how many outlets / circuit??

Bevis

Well-known member
Joined
Jan 10, 2006
Messages
808
Location
Moore Haven, Florida
Did a search earlier, but not really finding my answer. How many outlets, can I put on a circuit, with a 20amp breaker ? The wire should be 12-3 correct ?
 
To avoid these ads, REGISTER NOW!

MisterCMK

Well-known member
Joined
Nov 29, 2007
Messages
170
Location
USA
You can put as many outlets as you want on a circuit. However, you will want to figure in what you are planning on using the outlets for to decide how many circuits to use. As far as the wire goes, 12/2 with ground is what you will need.
 

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
I am prety sure the NEC says 8 outlets per circuit and you can use 12/2 with ground on a 20 amp circuit as was stated above.


Rick
 

Steve in Mi

Well-known member
Joined
Mar 13, 2007
Messages
1,042
Location
Mid Michigan
Did a search earlier, but not really finding my answer. How many outlets, can I put on a circuit, with a 20amp breaker ? The wire should be 12-3 correct ?

I have 4 - 6 outlets per ckt. however they are physically located (separated) such that it would be impossible for me to be using more than one outlet on a given ckt. at the same time. 12 -2 w/g for 120 volt outlets and 12 -3 w/g for 240 volt outlets on 20 Amp, single and 2 pole breakers respectively.
 

MisterCMK

Well-known member
Joined
Nov 29, 2007
Messages
170
Location
USA
I am prety sure the NEC says 8 outlets per circuit and you can use 12/2 with ground on a 20 amp circuit as was stated above.


Rick

Chapter and verse please.

There is nothing in the NEC that limits the number of outlets per circuit.
 

rcleaver

Well-known member
Joined
Oct 9, 2008
Messages
357
Location
Fairfax Station VA
Remember too, that you're less likely to have a problem with tripping breakers with a 20 amp circuit. I've run a 3 hp router, CNC machine and dust collector on the same circuit at once with no problems. I just start them one at a time.
 

nissan_crawler

Well-known member
Joined
Jan 12, 2008
Messages
9,638
Location
Wichita, KS
I prefer to keep circuits as separated as possible. I only have a 20x24 garage, and have almost all spaces used in a 20 slot panel.

Basically, I would separate them as much as possible, while leaving a few empty slots in the panel for a future circuit.

Also, you can never have too many outlets. I have 4-240 volt outlets, 2-4 plug 120 boxes, 2-3' outlet strips, and 7-2plug 120 boxes. They all get used quite frequently.
 

nissan_crawler

Well-known member
Joined
Jan 12, 2008
Messages
9,638
Location
Wichita, KS
Chapter and verse please.

There is nothing in the NEC that limits the number of outlets per circuit.

I know what you mean, and for a garage, that's usually right. However, depending on what's plugged into the circuit, there is a limit. In 99% of cases it wouldn't apply for garage, though.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Did a search earlier, but not really finding my answer. How many outlets, can I put on a circuit, with a 20amp breaker ? The wire should be 12-3 correct ?

Check with your inspector, many cities have amended the NEC to limit the amount of receps per circuit.

Or, you can look at how many tools you'll have running multiplied by the amount of people working at the same time and go from there.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
NEC 220.10 discusses branch circuit load calculations. For the number of receptacles on a single branch circuit, 220.14(L) is probably the best reference, requiring that you use 180 volt/amperes per outlet as a means of calculating this. An outlet would be a "strap" thus a single receptacle or a common duplex receptacle would be treated at the same 180 VA.

This works out to 180VA divided by 120 volts equals 1.5 amps per strap.
20 amp breaker divided by 1.5 amps equals 13.3 or 13 straps or outlets (receptacles)

Thats 10 receptacles on a 15 amp breaker.

As already noted, local inspectors may have different ways of figuring this, or different requirements, so your mileage may vary.....

Charles
 
Last edited:

JOHNMAN

Well-known member
Joined
Aug 14, 2006
Messages
194
Location
Southwest Indiana
So in a garage in general, (in the USA), it is required to have GFCI protection on all 110 VAC circuits that are not hard wired?

