Humidity control: what to do first?
Rusty Pilot
Indiana
I'm in NE Indiana (in the middle of this heatwave) and my barn has not handled humidity very well. The floor condenses like crazy. After fixing a separate issue this past month, I noticed the barn doesn't have a vapor barrier or even a tyvek house wrap. It's literally exterior metal then insulation. I'm assuming that is the source of my problem.
My wall now:
Being in Indiana, I see stupid hot weather and stupid cold weather (and sometimes in the same day). I'm assuming a vapor barrier in my case should be on the inside (interior wall, vapor barrier, insulation, exterior metal) as I do heat it in the winter. Is the house wrap worth it?
I do have 3 wall mounted oscillating fans to help move air. What makes it tricky is the I have an interior wall that separates the front to the main garage area. I'm not really sure what to expect when I remove the plywood or paneled walls. This issue makes the house wrap more appealing since the exterior panels need to come off rather than working around an interior wall and attic. (Not really sure how to slip the vapor barrier through the interior wall)
(Pardon the mess. Working on building a workbench and purging things at the same time)
In your opinion, what should I do first? Any contractors you would recommend in the NE IN/NW OH/S MI area?
Is double bubble useful? I have a source that will give quite a lot of it.
mikedodge
Is there any ventilation to outside? If you're sealed well you'll still have humidity problems if there's a lack of ventilation and the fans only move around air that's already there. I need to run a dehumidifier to keep mine under control.
AC-WC
NE, Indiana
I don't believe housewrap would help your current situation. Since the sheet metal is already up that's a ton of work to remove just for housewrap. Short of removing all your paneling I don't know of another way to install the vapor barrier to the interior.
I have the same condition in this weather as you. The floor is cold compared to the air and will continue to 'sweat' until the temps equalize. Fan is on with a couple windows open....
R
Rusty Pilot
Indiana
How large is this building ?
2400 sq ft.
Outside of a couple windows and 2 garage doors, the soffit goes above the panel ceiling and to the attic area. What kind of dehumidifier to you use? Should I consider an exhaust fan/vent or something like that?
Big ac units
Considering it
BillK
Beautiful Southern Maryland
2400 sq ft.
Considering it
I dont think the lack of vapor barrier has much to do with it. The condensation comes from temperature changes.
I think AC/heat is going to be your best bet and might actually be the least expensive in the long run. If you cant swing that right now then a small exhaust fan might keep the air moving enough to help in the short term.
racecougar
Missouri
In agreement with everyone else here. I'd take the time/money you would invest into vapor barrier and funnel that toward AC.
finn
The UP, God's country
The problem is that the slab is a large cold mass, and the warm humid air this time of year releases water when it contacts the slab, which is below the condensation point.
The water isn’t coming up through the slab, so a vapor barrier won’t help. It’s condensation.
I had a similar situation on a garage with an overly thick slab (whoever poured it must have been of the Garage Journal thicker must be better crowd). It would take forever to warm up in the spring since the door faced north, and never got sunlight, and the walls were insulated. The soffits were ventilated, though. Leaving the doors open when the weather started warming up after a cold winter brought the slab temperature up, and by July the floor was dry, with no condensation.
A larger garage within three hundred feet of that one, but with windows and SW facing doors and windows gets some sunlight and the floor doesn’t condense, as it heats up faster in the spring.
My shop, a mile away, is heated in the winter with in floor radiant, so the slab temperature never drops. It’s perfectly dry during hot humid days like we’re seeing now.
R
Rusty Pilot
Indiana
AC it is... anyone have any recommendations? I am not sure if a mini split would suffice. Just the quick google search suggests that a 5 ton unit is what I would need.
Favorite (or hated) brands?
racecougar
Missouri
I'd run a load calc to determine sizing.
When I chose my mini-split, I compiled a spreadsheet to build out a comparison of specs. I went with a Gree unit (basically a non-DIY version of Mr. Cool) and have been nothing but pleased with its performance.
pembol
Air flow. Create more of it.
