How many grounds question

m32825

Well-known member
Joined
Jul 26, 2015
Messages
1,009
Location
Central FL
If I'm running two circuits down one piece of conduit, does each one need its own ground wire? Using 12 gauge copper for all wires, each circuit is 20 amps.

-- Carl
 
To avoid these ads, REGISTER NOW!

mark flucke

Active member
Joined
Feb 14, 2016
Messages
33
one ground sized for the largest circuit-hence you would have :1 green or bare Copper #12, 2 white #12 and 2 Non-*********** conductors #12 traditionally black or red
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
Properly installed EMT doesn't need a ground wire.
If one is installed anyway, the EMT takes the large majority of the fault current. (like 75%)
 