I think I saw something like that before reading the selfhelp link posted above.

Can anyone other than the local building inspector really answer this?

I know that the detached building that is included with the property that I am buying is already built and occupied (and all circuits out there are not GFCI).

Only the "normal" outlets around water or outside are protected this way.

I don't intend to use GFCI breakers and I hate the outlets, but I could always put one GFCI outlet at the beginning of each branch run to be in compliance.



What are the typical rules regarding installing a 3-way switch in one structure that gets power from a separate structure? (i.e. a 3-way switch in the house that turns on outside lighting on the detached building and power comes from the detached building)? Are there special colors to be used? Any tags or labels required?
 
To avoid these ads, REGISTER NOW!

hidollartoys

Well-known member
Joined
Jul 15, 2008
Messages
594
Location
K. C. Metro area
NEC 220.10 discusses branch circuit load calculations. For the number of receptacles on a single branch circuit, 220.14(L) is probably the best reference, requiring that you use 180 volt/amperes per outlet as a means of calculating this. An outlet would be a "strap" thus a single receptacle or a common duplex receptacle would be treated at the same 180 VA.

This works out to 180VA divided by 120 volts equals 1.5 amps per strap.
20 amp breaker divided by 1.5 amps equals 13.3 or 13 straps or outlets (receptacles)

Thats 10 receptacles on a 15 amp breaker.

As already noted, local inspectors may have different ways of figuring this, or different requirements, so your mileage may vary.....

Charles


I agree with the interpertation. However I believe that you should also figure a 80% max load on a branch curcuit. This allows some safety factor for preventing breaker trip. This is how I figure the quanity of "loads" on a circuit when I do remodeling. I dont want to get called by the home owner that the breaker keeps tripping.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
So in a garage in general, (in the USA), it is required to have GFCI protection on all 110 VAC circuits that are not hard wired?

I think I saw something like that before reading the selfhelp link posted above.

Can anyone other than the local building inspector really answer this?

I know that the detached building that is included with the property that I am buying is already built and occupied (and all circuits out there are not GFCI).

Only the "normal" outlets around water or outside are protected this way.

I don't intend to use GFCI breakers and I hate the outlets, but I could always put one GFCI outlet at the beginning of each branch run to be in compliance.

This depends on which code the building was wired to. Not sure when the GFCI requirement came into effect, but if it was wired prior to that code, then it is quite legal. Its also possible that some building inspectors might allow some leeway on this requirement, so there are reasons why the building might not have GFCI protection.

Charles
 

nissan_crawler

Well-known member
Joined
Jan 12, 2008
Messages
9,638
Location
Wichita, KS
If I could get by without gfci, I would. I installed one for pressure washer/cord in lawn type use, but that's it. Otherwise, it's a PITA in a garage.
 

bofus

Well-known member
Joined
Dec 8, 2007
Messages
45
Location
Washington State, USA
In my shop, I have several 20 amp circuits with 12 duplex outlets on each with a 20 amp rated GFCI at the first postion and used 12-2. Passed inspection.
 

CalGeo

Active member
Joined
Jan 17, 2008
Messages
41
Location
Alameda & St Helena, California
NEC 220.10 discusses branch circuit load calculations. For the number of receptacles on a single branch circuit, 220.14(L) is probably the best reference, requiring that you use 180 volt/amperes per outlet as a means of calculating this. An outlet would be a "strap" thus a single receptacle or a common duplex receptacle would be treated at the same 180 VA.

This works out to 180VA divided by 120 volts equals 1.5 amps per strap.
20 amp breaker divided by 1.5 amps equals 13.3 or 13 straps or outlets (receptacles)

Thats 10 receptacles on a 15 amp breaker.

As already noted, local inspectors may have different ways of figuring this, or different requirements, so your mileage may vary.....