A lot of folks are suggesting more ventilation, but that may actually make the issue worse. A others have said, the root cause of the condensation is the temperature of the floor dropping below the dew point of the air. Just looking at the weather for Indianapolis, the dew points are often in the mid 70s (ugh). If your floor is cooler than this it will condense the moisture from the air. If you ventilate the garage and bring in more moist air, you are just bringing in more water to condense. Later in the season, when the floor warms up the problem will likely fix itself.
Sealing up the garage on its own may help a little bit, as the air the air that is in the garage will condense, but without new air coming in there won't be as much moisture coming in to condense, but probably not a huge amount on it's own. Warming up the slab by opening up the garage at the hottest part of the day may also help some, but makes the garage less pleasant to be in. Or you could actively heat the floor, but also not great for the working environment.
Your best bet is probably AC/minisplits AND air sealing. The minisplits will reduce the humidity in the garage and keep the dew point above the temp of the floor. Air sealing will stop more moist air from entering the garage and make the minisplits have to work less hard.
mikedodge
2400 sq ft.
Considering it
If the windows and doors are open regularely with your fans going that should handle the issue but im guessing you probably dont have that liesure (i dont). My space is maybe 1200sq feet? It's a normal dehumidifier I use.
Paycheck
Increasing airflow doesn’t work if all that air is coming from the outside. If you just recirculate inside air then the humidity doesn’t go anywhere. You need a big dehumidifier/HVAC system. And even that won’t work well if the space isn’t well sealed because of outside air coming in.
pembol
Do a real load calculation, and decide if you want the mini just for cooling/dehumidification or heating as well. If you want heat (which I am guessing you do) that will probably drive the sizing as I am sure your heat loads are much higher than your cooling loads.
Also, remember this is a garage, not your house, so you don't necessarily need to plan for the worst possible scenario. If it is -10F out, I am not working in garage so it is fine if the garage is only 50F. If you are above 3 ton, then two independent systems may be your best bet - it is more versatile and efficient than a multizone system, and not much more expensive.
R
Rusty Pilot
Indiana
I already have a heater in there. I'm looking for cooling/dehumidifying.
pembol
If the heat is the wall heater in the photo, you may find heating with the minisplit to be better, also the cost differential for a unit that heats well is small and gives you options for heat. Either way, definitely consider 2 units if you end up needing more BTU - also addresses the 2 room issue.
R
Rusty Pilot
Indiana
I got a gas heater in the corner. It keeps the barn pretty warm in the winter. I keep the barn at a min of 50 when I'm not in there.
finn
I agree. In my experience wth the garage I had a spring / early summer problem with the floor sweating opening the door actually made the problem seem worse, at first.
However, after a number of years of trying different things, opening the door and dealing with the floor sweating for a while was the lesser of all evils. sort of hold your nose and bite the bullet. Once the floor warmed up, everything was fine until the next spring, and it only took a week or two to get there if the door was open as much as feasible.. Keeping the door closed, using fans, etc just prolonged the agony, although I think a really high airflow like from a Big *** fan or the like would speed the floor slab warm up past the dew point.
racecougar
Missouri
Local dewpoint is going to play a role in whether or not that approach is reasonable. Getting the slab above 75F whilst still attached to the massive heatsink that is the Earth is a bit of a struggle here in MO, not to mention, entirely unpleasant. It looks like the dewpoint up in the UP is in the 50's-60's right now, by comparison.
Torka
Maybe throw in a window air conditioner or two and see how it goes, before pulling the trigger on a more permanent solution.
mikedodge
When you get moisture on the floor after opening a door that's usually from the temperature or humidity differences between inside and outside the same way a car can cover in in that condensation film when you drive it inside or outside at times, usually more noticable from parking garages or in the summer when you're going from hot outside to air conditioned inside.
BillK
I would say that 5 ton is probably not going to be enough. Thats what I have at my business but my unit is 30x60x 15 tall and is pretty "tight" I have other units on 3 sides so I dont have a lot of heat loss / gain. Flat roof has about 6" of foam.
