Did a search earlier, but not really finding my answer. How many outlets, can I put on a circuit, with a 20amp breaker ? The wire should be 12-3 correct ?
Did a search earlier, but not really finding my answer. How many outlets, can I put on a circuit, with a 20amp breaker ? The wire should be 12-3 correct ?
I am prety sure the NEC says 8 outlets per circuit and you can use 12/2 with ground on a 20 amp circuit as was stated above.
Rick
Chapter and verse please.
There is nothing in the NEC that limits the number of outlets per circuit.
Did a search earlier, but not really finding my answer. How many outlets, can I put on a circuit, with a 20amp breaker ? The wire should be 12-3 correct ?
NEC 220.10 discusses branch circuit load calculations. For the number of receptacles on a single branch circuit, 220.14(L) is probably the best reference, requiring that you use 180 volt/amperes per outlet as a means of calculating this. An outlet would be a "strap" thus a single receptacle or a common duplex receptacle would be treated at the same 180 VA.
This works out to 180VA divided by 120 volts equals 1.5 amps per strap.
20 amp breaker divided by 1.5 amps equals 13.3 or 13 straps or outlets (receptacles)
Thats 10 receptacles on a 15 amp breaker.
As already noted, local inspectors may have different ways of figuring this, or different requirements, so your mileage may vary.....
Charles
So in a garage in general, (in the USA), it is required to have GFCI protection on all 110 VAC circuits that are not hard wired?
I think I saw something like that before reading the selfhelp link posted above.
Can anyone other than the local building inspector really answer this?
I know that the detached building that is included with the property that I am buying is already built and occupied (and all circuits out there are not GFCI).
Only the "normal" outlets around water or outside are protected this way.
I don't intend to use GFCI breakers and I hate the outlets, but I could always put one GFCI outlet at the beginning of each branch run to be in compliance.
NEC 220.10 discusses branch circuit load calculations. For the number of receptacles on a single branch circuit, 220.14(L) is probably the best reference, requiring that you use 180 volt/amperes per outlet as a means of calculating this. An outlet would be a "strap" thus a single receptacle or a common duplex receptacle would be treated at the same 180 VA.
This works out to 180VA divided by 120 volts equals 1.5 amps per strap.
20 amp breaker divided by 1.5 amps equals 13.3 or 13 straps or outlets (receptacles)
Thats 10 receptacles on a 15 amp breaker.
As already noted, local inspectors may have different ways of figuring this, or different requirements, so your mileage may vary.....
Charles
I know what you mean, and for a garage, that's usually right. However, depending on what's plugged into the circuit, there is a limit. In 99% of cases it wouldn't apply for garage, though.
NEC 220.10 discusses branch circuit load calculations. For the number of receptacles on a single branch circuit, 220.14(L) is probably the best reference, requiring that you use 180 volt/amperes per outlet as a means of calculating this. An outlet would be a "strap" thus a single receptacle or a common duplex receptacle would be treated at the same 180 VA.
This works out to 180VA divided by 120 volts equals 1.5 amps per strap.
20 amp breaker divided by 1.5 amps equals 13.3 or 13 straps or outlets (receptacles)
Thats 10 receptacles on a 15 amp breaker.
As already noted, local inspectors may have different ways of figuring this, or different requirements, so your mileage may vary.....
Charles