Charles

Charles is correct again, plus the 80% factor. I run a 12/3 in the garage or shop to five locations and use a four plex (two duplex receptacles) at each location. This gives me two circuits at each locations in case I want to run two power tools at one time without worrying that I will trip a breaker. You can also run the 12/3 in and out of the single duplex box alternating the two circuits. Remember to tie the two breakers together too.

Most people don't have a real concern about tripping a breaker because of their shop use. IMO, it is best to keep the amount of receptacles to four or five per circuit in a multi person shop.
 

Torque1st

MEMBER EMERITUS
Joined
Sep 14, 2008
Messages
5,668
Location
KC Metro, Kansas
I always physically plan out my outlets so I only have one wall's outlets on each circuit. That is all the north wall outlets on a circuit either 110 or 220, all the east wall circuits on a circuit... Plus dedicated circuits for various shop tools etc. This works for normal 2-3 car size garages or shops. When you get to big places it does not.

When you buy a breaker panel get the big 40 size panels, they only run a few $ more than the 30 breaker panels.
 

MisterCMK

Well-known member
Joined
Nov 29, 2007
Messages
170
Location
USA
I know what you mean, and for a garage, that's usually right. However, depending on what's plugged into the circuit, there is a limit. In 99% of cases it wouldn't apply for garage, though.

I mentioned that in my first post; you need to plan ahead for what is being used.
 

MisterCMK

Well-known member
Joined
Nov 29, 2007
Messages
170
Location
USA
NEC 220.10 discusses branch circuit load calculations. For the number of receptacles on a single branch circuit, 220.14(L) is probably the best reference, requiring that you use 180 volt/amperes per outlet as a means of calculating this. An outlet would be a "strap" thus a single receptacle or a common duplex receptacle would be treated at the same 180 VA.

This works out to 180VA divided by 120 volts equals 1.5 amps per strap.
20 amp breaker divided by 1.5 amps equals 13.3 or 13 straps or outlets (receptacles)

Thats 10 receptacles on a 15 amp breaker.

As already noted, local inspectors may have different ways of figuring this, or different requirements, so your mileage may vary.....

Charles

220.14 is in regards to fixed multioutlet assemblies, not a general purpose receptacle, however it is a good number to go off of. For someone's personal garage or home, the best bet is to decide ahead of time what you are going to be using the outlets for and space them and add circuits according to the future use.

BTW, you should only plan on using 80% of the circuit for a safety margin, so that would give you 10 outlets using the 180VA on a 20amp circuit.
 
OP
B

Bevis

Well-known member
Joined
Jan 10, 2006
Messages
808
Location
Moore Haven, Florida
there i some good information here. I'll mainly be the only person in my shop running any power tools, unless a friend stops by. I'm trying to place outlets where I think that I might need them, or where I'm gonna have my power tools, and other electric needs. So with the 10 outlets per circuit, I can get away with about two maybe three circuits.
 

wayoff

Well-known member
Joined
Dec 31, 2006
Messages
134
Location
South east NH
There is no limit because the amount of current you can draw through a 10/2 wire is more than what the 20 amp breaker will handle. So the worst that can happen if you have too many things plugged in is you'll pop the breaker way before the wire can heat up. So it gets down to common sense. You'll find in most garage applications that people run 6-8 on a 20 amp breaker, but in a residential it is not uncommon to see people run up to 12 on a 15 amp.
 

Question

Well-known member
Joined
Aug 7, 2008
Messages
171
Location
New England
The only thing that the inspector tested in my garage was the GFI's, then went to each box and tripped the GFI. I asked how many more boxes I could add, he said as many as I want as long as they were GFI protected...
 

MisterCMK

Well-known member
Joined
Nov 29, 2007
Messages
170
Location
USA
If you have the tools/experience to run pipe for your outlets, do so. That way you can easily change things down the road as it is a simple matter of fishing some wire through the conduit to add/change circuits.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I got a bunch of them, single breaker to single duplex and left a lot of things so I could wire as I went. When I figured out what went where it got its own circuit, especially heavy draw items or hard motor starts.
 