Sorry. That sounded funny when I was typing it so I went with it... I can hear my wife groaning from across the room... lol
Anyway. Running new power to my barn. Neighbor came over to check the progress and said.. "Chris (guy we bought the place from) fancied himself an electrician. I've had to fix some stuff he did for neighbors so you better check yours.." Sweet.
Got the new wires ran to the panel and started checking things out. Came across a couple things that I'd like to ask about.
But first. As much info as I can think of.
QO load center. 200 amp. Powered by 4 wires. Main disconnect is outside under the meter. It looks like the neutral and ground are bonded. Separate bus for grounds, not sure if panel came that way or if it was added.
Now my questions.
#1. In the pics you will see that all the neutrals go to the bonded neutral/ground bar. All the grounds go to the ground bar that looks to be added (left side middle of box). Is this an acceptable way for the panel to be wired? I've never seen one one this way but I'm no electrician. I play hot rod builder during the week.
question 2. I have 2 circuits. One for the spa (not there anymore. circuit breaker off) and the other for the heat pump. Both fed by 3 wires. I was under the assumption that the 2 wires were power and the third would be ground. He has them both wired into the neutral bar. Should those be be moved to the ground bar? I ask about this because the a/c will dim the lights considerably when it kicks in.
pics attached.
Thanks a bunch,
Jason
Anyway. Running new power to my barn. Neighbor came over to check the progress and said.. "Chris (guy we bought the place from) fancied himself an electrician. I've had to fix some stuff he did for neighbors so you better check yours.." Sweet.
Got the new wires ran to the panel and started checking things out. Came across a couple things that I'd like to ask about.
But first. As much info as I can think of.
QO load center. 200 amp. Powered by 4 wires. Main disconnect is outside under the meter. It looks like the neutral and ground are bonded. Separate bus for grounds, not sure if panel came that way or if it was added.
Now my questions.
#1. In the pics you will see that all the neutrals go to the bonded neutral/ground bar. All the grounds go to the ground bar that looks to be added (left side middle of box). Is this an acceptable way for the panel to be wired? I've never seen one one this way but I'm no electrician. I play hot rod builder during the week.
question 2. I have 2 circuits. One for the spa (not there anymore. circuit breaker off) and the other for the heat pump. Both fed by 3 wires. I was under the assumption that the 2 wires were power and the third would be ground. He has them both wired into the neutral bar. Should those be be moved to the ground bar? I ask about this because the a/c will dim the lights considerably when it kicks in.
pics attached.
Thanks a bunch,