HiItsMeJimmy
Well-known member
- Joined
- Sep 1, 2012
- Messages
- 66
For you guys with a well insulated larger slab from a cold start how long for slab to get up to temperature?? 12 hours?? 24 hours??
how long is a piece of string ??
depends on so many variables; starting temp, design temp, insulation, mass of slab, tube spacing, ground water, etc etc .. typically a small properly built, well insulated, dry slab might take only a few hours .. whereas a large badly set up system with ground water leaching heat might never come up to design temp
some larger well built systems ive done took 2 or 3 days to slowly warm through the first time
how long is a piece of string ??
Building is 40x64x14
R-30 in ceiling with 6 inches of open cell on walls
2" XPS under 6" concrete perimeter insulated as well
8- 1/2" -300ft. runs 12" spacing, 6" around perimeter with adjustable reising manifold.
180000BTU Hardy outdoor wood burner with 45% glycol
3 insulated 12x12 doors
OO9 circulator pump at boiler and 009 circulator at manifold
1GPM through each circuit
3/4 feeds from boiler
Honeywell Mixing valve @113* Return water 83*
Radiant thermostat WITHOUT floor probe.:
Let system run for 12 hours and not much change in temp. Guess I need to fire boiler and let it eat!!
Let system run for 12 hours and not much change in temp. Guess I need to fire boiler and let it eat!!
Clarification, please. Was the boiler running for those 12 hours?
Sent from my SCH-I545 using Tapatalk 4
I have a reifing adjustable manifold. Some supply lines feel warmer then others even though flow through each circuit is identical. Gonna shoot it with them gun and see where I'm at
Have a closed system without outdoor wood burner, didn't think I needed an air purge.
didn't think I needed an air purge.
Since nobody has seem to answer your question, my system raises my room temp about 1 degree/hr of run time. 1/2" tubing on 12" centers, fed at approx. 100degrees and dropping approx 20* from input to output. Heating 30x40x12. I fired it up last week, initial warmup brought it up 10* and ran 9hrs to do it.
Played with system after work last night. The manifold has adjusters for each zone. I had adjuster turned clockwise to increase flow. Shot feed with temp gun and temp was 80s. Temp gauge on main feed is 120. For some reason when I had adjuster turned clockwise it shut flow off. Opened adjuster all the way counterclockwise and let system RUn for 8 hours. I had floor temp of 72. Garage was very warm. Tried to find manual for my reising. (Spelling?) Manifold . Looks like they are discontinued. Might be a reason why!

Why would I.need a purger when using an outdoor wood burner. I assume since boiler has vent it would be pushed out system and bleed through wood boiler. I have an 009 at boiler and 009 after mixing valve right before manifold inlet. Went off wood boilers instructions for hooking a radiant floor up. Seems to be working good now that I'm getting flow through all circuits. Should slab temp be 5* greater then desired room temp?
fyi; those guns don't work properly on any kind of reflective surface .. ie, pex, copper etc