rbcsaver said:
My Bro-in-law had an excellent idea, when running outlets run a single 20A circuit, to each series (number your choice depending upon use) of upper outlets, then a separate line for the lowers. Snap out the tabs to keep them isolated. Thus if you have some cahrgers plugged into the upper outlet and your chop saw on the lower, then there is separate line draws.
While this is a good idea, and you are even allowed to share a single neutral line to the two of them if the two hots are absolutely, positively, on opposite hot buss bars (240 volt potential between the two hots) (remember, the two hots are opposite phases so the alternating cycles on the neutral doesn't overload it)
you MUST also use a two pole breaker with a tie bar between the handles (like you use on a 240 circuit).
Other words of learned wisdom. Spend the money and buy good quality screw tighten backwire outlets. These are the ones that you loosen the screw, push it it all the way, insert the straight wire, and tighen up the screw. This pinches the wire with a serrated plate inside that is tighened by the screw. Very positive and effective. Leviton Pro Grade has a back wire model, and so does Eagle/Cooper. They have very stiff contact springs inside and are quite difficult to plug into and pull plugs from, what you want in a shop. They are also very good quality inside having the same guts as the 20 amp rated receptacles (same unit different faceplate)
Also, for commercial purposes you can have no more than 10 receptacles on a 15 amp breaker and no more than 13 on a 20 amp breaker. This would be a good rule to follow, however most people would never put that many on one breaker anyhow. I have 27 receptacles on nine breakers. A couple of circuits have 4 receptacles and a couple of circuits have only one receptacle (a single 20 amp rated outlet for super heavy duty 120V work such as Mig welders.) I did 4 inch square deep boxes with two receptacles in each, on opposite phase circuit breakers. Used metal fronts with three screws retaining each receptacle (top, bottom and center) into the stamped cover. Very solid.
Charles