Cobra4B
Well-known member
Update - Turns out my kitchen lights, laundry room light, garage lights, and outlets for the garage door openers are on one 15 amp circuit. The kitchen has 12 60watt cans, the laundry room a single 4' 2-bulb fluorescent, hallway to garage 1 60watt can, and the garage only has a single 1/3rd horse opener in the center bay.
It appears that it's maxed out already. Figure 0.54 amps per can light (13), 0.9 amps per fluorescent (4 currently - 1 laundry 3 garage), and 5 amps for the garage door opener = 16+??
Update 2 - The 3 exterior lights over each garage door are on the same circuit too.
----------------------
I haven't tracked the panel to see what amp circuit this runs off. We bought the house early September and only one light worked. Today I swapped the T12 stuff out for new T8 and new T8 5000k bulbs. I'd like to add another 6 lights so I have 3 in each bay. Can I wire it all together, or will I need to add another switch/circuit? Not sure what amperage a typical T8 4' 2 bulb fixture pulls.
~Brian
It appears that it's maxed out already. Figure 0.54 amps per can light (13), 0.9 amps per fluorescent (4 currently - 1 laundry 3 garage), and 5 amps for the garage door opener = 16+??
Update 2 - The 3 exterior lights over each garage door are on the same circuit too.
----------------------
I haven't tracked the panel to see what amp circuit this runs off. We bought the house early September and only one light worked. Today I swapped the T12 stuff out for new T8 and new T8 5000k bulbs. I'd like to add another 6 lights so I have 3 in each bay. Can I wire it all together, or will I need to add another switch/circuit? Not sure what amperage a typical T8 4' 2 bulb fixture pulls.
~Brian