My friend is having stucco installed on his house.
He found one room has no power and the circuit breaker trips straight away.
The contractors had removed the clapboard and banged the old nails back through, most likely hitting a cable.
How do we find "we" find which nail / nails are the culprit.
An electrican will be doing all the work, I am wondering if there is an efficient way to find the problem than just rip off all the siding like the builder wants to do.
I was wondering if there was some kind of pulse or tone generator that would work.
 
To avoid these ads, REGISTER NOW!

zuk123

Well-known member
Joined
Mar 25, 2012
Messages
957
Location
Houston TX via Chicago, Phoenix, LA, and San Diego
There are testers that will give you the distance to the end or a break. They are called Time Domain Reflectometers and are common with network installers. If you know someone in the low voltage install industry they might be able to help you. You still need to figure out where exactly the wire is though.

A stud finder with wire detection might work for you. Make some assumptions on where the wire starts and map it thru the wall...

Or possibly something like a Fox and Hound

http://www.amazon.com/dp/B001ULPREW/?tag=atomicindus08-20

would let you find the wire, but it won't tell you where the break is.

I think you might be stuck removing the siding.

zuk
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I think you are SOL.

Edit: If the wall hasn't been recovered and the nail heads are visible you could get a very long piece of wire and check for continuity from each nail head to the circuit that's dead.
 
Last edited:
OP
B

bd8134

Well-known member
Joined
Oct 16, 2008
Messages
219
Location
Franklin, MA
The Fox and Hound is interesting.
I like the idea of the continuity to the nail head.
He has the electrician coming tomorrow, just see what he wants to do for now.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
i would make them go back and pull out every single nail. You dont know if there are other nails that go through just the hot, could be fine now and could be a problem later. I would also be worried about a nicked wire burning through later.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
Make them re-wire that entire circuit... YESTERDAY! :bitchslap

This is the right answer. The wiring is damaged, the insulation is damaged, and it now presents a safety hazard. You need to rewire the whole circuit (or at least the section(s) that are damaged, and not just pull the nail and pray for the best. :evil:
 

eljefino

Well-known member
Joined
Feb 21, 2008
Messages
336
If you can pull both ends of the wire at the breaker box and hook to an AC wall wart through a series resistor (light bulb) a sniffer might be able to detect the AC up to the nail but no further.

But I agree, make them rewire. Then the boss will make sure his guys don't pull this stunt again-- who knows how many other nails they've almost driven into wires? Will being a hardass avert future catastrophes like burning down a daycare? Quite possibly!
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I'd most likely use my Amprobe circuit tracer to find the short. I'd then replace that section of cable, either by adding a splice box or repulling it between the two devices. Then I'd meg the circuit when I was finished.
 

Terry454

Well-known member
Joined
Jan 22, 2011
Messages
106
Location
Illinois
At the risk of being Mr. Obvious:
This is a good argument for wire in conduit. In my area we are often criticized for our insistence on this method, but now you know ...
 

deter

Well-known member
Joined
Jun 22, 2011
Messages
578
Location
Indiana
find all devices on the circuit, start disconnecting one at a time starting from the end of the chain. Try breaker after each one. might get lucky
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,761
At the risk of being Mr. Obvious:
This is a good argument for wire in conduit. In my area we are often criticized for our insistence on this method, but now you know ...


The conduit rule is due to organized labor/crime.

NM cable does have a good record for residential wiring....
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,618
Location
Long Island
find all devices on the circuit, start disconnecting one at a time starting from the end of the chain. Try breaker after each one. might get lucky

That's how I would start. Identify everything that doesn't have power, open up every box, and pull out every wire. Then make a guess as to where the middle is, split the wires up, and check for resistance between hot and neutral/ground, to see which direction the short is in.

Maybe once you've got the short narrowed down to a small area, I might try to trace it with a toner and probe, but it is probably not worthwhile finding the exact location of the damage. You just need to run a new wire between the two points that the damaged wire connects. Even if you could open up the walls, and put the damaged wire in a new box, you wouldn't have enough slack to repair it.
 
To avoid these ads, REGISTER NOW!

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
A nail will go through the armored cable with no problem....

There is a reason nail block is supposed to be used.

Another reason most of my exterior walls are 6".....

Sounds like things were done out of sequence.....the house should have been wrapped...and chicken wire installed 'before' drywall installed.

As noted....there is no real short cut to this....that section of wire has to be replaced.
 

jbberns

Well-known member
Joined
Jan 1, 2012
Messages
105
The conduit rule is due to organized labor/crime.

NM cable does have a good record for residential wiring....

organized labor/crime?
That is a stupid comment.
I think there was a big fire in Chicago years ago, that ended up putting that rule in place.
 

