I am not sure if theres a regional rule, but how many receptacles can be on a 20A circuit (with 12/2 cable and 20A breaker)?
ARTICLE 100—DEFINITIONS
Receptacle. A receptacle is a contact device installed at the
outlet for the connection of an attachment plug. A single
receptacle is a single contact device with no other contact
device on the same yoke. A multiple receptacle is two or
more contact devices on the same yoke.
I think code is minimum 48" from the floor, but I like the 49" recommendation.

I think code is minimum 48" from the floor, but I like the 49" recommendation.

When I built my last shop the best advice I got was to run to separate circuits to each 2-gang box so that the left side was one circuit and the right was another so that you could run two tools at once in one place and not trip the circuit.
And if I may ask, how often do you take full advantage of this setup?When I built my last shop the best advice I got was to run to separate circuits to each 2-gang box so that the left side was one circuit and the right was another so that you could run two tools at once in one place and not trip the circuit.
When I built my last shop the best advice I got was to run to separate circuits to each 2-gang box so that the left side was one circuit and the right was another so that you could run two tools at once in one place and not trip the circuit.
And if I may ask, how often do you take full advantage of this setup?
IMO it's a lot of extra work and/or expense for no real big benefit.
You don't neccessarily need 2 duplex receptacles in every location if you don't want.
2 circuits can be installed at a single duplex.