The 5 ton seems to be just about right for my place but yours is almost 40% larger.
Hank11
Tennessee
I kinda like the idea of two mini splits. You can get plenty of capacity that way, and maybe only run one at a time when you’re not in there or maybe just run both of them and let them do their mini split thing with their inverter motors. If the barn is one big room, I’m pretty sure that’s what I would do.
For a “right now cure“ you could go to a big box store and buy a couple of $250 dehumidifiers and make the place a whole bunch better after they’ve been running overnight. It won’t be cold, but it’ll be dry and nothing‘s gonna be sweating because you’ve moved the dewpoint significantly.
Boostingaz
Indiana
I am in Indiana as well. I run a Moiswell MP100 dehumidifier in the shop. I have it mounted up about 7ft on the wall and hooked up to a thermostat to control it from. It keeps my 56x56 with open trussed 16ft ceilings shop at 52-54%. I could probably set it even lower. It pulls out probably 20 gallons a day easy.
R
Rusty Pilot
Indiana
Got a picture of the setup?
R
Rusty Pilot
Indiana
Well, looks like near future will be a big dehumidifier then a mini split later on.
After looking a bit more, is there any bad thing about putting in a 10 mil vapor barrier to the main area of the barn and foam board up in the attic (since i can pull back the insulation easily)? My main area has no wall paneling on the upper half and the lower is wood paneling with a couple screws holding the panels. I'm not 100% sure how the front room in the barn is insulated as it has some annoying interlocked wood paneling. I'm not sure if doing the barrier in the main barn area is worth it if the front room has gaps.
yhprum
Brisbane Australia
How about an entry chamber of sorts, so when you have to open the big door, all the dry air doesn’t go out the door along with temperature swings.
PS, oh yeah, forgot to mention how nice your shop is!
finn
Vapor barrier goes on the conditioned side of the insulation.
R
Rusty Pilot
Indiana
That will be difficult for the 10x10 and a 18x10 garage doors. I do technically have that with the front room.
Ps: thank you
Mainiac Mat
Maine
House wraps (like Typar or Tyvek) are used on stick built houses on the outside of the esterior plywood sheathing, and their purpose is to protect the sheathing from water... i.e. rot. Typar (the better option) breaths, to allow moist air to pass through and not condense on the sheathing.
Vapor barriers (whether kraft scrim on fiberglass batt or poly sheet) go on the inside of the insulation, behind the interior finish wall (sheet rock, paneling, etc...) and prevent moist air from passing (in or out).
If you condition the interior air (AC) and remove the moisture, the outside air moisture will want to travel through the walls to the interior, as vapor drive will strive for equilibrium.
So if you condition the interior space, I suggest you also apply a poly vapor barrier to retard the moist air passing through the walls.
Hohn
Diesel Central, Indiana
I'd go further-- the vapor barrier would be a disaster.
Vapor barriers only ever make sense where you have a single seasonal dominant vapor drive. Think northern Canada where you'll have a massive vapor drive from warm inside humid air to frozen desiccated air outside.
Or if you are in Miami and trying to keep out warm humid air in an almost always colder/drier interior space.
Here in Indiana, with both seasons capable of extremes, a vapor barrier just means condensation and mold. Put it on the inside, you get mold in summer. Put it on the outside, it molds in winter.
Skip the vapor barrier entirely.
The order of operations is this:
- Seal out water FIRST.
- Then seal out air
- Then address vapor.
The order matters because there' no point is sealing out vapor if you have air bringing more of it in. And there's no point sealing out air if you have water ingress.
If you want to control the atmosphere inside a space, you must first enclose it.
The easiest option for most of us that makes sense and is fairly cost effective is a flash-and-batt. This is a skim coat of closed cell spray foam just enough to seal things and then stuff your wall cavities with kraft-faced insulation. The kraft facing is a vapor *retarder*, not a barrier. That means it lets things dry out, but slowly. It slows the vapor movement. And since the spray foam is sealing water and air, you end up with a surprisingly effective setup that doesn't cost a ton compared to other options.