Gooch

Well-known member
Joined
May 30, 2009
Messages
676
Location
Petersberg, IA
organized labor/crime?
That is a stupid comment.
I think there was a big fire in Chicago years ago, that ended up putting that rule in place.



pretty sure conduit wasn't around in 1871, or for atleast another 50 years.


I'm an Union Electrician and I've seen drywaller's run screws through conduit plenty of times. all current wiring methods have their place, NM is GREAT for residential.
 
Last edited:

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Here is an interesting thread on the same subject on a different forum...

http://www.electriciantalk.com/f2/conduit-vs-romex-28390/

It's pretty much common knowledge that unions were responsible for the rule....just like unions were responsible for the rule that you have to use a licensed electrician to do the work...oh yea, all the licensed electricians in Chicago are in the union.....
 

KnurledNut

Well-known member
Joined
Jan 28, 2011
Messages
8,156
Location
n/a
have you tried replacing the circuit breaker itself? it doesnt happen often, but sometimes they can fail too.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,761
organized labor/crime?
That is a stupid comment.
I think there was a big fire in Chicago years ago, that ended up putting that rule in place.

Who do you think ran the unions??? The bosses still behave as they are part of organized crime....


The Chicago fire is used for a lot of excuses, but the EMT being used, the requirements of other areas to not use plastics for DWV & water are all union featherbedding, because they want more labor intensive methods used.

EMT is a good wiring method, NM is also has a good history for wiring homes, if some Bozo goes wild with a nail gun, EMT will not hold up, might as well require rigid conduit & cast iron boxes....
 

jbberns

Well-known member
Joined
Jan 1, 2012
Messages
105
Who do you think ran the unions??? The bosses still behave as they are part of organized crime....


The Chicago fire is used for a lot of excuses, but the EMT being used, the requirements of other areas to not use plastics for DWV & water are all union featherbedding, because they want more labor intensive methods used.

EMT is a good wiring method, NM is also has a good history for wiring homes, if some Bozo goes wild with a nail gun, EMT will not hold up, might as well require rigid conduit & cast iron boxes....

Thanks for the info. I am an officer in my local and didn't realize I was also a crime boss. That dang wool that's pulled over my eyes!
 
OP
B

bd8134

Well-known member
Joined
Oct 16, 2008
Messages
219
Location
Franklin, MA
Turned out my friend was real lucky. :thumbup:
He had already put in a new breaker and that also tripped straight away. I had to tell him how to remove the old breaker from the panel over the phone..:shocking:
The electrican came, checked the first electrical box with a meter and said the short was going away from the panel. Opened the second box and a nail had pierced the plastic box and shorted 2 tightly packed wires inside. He repaired the wires and tested it, everything ok. He removed the nail from the outside. Luckily he did not have to get the sheeting removed to trace the problem.
I think he had AFCI breakers in his panel and in his case, the ground and white wire was shorted by the nail. If he had a regular breaker it most likely would have not have even tripped.:eyecrazy:
 

bassman

Well-known member
Joined
Feb 13, 2005
Messages
198
Location
florida
very lucky. But to find wich nail if you were'nt so lucky, I use one of those beeping testers where it dosen';teven have to make contact on the wire and it beeps and light blinks when it senses voltage. You could haave just run it by all the nails on the outside, and you'd have found it. Glad you got it fixed without much work needed
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,618
Location
Long Island
very lucky. But to find wich nail if you were'nt so lucky, I use one of those beeping testers where it dosen';teven have to make contact on the wire and it beeps and light blinks when it senses voltage. You could haave just run it by all the nails on the outside, and you'd have found it. Glad you got it fixed without much work needed

That would work if the nail was hot, but it wouldn't work, since the breaker was tripping.
 

bassman

Well-known member
Joined
Feb 13, 2005
Messages
198
Location
florida
Awe! Forgot about that. Than i guess I'd take the hot off the breaker and ground it and hit the nails with a Ohmeter to the nail and the other lead to ground. If there were a million nails to deal with, I'd start by removing devices from the affected circuit at different intervals till the br stayed on, then reconnect know where my starting point would be.
 

JakeKohl

Well-known member
Joined
Feb 23, 2012
Messages
1,365
Location
Greenville, SC
Turned out my friend was real lucky. :thumbup:
He had already put in a new breaker and that also tripped straight away. I had to tell him how to remove the old breaker from the panel over the phone..:shocking:
The electrican came, checked the first electrical box with a meter and said the short was going away from the panel. Opened the second box and a nail had pierced the plastic box and shorted 2 tightly packed wires inside. He repaired the wires and tested it, everything ok. He removed the nail from the outside. Luckily he did not have to get the sheeting removed to trace the problem.
I think he had AFCI breakers in his panel and in his case, the ground and white wire was shorted by the nail. If he had a regular breaker it most likely would have not have even tripped.:eyecrazy:

you should, errr...rush out and buy a lottery ticket...now.
 