How to Prevent Nuisance Trips

PJorgen

Active member
Joined
Oct 27, 2020
Messages
42
Location
Reno, NV
I replaced an existing breaker for a new dishwasher with a GFI breaker. I inadvertently purchased a GFI/AFCI breaker and am getting constant nuisance trips. Is there any way to correct this without swapping out the breaker?
 
To avoid these ads, REGISTER NOW!

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,660
Location
Austin, TX
Is there any way to correct this without swapping out the breaker?
The combo breakers are highly problematic for me. I've replaced most of them. And arc-fault breaker followed by a gfci outlet doesn't nuance trip like the afi/gfi combo breakers.

I'd replace the breaker with a GFI breaker, or "more correctly" an AFI breaker and a GFI outlet.
 
OP
P

PJorgen

Active member
Joined
Oct 27, 2020
Messages
42
Location
Reno, NV
The breaker does not differentiate between GF or AF trips. I don't think there is an issue with the circuit, it's a dedicated 20A circuit and the house is fairly new. I should have checked the receptacle when the dishwasher was being replaced but didn't think of that. None of the other receptacles are back-stabbed so I doubt that one is.

Would prefer to have used a GFI receptacle, but the receptacle is BEHIND the dishwasher! Not sure who thought that was a good idea.

Guess I'll replace the combo breaker with a GFI-only breaker, but it bugs me that I blew $63 on a breaker I can't use.
 
OP
P

PJorgen

Active member
Joined
Oct 27, 2020
Messages
42
Location
Reno, NV
Ugh! Just did a bit more research and learned that dishwashers are notorious for causing nuisance trips on combo breakers! Lesson learned for $63.

Will H-D accept a return of a used breaker?
 
To avoid these ads, REGISTER NOW!

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,257
Location
Coastal NJ
Note the combo breaker GFI offers equipment protection at 30 mA of fault current. In your kitchen you need the life safety protection offered by the stand alone GFI at 5 mA.

Walta
Those breakers with GFPE (30mA protection) do exist. But I suspect the OP bought a CAFCI/GFCI breaker with the class A 5 mA protection. I'm not sure GFPE combos are on the shelf in Home Depot. Has anyone seen one there?

"A standard Square D AFCI (Arc Fault Circuit Interrupter) breaker is generally not a GFPE (Ground Fault Protection of Equipment) unit, but rather protects against fire caused by arcing. However, Square D offers "Dual Function" (CAFCI/GFCI) breakers that combine arc-fault protection with Class A GFCI protection (typically 4-6mA), which is more sensitive than standard GFPE. "
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Ive never paid attention to that but now that you mention it, next time im at home depot im gonna specifically look because it has peaked my curiosity.... i suspect HD doesnt stock them as it creates a potential for a major issue (shock hazard) as homeowners and handyman wont know the difference.... or what to look for...
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,257
Location
Coastal NJ
Ive never paid attention to that but now that you mention it, next time im at home depot im gonna specifically look because it has peaked my curiosity.... i suspect HD doesnt stock them as it creates a potential for a major issue (shock hazard) as homeowners and handyman wont know the difference.... or what to look for...
The GFPE types with 30mA trip that I'm familiar with have an orange trip handle. I see them in shore power pedestals. On the boat itself, you should have class A protection, but the pedestal gets this:

1770320582637.png
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Is the orange handle a code requirement? Ive never heard of a code requiring that. if not then that will vary by brand
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,660
Location
Austin, TX
Those breakers with GFPE (30mA protection) do exist. But I suspect the OP bought a CAFCI/GFCI breaker with the class A 5 mA protection. I'm not sure GFPE combos are on the shelf in Home Depot. Has anyone seen one there?


The GFPE types with 30mA trip that I'm familiar with have an orange trip handle. I see them in shore power pedestals. On the boat itself, you should have class A protection, but the pedestal gets this:
I dunno about the combo breakers, but chasing a ground-fault on with an "marine" inverter equipped RV, I found that the inverter was designed for use in marinas and commercial marina GFI has an allowed leakage of 30mA before tripping. Residential is 5mA... Basically no way the RV I was working on was every going to play nice with a "residential GFCI" breaker at 5mA.

1770322474687.png
 