How many lights on 20 amp circuit?

legotech7

Active member
Joined
Oct 10, 2010
Messages
35
Location
Kannapolis NC
Hello everyone, I need to know how many lights I can run on a 20 amp circuit. My plan is to hang 10 florescent bulb fixtures with 2 T8 bulbs each at 32 watts for each bulb. The 20amp circuit used solely for the lights, but might add some more in the future, ( outside lighting and the such ). The ballast's would be the electric start types, if that makes a difference. Would that many lights be ok for the 20 amp circuit?

Thanks all......
 
To avoid these ads, REGISTER NOW!

jonjon1

Well-known member
Joined
Mar 11, 2015
Messages
1,036
For lights 1920 watts

I did 20a in my storage building, needed 20 a switches and 20 fixtures, 12-2, it wasnt cheap, especially them 3 ways, they were like $8 each, and we needed a TON of them, I think the regular ones are $1.50 each..

And I think its against code to do this in a non commercial application, you would be stuck with 15a circuit, still 1800 watts at 80% is 1440 so if that was 75 watt lights, you could put 19 of them...

most electricians in a residential setting around here go 12 fixtures per 15a circuit...
 
Last edited:

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,442
Location
USA
Hello everyone, I need to know how many lights I can run on a 20 amp circuit. My plan is to hang 10 florescent bulb fixtures with 2 T8 bulbs each at 32 watts for each bulb. The 20amp circuit used solely for the lights, but might add some more in the future, ( outside lighting and the such ). The ballast's would be the electric start types, if that makes a difference. Would that many lights be ok for the 20 amp circuit?

Thanks all......

With "normal" ballasts, you are only at 590 watts, only about 1/3 of the maximum.
Good luck
CD
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
The 2 lamp ballasts themselves draw .8 amp, or 96 watts.

10 of them would be OK on either a 15 or 20 Amp circuit.

With a 15 amp circuit you'd be able to install another 5 fixtures and not be overloaded.
With a 20 amp circuit you could install another 10 for a total of 20.

Lighting loads are figured at 80% of the breaker rating.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
Maybe you looked at a 4 lamp ballast? Or an 8' ballast?

Advance ICN2P32N draws .49 amps and 59 watts when running 2 F32T8 lamps.
CD

You are right of course, but I should explain my reasoning.
That's a dual voltage ballast. Normal household fluorescent fixtures from the big box stores don't have the dual voltage ballasts. You'd have to go to supply house to get them.

I was doing by the figuring by the REB-2P32-SC which is a 2 lamp ballast that draws .8 amp

http://www.homedepot.com/p/Philips-...7064?cm_sp=BazVoice-_-QA_PSVP-_-202977064-_-x

EDIT: I checked one of the Lithonia fixtures from HD that I had pulled the Accu-Pro ballast out to convert to 277V and it draws .49 amp, by gosh. :eek:
You could put 25 of these on a 15 amp circuit, or 32 on a 20 amp.
I guess the only way to answer this question is to check the individual ballast.
 
Last edited:

jonjon1

Well-known member
Joined
Mar 11, 2015
Messages
1,036
Nothing in the Code prohibits this

Like I said I was not sure, I remember a conversation when I was having my 20a lighting done, that the residential light fixtures did not have heavy enough wire to be on a 20a breaker, because on the strong of 20a lighting I wanted to include the bathroom light, I ended up having to buy a different fixture that was special ordered and again EXPENSIVE.

After I did it, I figured I could have ran 2 15a lines with less trouble and for less money...
 
OP
L

legotech7

Active member
Joined
Oct 10, 2010
Messages
35
Location
Kannapolis NC
Thanks guys, I did a little home work, I think I'll be OK with my original inquiry.. 10 light fixtures on a 20amp circuit at 32 watts per bulb... and then some. Now I just have to figure out my lay out.......

Thanks again.......
 
To avoid these ads, REGISTER NOW!

jonjon1

Well-known member
Joined
Mar 11, 2015
Messages
1,036
Pretty much figured that one.

Problem here is every state and every area of every state seems to have their own rules.

So much simpler to get a right answer when people put their location in their profile.

Agreed?:)

I would agree, but what if the member is an international man of mystery, then advertising said location would be a farce...
 

GuyllFyre

Banned
Joined
Sep 2, 2014
Messages
378
Location
Scotia, NY
Oh, just for the fun of it, I took my $12 wattometer thingie and plugged it into a standard dual tube 40W T12 shop light and saw an average of 62 watts per fixture.
2300W/62W=37 fixtures (approx)
 
OP
L

legotech7

Active member
Joined
Oct 10, 2010
Messages
35
Location
Kannapolis NC
Ok, researching some of the light fixtures from the big box stores, I noticed most of the fixtures are wired with their own standard type plugs. I wanted to hard wire the lights with two separate switches, so I can turn on just the one side witch will have five lights and only turn the other if I need them. Can I just remove the plugs and hard wire into them? I wanted to do this in series, ( daisy chain if you will ) . I'm a bit confused as how to wire them.. Sorry for all the questions, very much a nube at this...... While I'm asking, what type of bulb is best for lighting. The lights will hang at about 9 feet off the floor. They have cool white, day light and so on, confused about that also...

Thanks again........
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
You need to buy better fixtures. The ones with the plugs are UL listed with the plug and should not have the plug removed. In addition most of those are chain hung, and if you read the fine print, they must be chain hung, its again part of the UL listing, and is due to heat generated by the ballast.

Even with surface mount fixtures you are better off to set them off the ceiling surface with spacers at the mounting points, for cooling.

Buy fixtures that are designed to be hardwired.

Charles
 

MattN03

Well-known member
Joined
Nov 4, 2007
Messages
601
Location
KY
I've just wire a duplex outlet and then have an outlet for two lights from a box store. If it fails, it's a simple matter of unplugging and replacing.
 

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
I wanted to do this in series, ( daisy chain if you will ) .

I understand what you mean, but actually you are wiring them in parallel.
Also follows Charles (in GA) advice. The fixtures with plugs aren't what you want if you are going to "hardwire" / conduit install. There are multiple threads here about what others have use and which big box store carries them. I used Lithonia T8 tandam fixture like these:
T8 fixtures link
But they are harder to mount if you are by yourself. You can do it, you have to be creative on how to hold the fixture to the ceiling while you screw it up. 4 foot twin tubes are easier to handle.
If you wish to hang them, then yes you can use the plug type. But then you must run conduit and receptacles to each fixture location.
 
Last edited:

MattN03

Well-known member
Joined
Nov 4, 2007
Messages
601
Location
KY
I used 4' quad fixtures from Lowe's on my last few fixtures and like them a lot.
 
OP
L

legotech7

Active member
Joined
Oct 10, 2010
Messages
35
Location
Kannapolis NC
Yes in parallel, as for hanging them , this whole project I have dome by myself. Suffering from RA and doing them on my good days..But anyway,...Doing this on a budget, the hard wired fixtures are a bit more expensive. If I wire them in parallel, can I just tap into one juction box for each side, and wire it that way? would I need to add more J boxes? Here's a layout, a bit rough, but it is what it is.... please feel free to add to it or any other suggestion you might have. Obviously the light switches are coming from the source panel and so on, so my routing from there on, is where I'm a little leery on. I hope this all makes sense.

Once again, Thank you all.......
 

Attachments

  • light layout.jpg
    light layout.jpg
    32.5 KB · Views: 25