nice to make sure (as the installer) that your part is not the weakest link.
The anchor bolt isn't close to its breaking point, so I would expect everyone omits it because its so far from being critical.
My back of the napkin math:
- Concrete tensile strength is roughly 1/10 that of the compressive strength. (say 300 psi)
- A 4" bolt will grab at 3.5" down giving a stress cone surface area of around 30 sq in.
- That is around 9000 lbs of force before the bolt pulls out of the concrete
- A 3/4" anchor bolt has .45 sq. in. of cross section, which would be just over 20ksi of tensile force before the thing pulls out of the concrete...
A cheap, mild steel will withstand over 50ksi of force, so the concrete slab should fail/pull-out way before any 4", 3/4" wide anchor bolt does.
^ This would not hold true for longer and/or thinner bolts. The lift manufacturers usually spec the 3/4" bolts, which makes us good as long as we follow that guideline.