How to check amp draw on motor

tpierce

Well-known member
Joined
Jun 23, 2011
Messages
177
I need to check amp draw on a furnace blower motor with a multimeter. The motor is single phase 220. Do I check both legs and add together, or check both legs and go with higher reading? I don't have a clamp-on meter.
The motor sounds like it's drawing a lot of amps on start-up. I've replaced the run capacitor.
 
To avoid these ads, REGISTER NOW!

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
You can only test one leg at a time or it won't measure right. And each leg will tell you what it's drawing
 

bsaint

Well-known member
Joined
Apr 26, 2010
Messages
5,109
Location
Manchester, CT
I think you're safest bet is to pick up an amp clamp. Im not sure if you can even do AC current on a meter with just the leads.
 
OP
T

tpierce

Well-known member
Joined
Jun 23, 2011
Messages
177
I bought a clamp meter and checked 1 leg. Start-up amps were 8, run amps were 3. I think that's within normal specs, although I can't see the data plate on the motor. It's a 1/2 horse motor, 230v.
 
To avoid these ads, REGISTER NOW!

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
Whatever meter you use, you need one with a peak hold feature. The response time on most digital meters is such that you'll not see the true startup current without peak hold. And yes, clamp on meter is the way to go for this application, but an inline with a shunt might work.
 

ForceFed70

Well-known member
Joined
Apr 27, 2010
Messages
3,441
Location
BC, Canada
Startup amp draw is irrelevant when troubleshooting or testing to see if motor is good/bad.

Theoretically, the startup draw is infinite and the load is a dead short. The number a meter spits out is just a representation of how quickly it can take a reading rather than an actual valid measurement of the draw.

I'm curious tho. If it's a single phase 220V motor, why are you guys telling him to measure both legs?
 

bsaint

Well-known member
Joined
Apr 26, 2010
Messages
5,109
Location
Manchester, CT
We use three wire single phase (technically split phase) 220 in the states. We havet graduated to two wire l1/n like Europe yet. That's why he's checking both hot legs.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Use a clamp on ammeter. Unless you're specifically checking just the T1 or T2 windings, you only need to check one leg. You also need to do it with the access panels on the unit, otherwise the readings will not be accurate.

Tommy
 
Last edited: